User: Revous, Location: NJ
Asked on: Monday, August 12, 2024 at 5:21 pm EDT
Answered on: Thursday, March 6, 2025 at 1:05 am EST
Question: I have an existing building with a 208V service that I would like to backfeed from an outside transformer. To accommodate future mechanical loads we selected a Outdoor 480V service entrance rated switchboard and a 480V to 208V transformer to back-feed the existing 208V service. We are providing the system bonding jumpers per 250.30(A)(1) Exception #2 so that we can re-use the existing feeder and system bonding jumper at the existing switchboard.In the future, we may bring in a feeder to a 480V switchboard for some mechanical equipment. Per 250.32 we need to connect the equipment grounding conductor to the grounding electrode system of a building served by an outside feeder. My understanding of 250.32 (B) (1) Exception #2 seems to be that we need to connect the EGC to the buildings GEC but by doing so we will create a parallel path in the grounding system. That means we won't be able to use 250.30(A)(1) Exception #2 and would need to run a system bonding jumper between the outside transformer and the existing 208V switchboard.Is my understanding correct or have I missed something?I created a diagram in the PDF attached of what I think the requirements of 250.32(B)(1) Exception #2 are just as a visual aid.
You've identified a critical point regarding the interaction between NEC 250.30, 250.32, and the potential for creating unintended parallel grounding paths. Let's break down your understanding and see where we can refine it
Your Understanding is Generally Correct
You're right to be concerned about the potential conflict between: NEC 250.30(A)(1) Exception #2
Allows you to reuse the existing grounding electrode system and not run a new system bonding jumper (SBJ) from the transformer if the existing 208V system already has a robust grounding electrode system and SBJ. The implicit assumption here is that this is the only connection to that grounding electrode system.
NEC 250.32(B)(1)
Requires the equipment grounding conductor (EGC) for each feeder supplying a building from an outside source to be connected to the building's grounding electrode system. 250.32(B)(1) Exception #2 says you can use the feeder EGC to connect to the grounding electrode system if you don't have a grounding electrode at the separate building. You do have a grounding electrode at the building, so that exception doesn't apply.Your diagram accurately represents the dilemma. Connecting the EGC from the future 480V feeder to the existing building's grounding electrode system will create a parallel grounding path if you maintain the original grounding scheme per 250.30(A)(1) Exception #2.
The Conflict and Resolution
The problem arises because you have two services (effectively) feeding the same building, albeit at different voltages and from the same point of origin (the outside transformer).Here's the core issue and how to address it:1. The Parallel Path
The 480V feeder's EGC, connected to the building's grounding electrode system, provides a path for ground fault current separate from the neutral conductor of the 208V service. This parallel path can lead to circulating currents, potential noise issues, and challenges with fault clearing.2.
The Solution: Embrace the "Complete" Grounding System You are correct, the best approach is to establish a comprehensive grounding system at the outside transformer. This means: Run a System Bonding Jumper (SBJ) from the neutral (X0) of the 480V-208V transformer to the enclosure of the transformer, and then to the GEC. This is in compliance with 250.30(A)(1). This is required if you are connecting the EGC of a new feeder to the building's GEC. Connect the 480V feeder's EGC to the same grounding electrode system at the transformer. Ensure the 480V switchboard has an EGC connection to the building's grounding electrode system.By doing this, you create a single, unified grounding system that satisfies both 250.30 and 250.32 while minimizing the potential for parallel paths. In your current setup you do not have a SBJ on the transformer as 250.30(A)(1) exception #2 allows you to not run a SBJ, but you lose that exemption if you have another grounded system.
Revised Strategy and Justification1. Accept that you need to run a SBJ from the outside transformer to the GEC.2. Grounding at the Transformer (Key Point)
The transformer's neutral point (X0) becomes the primary grounding point for both the 480V and 208V systems. All grounding connections converge here: The transformer's neutral is bonded to the enclosure and the grounding electrode system via the SBJ. The EGC of the 480V feeder connects to this same grounding point at the transformer.3.
480V Switchboard Grounding
The EGC for the 480V feeder is run to the switchboard.4.
The 208V Service
You are now required to install the SBJ from the transformer back to the service. This means 208V ground faults clear via the grounded conductor and SBJ.
Why This Works Single Point Ground
All grounding paths converge at the transformer, minimizing circulating currents.
Compliance
Satisfies both 250.30 and 250.32 requirements.
Safety
Ensures reliable fault clearing.
Future-Proofing
Accommodates the addition of the 480V feeder without creating grounding issues.
Important Considerations Grounding Electrode System
Ensure the grounding electrode system at the building is adequate (sufficiently low impedance to ground). This is critical for effective fault clearing.
Conductor Sizing
Size all grounding and bonding conductors according to NEC 250.66 and 250.
102.
Documentation
Document the grounding system design, including conductor sizes, connections, and grounding electrode details.*
Inspection
Have a qualified electrical inspector review the grounding system installation.
In summary, your initial instinct about the conflict was correct. By embracing a comprehensive grounding system at the transformer and ensuring all grounding paths converge there, you can create a safe, code-compliant, and reliable electrical system that can accommodate future expansion. Revising your design to include an SBJ at the transformer and properly grounding the 480V feeder will resolve the potential issues. Flag for review