User: kingpb, Location: SE USA as far as you can go
Asked on: Tuesday, August 13, 2024 at 12:11 pm EDT
Answered on: Thursday, March 6, 2025 at 1:07 am EST
Question: If I have a 100% rated power circuit breaker (800A) feeding a MLO 800A rated panelboard. I believe I can load the panel to 800A and do not have to limit it to 640A since it doesn't have a min breaker ( or if I did it isn't 100% rated).Looking for thoughts on this.
You're on the right track, but let's break it down to ensure we're clear and covering all the bases.
Your Understanding
You have an 800A, 100% rated circuit breaker feeding an 800A Main Lug Only (MLO) panelboard. You believe you can load the panel up to 800A without applying the typical 80% derating. This is because the panel doesn't have a main breaker that isn't 100% rated, which would impose the 80% rule.
Analysis and Confirmation
Your reasoning is
correct, provided certain conditions are met. Here's a detailed explanation:1. 100% Rated Circuit Breaker
A 100% rated circuit breaker is designed and tested to carry 100% of its rated current continuously without tripping. This is a critical aspect. You must have documentation from the manufacturer verifying this rating. Not all circuit breakers are 100% rated. This is determined by testing and listing requirements found in UL 489, which covers molded-case circuit breakers.2.
MLO Panelboard
The MLO panelboard simply distributes power to the branch circuits. Since it doesn't contain a main breaker, it doesn't have an inherent overcurrent protection limitation at the panel level (other than the 800A rating itself). The overcurrent protection is provided by the upstream 100% rated breaker.3.
80% Continuous Load Rule (General): The NEC (National Electrical Code) typically requires that overcurrent devices be sized such that the load does not exceed 80% of the breaker's rating, where it is expected that the load is continuous. A "continuous load" is defined by the NEC as a load where the maximum current is expected to continue for three hours or more.4. Exception for 100% Rated Breakers
The NEC allows for 100% loading of a circuit breaker if the breaker is specifically identified as 100% rated and is used in a 100% rated enclosure. The enclosure is important because heat dissipation is a factor. This is typically covered in
NEC 210.19(A)(1) and 215.3 for branch and feeder circuits. These sections refer to limitations placed on breakers that are 100A or less. NEC 220.18(C) and 220.18(D) is more applicable for your scenario.5. Panelboard Rating
While you're focusing on the breaker, the panelboard itself has a rating (in your case, 800A). You cannot exceed the panelboard's listed and labeled rating.
Important Considerations and Caveats
Manufacturer's Instructions
Always follow the manufacturer's instructions for both the circuit breaker and the panelboard. These instructions may contain specific limitations or requirements.
Coordination Study
It's highly recommended (and often required for larger systems) to perform a coordination study. This study ensures that the overcurrent protective devices (OCPDs) are properly coordinated, so that the smallest possible area is de-energized during a fault.
Ampacity of Conductors
The conductors feeding the panel must have an ampacity equal to or greater than the load served, and not less than the rating of the overcurrent protective device (800A in your case). Ensure the conductors are properly sized per NEC Table 310.16 (or 310.15(B)(16)). You also need to account for any adjustment or correction factors.
Temperature Rating
Pay close attention to the temperature rating of the terminations (lugs) in the panelboard and the circuit breaker. NEC 110.14(C) dictates conductor ampacity selection based on these termination temperature ratings.
Enclosure type and Ambient Temperature
As stated above, your 100% rated breaker will need to be installed in a 100% rated enclosure. You will also need to consider ambient temperature, as this will affect the breakers ability to dissipate heat, therefore affecting its ability to hold the 100% rating.
In Summary:
If you have a documented, 100% rated 800A circuit breaker installed in the proper enclosure and feeding an 800A MLO panelboard, and all other NEC requirements (conductor ampacity, termination ratings, coordination, etc.) are met, then you can load the panel up to 800A. However, extreme caution is advised, and diligent verification of the 100% rating and all associated requirements is absolutely crucial.Before proceeding, consult with a qualified electrical engineer and your local authority having jurisdiction (AHJ). This is particularly important for large electrical systems. Flag for review