Question: I know in the 2023 NEC you can't put outlets on the ends of islands. I have a builder that builds a 2x6 wall that the island cabinets abuts to and comes up under the counter top. He is wanting an outlet to be shown in this wall. My interpretation of the code prohibits this also even if the outlet is say a foot above the floor. Am I right or would this be permitted?
You are correct, your interpretation of the 2023 NEC likely prohibits placing receptacles in that short wall section under the countertop overhang of an island. Here's a breakdown of why, and the relevant code section
NEC 210.52(C)(2): Island Countertop Receptacle Outlets
This section specifies the requirements for receptacle outlets at island countertops. The relevant portion states:"(2) Island Countertop Spaces. At least one receptacle shall be installed at each island countertop space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater.(a) At least one receptacle shall be located within 600 mm (2 ft) of the outside edge of the countertop."Why the Wall is Problematic
Wall Under Countertop is Considered Part of Island
While technically a wall, because it abuts the island cabinets, comes up under the countertop overhang, and is an integral part of the island structure, inspectors will almost certainly consider it part of the island. The intent of the code is to require readily accessible outlets at the countertop surface of the island.
Accessibility
Outlets on a low wall under an overhang are not as readily accessible as outlets on the countertop itself. People tend to use countertop receptacles for appliances like blenders, toasters, and chargers. Crouching down and reaching under an overhang to plug in appliances is awkward and less safe.
Intent of the Code
The code is designed to provide conveniently located outlets for countertop appliances. Putting them in a less-than-ideal location defeats the purpose.
Where ARE Acceptable Locations? Surface of the Countertop
This is the ideal location. Receptacles designed for countertop mounting are readily available.
Sides of the Island Cabinets
You can mount receptacles on the sides* of the island cabinets, as long as they are within 2 feet of the countertop edge and readily accessible.
In Summary
While you might be able to argue the technicality of it being a wall, the intent and spirit of the NEC, plus the practical considerations of accessibility, will almost certainly lead an inspector to reject receptacles mounted low on a wall section directly abutting the island cabinets and under the countertop overhang.
Recommendation:
Discuss this with your builder and, more importantly, with the local electrical inspector before proceeding. Explain your understanding of the code and the reasoning behind it. Get the inspector's official interpretation. This will save you time, money, and potential rework later. It's also a good idea to suggest alternative locations that comply with the code and are more convenient for the homeowner. Flag for review