Question: Hello,I have about 1000 feet of existing 10/2 for post lighting on a dedicated 20 amp breaker if I insure all new cables that I splice on to get up into the sauna tube and post are 24 inch deep in ground do I have to GFCI this circuit I really don’t want to because of tripping.Thanks
Okay, let's break down the requirements for GFCI protection and direct burial wiring to see if your plan necessitates GFCI for your post lighting circuit.
Summary
Generally, yes, you will likely need GFCI protection. The National Electrical Code (NEC) is very specific about the need for GFCI protection in outdoor lighting circuits, especially when those circuits supply outdoor receptacles. Direct burial depth alone doesn't negate the GFCI requirement. GFCI protection is important for safety.Here's a more detailed explanation
GFCI Requirements (NEC Perspective)
The NEC (National Electrical Code) requirements for GFCI protection are in place to protect people from electrical shock hazards, particularly in wet or damp locations such as outdoors.
Outdoor Lighting Circuits
The NEC (specifically NEC 210.8) requires GFCI protection for 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in readily accessible outdoor locations. Although your lights are not outlets, there is a very good chance that it will require GFCI protection. Local codes may differ, but are usually based upon the NEC.
Purpose of GFCI
GFCIs (Ground Fault Circuit Interrupters) detect current leakage to ground and quickly shut off the power, preventing electrical shock. This is crucial in outdoor environments where moisture increases the risk of a ground fault.2.
Direct Burial Wiring
Depth
Burying the cable at a depth of 24 inches is generally adequate for direct burial, based on NEC 300.5(A) Table 300.
50. However, the depth alone doesn't exempt the need for GFCI protection. Direct burial depth is related to physical protection of the cable, not electrical safety in the event of a ground fault.3.
Why GFCI Tripping Can Occur (and Solutions)
Moisture Intrusion
If you're experiencing nuisance tripping, it's likely due to a small amount of moisture getting into the wiring, connections, or the lights themselves.
Older Equipment
Older electrical equipment can sometimes be more prone to leakage.
Troubleshooting Steps
Inspect all connections
Make sure all connections are tight, well-insulated, and protected from moisture. Use waterproof wire connectors or gel-filled wire nuts specifically designed for direct burial.
Check the light fixtures
Ensure the light fixtures themselves are rated for outdoor use (wet location) and are properly sealed to prevent water intrusion.
Verify wire insulation
Check the insulation on the wire for any damage or cracks.
Use a high-quality GFCI breaker
Some cheaper GFCI breakers are more prone to nuisance tripping. Consider using a better-quality one.
Consider a GFCI deadfront
If you are still have trouble with the breaker tripping you can use a GFCI deadfront at the first pole/ light and then regular wiring up to the rest of the posts.4.
Code Compliance
Local Inspections
Always consult your local building codes and electrical inspector. They have the final say on what's required in your area. It's possible, though unlikely, that your local inspector may have a different interpretation or specific requirements.
Recommendations
Install GFCI Protection
To be on the safe side, and to likely comply with the NEC and your local electrical codes, install GFCI protection for this circuit. It's the responsible thing to do for safety.2.
Address Potential Tripping Issues
Carefully inspect and weatherproof all connections. Use high-quality, outdoor-rated fixtures and wiring. Consider using a better GFCI breaker.3.
Consult with a Qualified Electrician
If you are unsure about any aspect of this project or are experiencing persistent tripping issues, it is always best to consult with a qualified electrician. They can assess the situation, troubleshoot any problems, and ensure the installation is safe and code-compliant.
In summary, you will most likely be required to install a GFCI breaker on this circuit. You can minimize tripping by using high-quality components and making sure that the connections are water proof. Flag for review