Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: THHN vs. THWN-2

User: ggunn, Location: Austin, TX, USA

Asked on: Wednesday, August 14, 2024 at 10:56 am EDT
Answered on: Thursday, March 6, 2025 at 1:10 am EST

Question: I know that this has been discussed before, but is the inside of conduit on a roof or otherwise outdoors considered a wet location, i.e., does the conditions of use derate calculation have to start with the 75 degree ampacity for THHN conductors?

This is a nuanced question with no single, simple "yes" or "no" answer. Here's a breakdown of the factors to consider and how the NEC addresses this situation

NEC Perspective & Rationale:
Article 310.15(C)(1) of the NEC (2023 and similar versions) - Ambient Temperature Correction

You are correct that this section deals with temperature derating. However, you're specifically asking if a conduit on a roof
always triggers the 75°C ampacity starting point.

Dry, Damp, or Wet Locations

The inside of a conduit is often not automatically classified as a wet location. This is a common misconception.

Wet Location (NEC Definition)

Locations subject to saturation with water or other liquids, and unprotected locations exposed to weather. Think: direct burial, car washes, some industrial processes, etc.


Damp Location (NEC Definition)

Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Think: partially protected locations under canopies, some basements, etc.

Dry Location (NEC Definition)

Location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.


Conduit as Protection

Conduit systems (especially when properly installed with sealed fittings) are designed to protect conductors from the elements. Therefore, the inside of the conduit isn't automatically assumed to be a constantly wet location.

Factors Determining if You Need to Use the 75°C Ampacity Starting Point


Conduit Type & Installation Quality



RMC/IMC (Rigid Metal Conduit/Intermediate Metal Conduit) with Threaded Connections and Sealant

If properly installed with threaded connections and sealant suitable for wet locations, these provide a high degree of watertightness. The
intent is to keep water out.

PVC Conduit with Glued Joints

Similarly, when PVC conduit is properly glued, it creates a watertight seal at the joints.

Liquidtight Flexible Metal Conduit (LFMC) / Liquidtight Flexible Nonmetallic Conduit (LFNC)

These
are often used in exposed locations and are designed to handle moisture. However, even with LFMC/LFNC, the degree of water ingress depends on the fittings used and the installation.

Poor Installation

Loosely assembled conduit, missing fittings, cracks, gaps, or improper sealing will allow moisture to enter, making it more likely the inside of the conduit will be a wet location.2.

Extreme Ambient Temperatures and Solar Exposure



Direct Sunlight on Roof

Conduit on a roof, especially a dark-colored conduit, will absorb significant heat from the sun. This can easily raise the conductor temperature well above ambient, requiring derating. This derating is based on the elevated ambient temperature,
not because the location is inherently wet.

Ambient Temperature Correction (Table 310.15(B)(1))
- This is the key. If the ambient temperature around the conduit exceeds the temperature rating of the conductor (typically 30°C or 86°F for THHN), you must apply the correction factors from this table. Note 2 to Table 310.15(B)(1)

Specifically addresses installations exposed to sunlight on rooftops: "Where conductors are installed in raceways exposed to sunlight on or above rooftops, the ambient temperature adjustment of Table 310.15(B)(1) shall be increased by 17°C (30°F)."3.

Code Enforcement Interpretation

Your local electrical inspector has the final say. Some inspectors may be more conservative and require the 75°C starting point regardless of the conduit type or installation quality, especially if the location is extremely exposed. It's best to discuss your specific installation with them beforehand to avoid surprises.

Practical Guidelines


Assume the Worst (Conservative Approach)

If there's any reasonable doubt about the watertightness of the conduit system or if it's subject to extreme temperatures, it's safer to assume the inside of the conduit will experience moisture or high heat. Start your ampacity calculations with the 75°C rating for THHN. This is generally a good practice, especially for critical circuits.2.

Best Practices for Outdoor Conduit

Use RMC or IMC with threaded connections and proper sealant for maximum protection against moisture. For PVC conduit, use high-quality glue and ensure joints are properly made. Use listed conduit bodies, boxes, and fittings suitable for wet locations. Seal conduit entries to enclosures (e.g., with sealing locknuts). Consider using a lighter colored conduit to reduce heat absorption from sunlight. Follow the 2023 NEC Note 2 to Table 310.15(B)(1) for temperature adjustment.

In summary

The inside of a conduit on a roof isn't automatically a wet location requiring a 75°C starting point. However, factors like the conduit type, installation quality, exposure to sunlight, and local inspector's interpretation all play a role. You must account for ambient temperature correction, especially considering the increased heat from rooftop sun exposure (17°C/30°F increase per NEC). When in doubt, assume the 75°C starting point to ensure a safe and compliant installation.

Recommendation:
Consult with your local electrical inspector before starting your installation. They can provide guidance specific to your local codes and conditions. Also, clearly document your assumptions and calculations to justify your design decisions. Flag for review

Previous Question Next Question