Topic: Grounded Conductor Sizing for Parallel Feeder

User: JC_ELEC, Location: Dominican Republic

Asked on: Monday, August 12, 2024 at 9:20 pm EDT
Answered on: Thursday, March 6, 2025 at 1:06 am EST

Question: Hello, i'm a bit confused about grounded conductor sizing for parallel feeders. Nec 215.2(B) states the following:"The size of the feeder circuit grounded conductor shall not be smaller than the equipment grounding conductor size required by 250.122, except that 250.122(F) shall not apply where grounded conductors are run in parallel"So it says that 250.122(F) shall not apply for parallel runs. So, does that mean that 250.122 won't dictate the minimum neutral conductor size for a parallel run? Here is an example:In this scenario i have a 1000A 3phase Breaker in a Switchboard feeding a 1000A Panelboard. The neutral load is non-existent but the client wants a minimum sized neutral conductor (don't ask why, it's an example). The conductors sizing are as follows:- Ungrounded conductors sizing: 5 x #3/0AWG (200A) per phase = 1000A.- 5 x EMTs (one per parallel set).- Equipment Grounding Conductor: 5 x #2/0AWG EGC (per table 250.122).- Grounded/Neutral Conductor: can i size the minimum neutral conductor as 5 x #1/0AWG (minimum size for parallel neutral size per 310.10(G)(1)? Or do i have to size the neutral in each set per the minimum allowed size in 250.122 (in this case 5 x #2/0AWG)?

You've hit on a point of confusion in the NEC, and your question is perfectly valid. Let's break down the relevant sections and then apply them to your example.

Understanding the Code Sections 215.2(B)

This is the general rule for sizing feeder grounded conductors. It states that the grounded conductor (neutral) must be at least as large as the equipment grounding conductor (EGC) required by 250.122.
However, it specifically excludes 250.122(F) when dealing with parallel grounded conductors.

250.122

This section dictates the minimum size of the EGC based on the overcurrent protective device protecting the circuit. It also covers adjustments for increased size of ungrounded conductors in 250.122(B).

250.122(F)

This subsection is CRUCIAL. It addresses situations where ungrounded conductors are increased in size beyond what is needed for the load (e.g., for voltage drop). Normally, if you upsize the ungrounded conductors, you must also proportionally upsize the EGC. However,

215.2(B) specifically states that this subsection (250.122(F)) does
not apply when dealing with parallel runs.
310.10(G)(1)

This section establishes the requirements for paralleled conductors, including the minimum size of conductors (1/0 AWG).

Applying the Code to Your Example


You have a 1000A feeder protected by a 1000A breaker. You're using five sets of parallel conductors per phase. Here's how the code applies:1. EGC Sizing (per 250.122)

For a 1000A breaker, Table 250.122 requires a minimum EGC of #2/0 AWG per parallel run. So, you are correct in that you need 5 x #2/0 AWG EGCs.2.

Neutral Sizing (per 215.2(B))

Here's where the key point comes in. 215.2(B) says the grounded conductor (neutral) must be at least as large as the EGC required by 250.122, except that 250.122(F) doesn't apply to parallel runs. This is the point of confusion and the "loophole".
3.


Neutral Sizing (per 310.10(G)(1))

Because you are paralleling conductors, 310.10(G)(1) comes into play. This section requires that any conductor used in parallel be a minimum of 1/0 AWG.

The Outcome

Based on the code, you would need:

Ungrounded conductors

5 x #3/0 AWG per phase


Equipment Grounding Conductors (EGCs)

5 x #2/0 AWG

Grounded (Neutral) Conductors

5 x #1/0 AWG

Explanation of the Logic


The reason 250.122(F) is excluded for parallel runs is that the code recognizes that with multiple parallel paths, the impedance is reduced, and the fault current-carrying capacity of the ground path is inherently increased. Also, the code places a minimum size requirement for parallel conductors regardless of what load they serve, and it's intended to be installed to that spec.

Important Considerations and Best Practices
Local Amendments

Always check for local amendments to the NEC, as some jurisdictions may have stricter requirements.

Engineering Judgment

Even though the code may allow a smaller neutral in this case, it's always good practice to consider the actual load and potential future needs. If there's a possibility of significant neutral current in the future (even if it's not present now), it might be prudent to upsize the neutral conductors.


Voltage Drop

Ensure that the chosen conductor size for both the ungrounded and grounded conductors is adequate to maintain voltage drop within acceptable limits.

Coordination:
Ensure that all conductors within each parallel set are of the same length, material, conductor size, same insulation type, and terminated in the same manner.In summary, while the NEC allows* you to use #1/0 AWG neutral conductors in your parallel setup, it's crucial to understand the reasoning behind the code, consider future needs, and adhere to best practices to ensure a safe and reliable installation. If you are unsure, it's always best to err on the side of caution and use a larger neutral conductor. Flag for review