Topic: Does this new installation comply with 110.26(F)(1)(a)?

User: Tainted, Location: New York

Asked on: Tuesday, August 13, 2024 at 6:40 pm EDT
Answered on: Thursday, March 6, 2025 at 1:09 am EST

Question: Does this new installation comply with 110.26(F)(1)(a)? See picture below:If it does not comply 110.26(F)(1)(a), how are people in NYC getting away with this?

Okay, let's analyze the image and the NEC 110.26(F)(1)(a) code.

Understanding NEC 110.26(F)(1)(a)

This section of the National Electrical Code (NEC) deals with dedicated equipment space. Specifically, it states: 110.26(F)(1) Dedicated Equipment Space. All switchboards, switchgear, panelboards, and motor control centers shall be located in dedicated spaces and protected from damage. (a) Indoor. Indoor installations shall comply with 110.26(F)(1)(a)(1) through (F)(1)(a)(4). (1) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ductwork, or other equipment foreign to the electrical installation shall be located in this zone.In simpler terms: In the area directly above the electrical panelboard (or switchboard, etc.), from the floor up to 6 feet or the ceiling (whichever is lower), you cannot have unrelated pipes, ducts, or other non-electrical equipment. This is to protect the electrical equipment and provide clear, unobstructed access for maintenance and repairs.

Analysis of the Image

Based on the image, there are pipes/ductwork running directly in front of and above the panelboards.

ConclusionBased on the image provided, the installation in the picture
does not comply with NEC 110.26(F)(1)(a). The pipes above the panelboard would be considered "equipment foreign to the electrical installation" within the dedicated electrical space.

Why are such installations seen in NYC (or elsewhere)?

Here are the possible reasons why you might see installations like this despite the code requirements:1. Grandfathered Installations

The most likely explanation is that these installations were done
before the current NEC code cycle was adopted in NYC (or the specific jurisdiction). Electrical codes are updated every three years. If the installation predates the current code requirements, it may have been compliant at the time of installation and is "grandfathered in." However, if any significant modifications or expansions are done to the electrical system, the entire installation may be required to be brought up to current code.2.

Variances or Waivers

In some very specific circumstances, a building owner or contractor might obtain a variance or waiver from the local electrical authority. This would be granted if strict compliance with the code is impractical or impossible due to existing building conditions, and the proposed alternative provides an equivalent level of safety. Variances are not easy to obtain and are usually heavily scrutinized.3.

Limited Space and Existing Infrastructure

NYC, in particular, is known for its densely packed buildings and challenging construction conditions. Retrofitting existing buildings to meet modern code requirements can be extremely difficult and expensive. Sometimes, compromises are made, or older installations are simply left as-is unless significant renovations occur.4.

Inspection Oversight or Inconsistent Enforcement

While inspectors are responsible for enforcing the code, they cannot be everywhere all the time. Sometimes, violations slip through the cracks, especially in older buildings or during less thorough inspections. Also, the level of enforcement can vary between different inspectors and jurisdictions.5.

Lack of Awareness

Sometimes, contractors or building owners may simply be unaware of the specific code requirements.6.

Hidden during Inspections

In some cases, contractors may temporarily move or conceal the obstructing elements during inspections and then replace them afterward. This is, of course, highly unethical and illegal.

Important Considerations



Local Amendments

Remember that local jurisdictions often amend the NEC to address specific local conditions or concerns. NYC may have its own specific modifications to 110.26(F)(1)(a). You should always check with the NYC Department of Buildings or the local electrical authority to confirm the applicable code requirements.

Safety First

Even if an installation is "grandfathered in," it's essential to assess its safety. Non-compliant installations can pose risks of electrical shock, fire, and difficulty in maintaining the equipment.


Future Work:
Any new electrical work or modifications to existing electrical systems must comply with the current code.In summary, while the installation in the picture appears to violate the NEC, there are several possible reasons why it might exist. The most probable explanation is that it predates the current code requirements. However, it's crucial to verify the applicable local codes and assess the safety of the installation regardless. Flag for review