Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Purged enclosure sealing in CL I Div 2

User: HazLocCdn, Location: Alberta, Canada

Asked on: Tuesday, August 13, 2024 at 12:27 pm EDT
Answered on: Thursday, March 6, 2025 at 1:07 am EST

Question: I'm a Canadian familiarizing myself with NEC.Currently working on a project that will be installed in a Class I Div 2 area. I have an large enclosure I'll be entering with cable and conduit from a Class I Div 2 area exterior to the enclosure, whereas the enclosure itself will be purged to allow a GP area class. Reading through 501.15 2 Pressurized Enclosures, am I correct in interpreting that I will need conduit seals packed and poured (ie: crouse EYS type) for rigid conduit, and sealed cable glands (ie: T&B STX) for MC-HL?If this is my correct interpretation, will the seals be required to be installed on the exterior of enclosure in the Div 2 area? or would they be permitted to be install just on the inside wall of the purged enclosure?Any guidance would be greatly appreciated!

You're asking a good question that highlights some key considerations when dealing with purged and pressurized enclosures in hazardous locations. Let's break it down.

Your Interpretation of 501.15(E) 2 Pressurized Enclosures (and generally)

You are on the right track with your interpretation, but it needs some clarification. Here's a more detailed breakdown based on NEC 501.15(E) and related articles: Purpose of Sealing

The primary purpose of the seals is to prevent the migration of flammable gases or vapors from the Class I, Division 2 location into the purged/pressurized enclosure, even if the purging system fails. This is to maintain the non-hazardous classification inside the enclosure. It also prevents flammable gases from propagating through the conduit system to other areas.


Conduit and Cable Entry



Rigid Conduit

Yes, you
generally will need conduit seals (like Crouse-Hinds EYS or equivalent) unless the conduit run meets specific exceptions (see below). The seal fitting itself, its components, and the sealing compound must be suitable for the Class I, Division 2 location.

MC-HL Cable

Yes, you'll need appropriately rated sealing cable glands (like T&B STX or equivalent). These glands are designed to prevent the passage of gases or vapors through the cable interstices.

Location of the Seals


Here's where it gets very specific and depends on the enclosure's construction and listing: Crucial Point: Read the Enclosure Manufacturer's Instructions (IMI). The most important factor here is the manufacturer's instructions for the purged/pressurized enclosure. These instructions must be followed for the enclosure to maintain its listing and be compliant. The instructions will specifically state what sealing requirements are necessary. Likely Scenario - Exterior of Enclosure in Div 2

The most common requirement is that the seals be located on the outside of the enclosure, as close as practicable to the enclosure. The NEC (501.15(A)(1)) states for Division 2 locations: "Seals shall be provided in each conduit run entering an enclosure for switches, circuit breakers, fuses, relays, resistors, or similar apparatus which may produce arcs, sparks, or high temperatures that are considered to be sources of ignition in normal operation or which contain flammable liquids, and the location of such seals shall be in accordance with 501.15(A)(1)(a) through (A)(1)(e)." and 501.15(A)(1)(a) states "For raceway of 2 in. size or smaller, seals shall be located within 18 in. of the enclosure."

Rationale

This ensures that any potential leak of flammable vapors into the conduit or cable is blocked
before it reaches the enclosure's purged interior.

Possible (But Less Common) Alternative - Interior of Enclosure

If the enclosure manufacturer specifically allows for seals inside the enclosure and the enclosure is designed and tested to contain a potential explosion in the event of a purge system failure and the manufacturer's instructions explicitly allow this installation, then you might be able to install the seals inside. However, this is less typical. It would require a very robust enclosure design.

Sealing Fittings

The seals must be accessible for inspection and maintenance. You can't bury them in the wall of the enclosure where you can't access them to check and maintain them.

Important Considerations and Exceptions
Purge System Certification

Ensure your purge system is certified for the type of enclosure and the Division 2 environment.

Grounding/Bonding

Proper grounding and bonding are critical in hazardous locations to prevent static discharge.


Exception to Sealing Requirements



Continuous Gas-Tight Conduit/Cable

If the conduit run or cable is demonstrated to be
gas-tight along its entire length and enters the enclosure in an area that does not contain arcing devices, sparks, or high temperatures, the sealing requirements may be relaxed if the enclosure manufacturer allows it. However, demonstrating gas-tightness can be challenging in practice.

Intrinsically Safe Circuits

Intrinsically safe circuits have specific wiring and sealing requirements (Article 504) that may differ from standard Division 2 wiring.

Summary and Recommendations
1. Read the Enclosure Manufacturer's Instructions (IMI)

This is the most important step. Follow the manufacturer's instructions for the purge system and enclosure explicitly.2.

Assume Exterior Seals Unless Explicitly Allowed Otherwise

Default to placing the seals on the exterior of the enclosure as close as practicable unless the manufacturer's instructions specifically allow for interior seals.3.

Consult with the AHJ (Authority Having Jurisdiction)

Discuss your installation plan with the local electrical inspector before starting work to ensure compliance and address any specific local requirements.4.

Document Everything

Keep detailed records of all equipment certifications, installation procedures, and inspections.

Disclaimer:
This information is for educational purposes only. Consult with a qualified electrical engineer or hazardous location expert to ensure compliance with all applicable codes and standards. Flag for review

Previous Question Next Question