Asked on: Tuesday, August 13, 2024 at 4:59 pm EDT
Answered on: Thursday, March 6, 2025 at 1:08 am EST
Question: I had the POCO here today to make the final connections to the service drop for my new service. The old bare neutral was a bit short so rather than extend it the lineman just bent it over and caught a few wraps. Does this look correct? (The old insulator was bent is being removed). The old drop connection was wrapped almost up to the drop point of attachment.And I guess things must be tight over there at the utility company. Normally they put plastic insulators over the crimps. Not today, a few wraps of tape and you're to go.
Okay, I understand your concerns. Let's break down the issues you've raised and what's considered best practice
Regarding the Bare Neutral Conductor:
Bending and Wrapping Instead of Extending
This is definitely a cause for concern. Here's why:
Compromised Connection
Bending and wrapping a conductor, especially the neutral, is not a reliable long-term connection. It can loosen over time due to weather, vibration, and expansion/contraction cycles. This can lead to a high-resistance connection.
Potential for Corrosion
The point where the conductor is bent and wrapped is susceptible to corrosion, especially if exposed to moisture and air. Corrosion increases resistance and can further weaken the connection.
Safety Hazard
A poor neutral connection can create a dangerous imbalance in voltage within your electrical system. This can damage appliances, create shock hazards, and even increase the risk of fire.
Not Best Practice/Potentially Code Violation
Electrical codes generally require connections to be made with approved methods and materials (e.g., connectors, splices). Bending and wrapping is unlikely to meet these requirements.
Correct Solution
The correct approach would have been to:
Extend the Neutral Conductor
Using a proper splicing method (e.g., a compression connector or an approved split bolt) to extend the existing neutral with a new section of conductor of the same size and material. The utility should have the appropriate tools and connectors for this purpose.
Replace the Entire Service Drop (If Necessary)
If the existing neutral was too short to allow for a proper extension, the utility should have replaced the entire service drop.
Regarding the Insulation of the Crimp Connectors
Tape Instead of Insulators
While electrical tape can be used to insulate connections, pre-molded insulators or heat shrink tubing are generally preferred, especially for outdoor applications.
Tape's Limitations
Electrical tape can dry out, crack, and peel over time, especially when exposed to UV light and weather. This can expose the connection to moisture and create a potential for arcing or short circuits.
Insulators' Advantages
Pre-molded insulators and heat shrink tubing provide a more durable and reliable barrier against the elements. They are also specifically designed for this purpose and are less likely to degrade over time.
What to Do
Contact the Utility Company Immediately
Explain your concerns about the bent and wrapped neutral conductor and the lack of proper insulation on the crimp connectors. Emphasize the potential safety hazards and the importance of a reliable connection. Request that they send a qualified lineman to correct the issues. Be polite but firm.2.
Document Everything
Take detailed photos and videos of the connections as they are now. Keep a record of your conversations with the utility company, including the dates, times, and the names of the people you spoke with.3.
Consider a Second Opinion
If you are not satisfied with the utility company's response, consider contacting a licensed electrical contractor to inspect the connections and provide a professional assessment. They can provide you with an independent opinion and can advise you on the best course of action.4.
Code Inspection (Optional)
If you are still concerned after speaking with the utility and/or an electrician, you could* contact your local building department to request an inspection. However, this is usually a last resort, as it can sometimes create friction with the utility company.
In summary, the bent and wrapped neutral conductor is not acceptable, and the lack of proper insulation on the crimp connectors is also concerning. Contact the utility company immediately to request that they correct these issues. Flag for review