Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Looking for megger procedure for 1,000 hp motor

User: shockking, Location: Sacramento, CA

Asked on: Monday, August 12, 2024 at 4:34 pm EDT
Answered on: Thursday, March 6, 2025 at 1:05 am EST

Question: We're helping some folks troubleshoot a 1,000 hp motor (GE 752). They were advised by a consultant that the unit could remain in service as long as the megger results are ok. We have a megger MIT515 but we're typically testing cable, we've never tested a motor like this. They're also considering adding this measurement to their regular maintenance routine. Is there a good IEEE or GE instruction for how to perform this testing? And do they need something like the MIT515 or would they get what they need with something cheaper? Any advice appreciated.

Okay, let's break down the insulation resistance testing (megger testing) of a large DC motor like a GE 752, addressing your concerns about procedures, standards, and equipment choices.

Understanding the Goal of Insulation Resistance Testing

The primary goal of a megger test is to assess the condition of the insulation between the motor windings and ground (the motor frame). Deterioration of this insulation can lead to ground faults, which can damage equipment, injure personnel, and cause downtime. Megger testing detects weakened insulation before it leads to catastrophic failure.

Is "Megger OK" Enough to Keep it Running?

This is where things get nuanced. The consultant's advice is a starting point, but it's an oversimplification. A "megger okay" result doesn't guarantee the motor is in perfect health or that other problems don't exist. Here's why: Insulation Resistance is a Snapshot

Megger testing only provides a snapshot of the insulation resistance at the time of the test. It doesn't predict future degradation.


Other Issues

Megger tests don't detect problems like winding shorts (turn-to-turn), open circuits, loose connections, mechanical issues (bearings, balance), or contamination (dirt, moisture, oil) on the windings.

Temperature Dependence

Insulation resistance is highly temperature-dependent. Results must be corrected for temperature for accurate comparison over time.


Polarization Index/Dielectric Absorption Ratio

A single megger reading at one time isn't as informative as performing a timed test to calculate the Polarization Index (PI) or Dielectric Absorption Ratio (DAR). These ratios give a better indication of insulation condition.

Therefore, a comprehensive motor maintenance program should include



Regular Megger Testing (with PI/DAR)

This is an essential part.


Visual Inspections

Look for physical damage, dirt, oil, corrosion, etc.

Bearing Temperature Monitoring



Vibration Analysis



Thermography (Infrared Scanning)

To detect hot spots.


Winding Resistance Measurements

To check for open circuits or shorted turns (requires specialized equipment).

Surge Testing

To check insulation between turns.


Motor Current Signature Analysis (MCSA)

To identify a broad range of electrical and mechanical problems.

Oil Analysis (if applicable)

In large motors with oil lubrication.

IEEE and GE Standards/Instructions
IEEE 43 - Recommended Practice for Testing Insulation Resistance of Rotating Machinery

This is the definitive IEEE standard for insulation resistance testing of rotating machinery. It covers procedures, acceptable values, temperature correction factors, and interpretation of results.

This is your primary reference.
IEEE 56 - Guide for Insulation Maintenance of Large AC Rotating Machinery (10000 kVA and Larger)

While specifically for larger AC machines, it contains useful concepts applicable to large DC motors regarding insulation degradation mechanisms and maintenance practices.


GE Instruction Manuals

If you can find the original GE instruction manual for the 752 motor (or a similar model), it may contain specific recommendations for testing and maintenance. Contact GE or look for online archives. Search for manuals related to "DC Motor Testing and Maintenance" from GE.

NEMA Standards

NEMA standards provide general guidelines for motor performance and construction, but they don't typically delve into detailed testing procedures like IEEE 43.

Performing the Megger Test (Using IEEE 43 as your guide)


Safety First!
Lockout/Tagout

De-energize and lockout/tagout the motor circuit. Verify zero voltage before proceeding.

Discharge Capacitance

Large DC motors can hold a significant electrical charge even after being de-energized. Use a suitable discharge resistor to safely discharge any stored capacitance in the windings. Follow proper discharge procedures.


Personal Protective Equipment (PPE)

Wear appropriate PPE (insulated gloves, safety glasses, etc.).2.

Preparation



Disconnect

Disconnect the motor leads from the power source and any other connected equipment. Isolate the windings you're testing. If you can isolate the armature and field windings separately, test them separately.


Cleanliness

Clean the motor exterior and connection points to remove any surface contamination that could affect the readings.

Temperature Measurement

Accurately measure the winding temperature. Use a temperature probe in contact with the windings, if possible. Otherwise, measure the ambient temperature near the motor. Accurate temperature is essential for proper correction.


Humidity

Note the ambient humidity.3.

Connections

Connect one lead of the megger to the motor winding (armature or field, as applicable). Connect the other lead of the megger to the motor frame (ground). Make sure you have a good, clean connection to the frame.4.

Test Voltage Selection (Crucial)

This is determined by the motor's rated voltage.

IEEE 43 provides voltage recommendations.
For a large motor, a 500V or 1000V test voltage is common. Refer to IEEE 43. Do NOT overvolt the insulation!5. Testing Procedure (Following IEEE 43)



Short-Time or Spot Reading Test

Apply the test voltage for a short period (e.g., 60 seconds) and record the insulation resistance reading at the end of that time. This is the simplest test, but it provides the least information.


Time-Resistance Method (Polarization Index - PI)

Apply the test voltage for 10 minutes. Record the insulation resistance reading at 1 minute and at 10 minutes. Calculate the Polarization Index (PI): PI = (Resistance at 10 minutes) / (Resistance at 1 minute)

Dielectric Absorption Ratio (DAR)

Apply the test voltage for 10 minutes. Record the insulation resistance reading at 30 seconds and at 1 minute. Calculate the Dielectric Absorption Ratio (DAR). DAR = (Resistance at 60 seconds) / (Resistance at 30 seconds)

Step-Voltage Test

Apply the test voltage in steps (e.g., 500V, then 1000V). This can help identify weak spots in the insulation. This test is more advanced and requires careful interpretation.6.

Temperature Correction

Use the temperature correction factors provided in IEEE 43 to correct the insulation resistance readings to a standard temperature (usually 40°C or 104°F). This allows you to compare readings taken at different times and temperatures.7.

Interpretation of Results (Using IEEE 43 as Your Guide)



Minimum Acceptable Insulation Resistance

IEEE 43 provides guidelines for minimum acceptable insulation resistance values based on the motor's rated voltage and horsepower. Corrected values should meet or exceed these minimums.

Polarization Index (PI)

PI > 2.0: Generally considered good insulation. PI between 1.0 and 2.0: Questionable insulation. Further investigation may be needed. PI < 1.0: Indicates significant insulation degradation. The motor should be taken out of service for repair or replacement.

Dielectric Absorption Ratio (DAR)

DAR > 1.4: Generally considered good insulation. DAR between 1.0 and 1.4: Questionable insulation. Further investigation may be needed. DAR < 1.0: Indicates significant insulation degradation. The motor should be taken out of service for repair or replacement.

Trending

The most valuable information comes from tracking insulation resistance readings (corrected for temperature) and PI/DAR values over time. A sudden drop in insulation resistance or a decrease in PI/DAR indicates a problem.8.

Discharge

After the test,
carefully discharge the motor windings before reconnecting them.9.

Reconnection

Reconnect the motor leads, ensuring proper connections and torque.

Equipment Choices: MIT515 vs. Cheaper Options
MIT515

The Megger MIT515 is a good quality, general-purpose insulation resistance tester. It is suitable for testing motors of this size, as it offers a range of test voltages. A good meter offers a wide range of voltage selection, onboard data logging, and the ability to perform timed tests for PI/DAR calculations.

Cheaper Options

Cheaper insulation resistance testers are available. However, consider these limitations:

Voltage Range

Ensure the tester provides the correct voltage range recommended by IEEE 43 for the motor's voltage.


Accuracy

Lower-cost testers may have lower accuracy.

Features

They may lack features like data logging, PI/DAR calculation, and temperature compensation.


Durability

Cheaper testers may not be as rugged or reliable in an industrial environment.

Recommendation

For regular motor testing, a meter similar to the MIT515 is a good investment. Accurate and reliable data is essential. If budget is a major constraint, ensure the cheaper meter meets the voltage requirements and accuracy standards, and be diligent with manual data recording and temperature correction.

Important Considerations



Experience

Performing megger tests and interpreting the results requires experience. If your team is not familiar with these tests, consider seeking training or consulting with an experienced motor technician.*

Documentation

Keep detailed records of all tests, including the date, time, temperature, humidity, test voltage, insulation resistance readings, PI/DAR values, and any observations.

In summary, your team should


Obtain and study IEEE 43.
2. Develop a comprehensive motor maintenance program that includes more than just megger testing.3. Use a suitable insulation resistance tester (the MIT515 is a good option).4. Follow proper testing procedures and safety precautions.5. Correct for temperature.6. Track insulation resistance, PI, and DAR values over time.7. Consult with an experienced motor technician if you have any questions or concerns.By following these guidelines, you can effectively use megger testing to assess the condition of your motors and prevent failures. Remember that "Megger OK" is just one piece of the puzzle. Flag for review

Previous Question Next Question