Topic: Duct Bank Concrete Reinforcing

User: JasonWrenn, Location: Louisville,KY

Asked on: Monday, August 12, 2024 at 3:10 pm EDT
Answered on: Thursday, March 6, 2025 at 1:04 am EST

Question: We are starting a new major 3 year project, apparently the EPC convinced my engineering team to allow the elimination of rebar reinforcing in the concrete for electrical duct banks to save money. We will have dozens of major duct banks. The EPC sold the idea that Fiber would work just as well. Please give thoughts or referencing on why this is a bad idea or should not be allowed. Located in Kentucky where freeze and thaw (frostline) is an issue, also will have potential truck loading over the duct banks. I am not finding much online. Thanks

Okay, eliminating rebar in electrical duct banks in Kentucky (with its freeze-thaw cycles and potential truck loading) and replacing it solely with fiber reinforcement is a very risky proposition and deserves intense scrutiny. Here's a breakdown of why it's a bad idea, referencing relevant concepts and why you're likely struggling to find direct online comparisons specifically for duct banks

Why Eliminating Rebar is Problematic (Especially in Your Environment):

1. Load-Bearing Capacity and Structural Integrity



Rebar's Role

Rebar (steel reinforcing bars) provides the primary tensile strength in concrete structures. Concrete is strong in compression but weak in tension. Rebar resists bending and cracking under load. Duct banks, even if buried, are subject to significant loads:


Dead Load

Weight of the duct bank itself (concrete, conduits, cables).

Live Load

Weight of soil above, vehicular traffic (trucks), construction equipment.


Impact Load

Sudden forces from traffic or nearby construction.

Fiber's Limitation

While fiber-reinforced concrete (FRC) improves ductility and crack resistance
after cracking occurs, it

does not provide the same level of tensile strength or load-bearing capacity as rebar.
Fibers primarily act to hold the concrete together after a crack forms, preventing it from widening and potentially spalling. They delay failure, they don't prevent it to the same degree as rebar. Kentucky Specific

The freeze-thaw cycles require an extra level of strength and crack resistance that is difficult to achieve without traditional steel reinforcement.2.

Durability and Freeze-Thaw Resistance



Rebar's Contribution (When Properly Designed)

Well-designed rebar placement and concrete cover help prevent cracking, which is critical for durability. Cracks allow water to penetrate, leading to:


Freeze-Thaw Damage

Water expands when it freezes, exerting pressure within the concrete. This repeated cycle causes cracking and disintegration, especially in saturated conditions common in buried structures. Rebar helps to limit crack width, mitigating this.

Corrosion

Water and de-icing salts (if near roadways) can corrode the rebar itself, weakening the structure. Proper concrete cover over rebar protects it from these elements.


Fiber's Impact

Fibers can improve freeze-thaw resistance to some degree by reducing crack width and improving the concrete's ability to resist micro-cracking. However, they

do not eliminate the risk completely,
especially in a harsh freeze-thaw climate like Kentucky. If the concrete is already highly saturated with water, the benefits of fiber are reduced. Potential Issues

Fibers themselves can be susceptible to degradation over time, depending on the type of fiber used (e.g., some synthetic fibers can degrade in alkaline environments). The type of fiber and its degradation properties need to be considered.


Increased risk of spalling of the corners and faces of the ductbank with Freeze and Thaw issues.
3. Crack Control



Rebar's Role

Rebar is specifically sized and spaced to control crack width. Smaller, closely spaced bars are more effective at crack control than fewer, larger bars. Controlling crack width is essential for:


Durability

As mentioned above, limiting water ingress.

Structural Integrity

Preventing cracks from propagating and leading to structural failure.


Fiber's Limitation

Fibers help control crack width after a crack has already formed, but they are

less effective at preventing the initial cracking
under tensile stress. While they can distribute stresses, they don't have the same anchoring effect as rebar. Wider cracks, even if held together by fibers, still allow moisture and contaminants to penetrate.4. Code Compliance and Engineering Standards



ACI 318 (Building Code Requirements for Structural Concrete)

While ACI 318
does allow for the use of fiber-reinforced concrete in certain applications, it

does not eliminate the need for traditional rebar in many structural elements, especially those subject to significant loads or environmental exposure.
You need to very carefully review the code to ensure that a fiber-only design meets all requirements for load capacity, durability, and crack control in your specific application and location. You will likely find that rebar is still required to meet minimum reinforcement requirements. Industry Standards

Check for any relevant industry standards specific to electrical duct banks (IEEE, NEMA, etc.). These standards may have specific requirements for reinforcement.

Local Building Codes

Kentucky's building codes will likely reference ACI 318. Ensure your design complies with all applicable codes.
5.


Long-Term Performance and Maintenance



Unknowns with Long-Term Fiber Performance

The long-term performance of FRC in buried structures, especially under repeated loading and harsh environmental conditions, is still an area of ongoing research. There is less historical data and experience compared to traditional reinforced concrete.

Repair and Maintenance

Repairing damaged FRC structures can be more complex and potentially more expensive than repairing traditional reinforced concrete. Specialized techniques and materials may be required.

Why You're Not Finding Much Online Directly About Duct Banks



Duct banks are considered utilitarian structures

They're not typically the subject of extensive research or widely publicized failures. They are usually designed based on established reinforced concrete principles.

Risk Aversion

Most engineers and owners are risk-averse when it comes to buried infrastructure, especially electrical systems. The potential consequences of failure (power outages, safety hazards) are high, so they tend to stick with proven methods.


Proprietary Designs

Many duct bank designs are proprietary, and details about materials and construction methods are not publicly available.

What You Need to Do Immediately


Demand Detailed Engineering Calculations

Insist on seeing detailed structural calculations from a qualified and experienced structural engineer, specifically demonstrating that the fiber-only design meets all applicable load requirements, durability requirements, and code requirements. This should include calculations for: Bending moments and shear forces under all loading scenarios (dead load, live load, impact load). Crack width calculations. Freeze-thaw durability analysis. Reinforcement requirements based on ACI 318. Life Cycle Cost analysis, including long term maintenance.2.

Independent Review

Hire an independent structural engineer (not affiliated with the EPC) to review the design and calculations. This is crucial for getting an unbiased assessment of the risks.3.

Material Specifications

Get detailed specifications for the type of fiber being proposed, including its mechanical properties, durability characteristics, and long-term performance data.4.

Consider a Hybrid Approach

If you are open to considering FRC, explore a hybrid approach that
combines fiber reinforcement with a reduced* amount of rebar. This can provide some of the benefits of FRC (improved crack resistance) while still maintaining the necessary load-bearing capacity and structural integrity provided by rebar.5.

Full Scale Testing

If the EPC is very persistent, require them to build a small section of duct bank using their FRC design, subject it to the specified loads, and put it through a full freeze-thaw cycle.6.

Life Cycle Cost Analysis

Ask for a long-term life cycle cost analysis. Are the savings up front offset by increased maintenance costs or shorter lifespan.

In summary, while fiber reinforcement can enhance concrete performance, it is not a suitable replacement for rebar in electrical duct banks, especially in environments with freeze-thaw cycles and potential truck loading, without extremely careful engineering and a very high level of confidence in the long-term performance of the fiber material. Proceed with extreme caution and get independent expert advice.