Topic: RTUs built in breakers

User: Danielinho, Location: Texas

Asked on: Tuesday, August 13, 2024 at 8:12 pm EDT
Answered on: Thursday, March 6, 2025 at 1:09 am EST

Question: I have a question that’s been on my mind all weekend. Some RTUs have a built in breaker size at 125amps, the nameplate(s) say max amps are 15a, 20a, 25a. At the electrical panel they have breakers size accordingly to the nameplate. What’s messing with my head is the 125amp built in breaker, should the built in breaker be changed to a smaller size according to the nameplate?

You're right to be questioning this! It can be confusing. Here's the breakdown of why RTUs are often designed this way and why you DO NOT typically change the built-in breaker: Purpose of the Built-In Breaker (125A in your case)

The 125A breaker inside the RTU is there to serve as the

main overcurrent protection
for
the entire unit itself. It's there to protect the RTU's internal wiring, components, and overall enclosure from catastrophic overcurrent conditions. Nameplate MCA and MOP

The Minimum Circuit Ampacity (MCA) and Maximum Overcurrent Protection (MOP) values listed on the individual nameplates of the RTU's different components (fans, compressors, heaters, etc.) are for those specific components.

Coordination

The larger breaker rating protects all the smaller components of the RTU. The smaller breakers at the electrical panel protect all equipment between the disconnect and breaker.


Manufacturer Design

RTU manufacturers design their units with specific breaker sizes to handle the potential inrush current of motors, compressors, and other components that can spike significantly during startup.

In Summary
Leave the 125A breaker in the RTU alone. It's there for a critical purpose and is sized appropriately by the manufacturer. The smaller breakers at the electrical panel are there to protect the RTU from a dead short and protect the upstream wiring.

Important Considerations Verify



Always
double-check the RTU's wiring diagram and installation manual. They will provide the most accurate and specific information for your particular model.
Qualified Electrician: If you are at all unsure, consult with a licensed and qualified electrician familiar with HVAC systems.In short, the built-in breaker is to protect the entire RTU from within. The panel breakers protect the individual components. Leave the 125A breaker alone and don't reduce its size based on the component nameplates! Flag for review