Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Bonding Multiple Service Disconnecting Means - Objectionable Current

User: W6SJK, Location: New Jersey

Asked on: Tuesday, August 13, 2024 at 6:30 pm EDT
Answered on: Thursday, March 6, 2025 at 1:09 am EST

Question: Couldn't find a Mike Holt graphic for this - pardon meIn the scenario with 2 or more separate service disconnecting means, each with N-G bonding, we will have current flowing on the neutral and the enclosures / metallic raceways under normal and fault conditions, correct? Even worse if one disco is 5-10 ft away due to wall space. Never really noticed that since I always deal with service switchboards.Cheers!

You've hit on a key concept that often gets overlooked with multiple service disconnects, and your understanding is correct. Let's break down why

The Problem: Parallel Neutral Paths
Multiple Bonding Points

When you have two or more service disconnects,
each is required to have a connection to the grounding electrode system (GES) and a bond between the neutral conductor and the equipment grounding conductor (EGC) at each disconnect (250.24(C)).

Parallel Paths

This creates parallel paths for neutral current. Normal neutral current will now split and flow back to the utility transformer through: The neutral conductor. The grounding electrode conductors (GECs) connected to the grounding electrode system. Metallic enclosures and raceways which are bonded back to the EGC at the service equipment.

Voltage Drop

The current flow through the enclosures and raceways creates a voltage drop along those paths.

Why This is Undesirable


Elevated Enclosure Voltage

The voltage drop on metallic enclosures means the enclosures will have a slight voltage relative to true earth potential. Although small, this can contribute to objectionable current.2.

Increased Noise (EMI/RFI)

Current flowing on metallic raceways can induce noise into nearby sensitive electronic equipment.3.

Fault Current Distribution

During a ground fault, some fault current will take the path through the GEC, GES, and metallic enclosures back to the source instead of solely on the equipment grounding conductor. While all paths contribute to clearing the fault, the ideal scenario is for the majority of fault current to flow on the EGC back to the source.4.

Safety

The current flowing on the enclosures does not mean shock hazard but it increases the chances of someone accidently touching a fault current.

The Solution

The NEC generally discourages multiple services to a single building unless specific conditions are met. Where unavoidable, solutions like this are used:

Service Switchboards

As you mentioned, using a single service switchboard is the ideal solution. This consolidates all service disconnects into a single location, with a single N-G bond and a single connection to the GES.


Careful Planning

If multiple disconnects are truly necessary, minimize the distance between them to reduce impedance differences in the parallel paths.

Insulated/Isolated Grounding

If there are problems with multiple services, one of the solutions is to have an isolated/insulated ground. This isolates ground from the building to prevent stray currents from flowing on metallic enclosures.

Code References



250.24(C)

Grounding of Service-Supplied Alternating-Current Systems. This section specifically requires the N-G bond at each service disconnecting means.

250.6

Objectionable Current. This section addresses the potential for objectionable current flow and provides methods for mitigating it.


230.2

Number of Services. This section limits the number of services allowed to a single building.

In Summary:


You are absolutely correct. Multiple service disconnects, each with N-G bonding, will result in parallel neutral paths and current flowing on the neutral, enclosures, and metallic raceways under normal and fault conditions. While not inherently unsafe, this is generally undesirable and should be avoided where possible through careful design and planning. It's a situation where "code-compliant" doesn't necessarily mean "best practice." Using a service switchboard is the preferred approach. Flag for review

Previous Question Next Question