Question: Just to verify,If a shop with a concrete floor is fed with a Feeder, and, has a piece of rebar stubbed out of the concrete, but, has no metal water pipes, metal support structures, ground rings, rod and pipe electrodes or plate electrodes installed, that one rebar concrete encased electrode can serve as the sole point of contact for the grounding electrode conductor at the structure with no need for any other GEC's to be installed, correct?JAP>

You are correct, provided the rebar meets the requirements to be considered a concrete-encased electrode (CEE).Here's a breakdown and the key NEC requirements: Acceptability as Sole Grounding Electrode

Yes, a single properly sized and installed concrete-encased electrode can serve as the
sole grounding electrode system for a building or structure.

NEC 250.52(A)(3): Concrete-Encased Electrode

This section outlines the requirements for a CEE to be used as a grounding electrode. Specifically, it must be:

(a)
At least 20 ft. of bare, zinc galvanized, or other electrically conductive coated or noncoated steel reinforcing bar or rod of not less than 1/2 in. in diameter,or (b) Consist of at least 20 ft. of bare copper conductor not smaller than 4 AWG. Encased by at least 2 in. of concrete and be located within the bottom of a concrete foundation or footing that is in direct contact with the earth.

Important Considerations



20 ft. Minimum Length

The most common error is that the rebar is
not at least 20 feet long in total contact with the concrete. The stub-out you describe may only be a short piece sticking out of the floor. It's the total length encased that matters.

1/2 inch Diameter Minimum

The rebar must meet the minimum diameter requirement.

2 inches of Concrete

The rebar must have at least 2 inches of concrete surrounding it.


Contact with Earth

The concrete foundation or footing must be in direct contact with the earth.

Feeder and Service

While your question mentions a feeder, the rules are the same regardless of whether it is fed with a feeder or service.


Grounding Electrode Conductor (GEC)

You still need to connect a properly sized GEC from the service equipment to the rebar CEE. The GEC must be sized according to NEC Table 250.66.

In summary

If the single rebar stub is actually part of at least 20 feet of 1/2" or greater diameter rebar encased in at least 2" of concrete and the footing/foundation is in direct contact with the earth, and is properly connected to the service with an appropriately sized GEC, then yes, it can be the sole grounding electrode.

Caveat: It's always best practice (and sometimes required by local codes or good engineering practices) to install more than one type of grounding electrode. While a single CEE is permissible, having a supplemental electrode (like a ground rod) can improve the overall grounding system performance and provide redundancy. Flag for review