Question: What dictates the size of the bonding jumper required for Rigid Metal Conduit stubups if there are multiple involved?
The size of the bonding jumper for multiple rigid metal conduit (RMC) stub-ups is dictated primarily by NEC 250.102(C), which outlines the requirements for equipment bonding jumpers. Here's a breakdown of the key factors:1. Based on the Size of the Supply Conductors
NEC 250.102(C)(1)
The equipment bonding jumper's minimum size is based on the size of the largest ungrounded conductor (hot/phase conductor) feeding the equipment. You'll use
Table 250.102(C)(1) to determine the minimum size. This table relates the size of the ungrounded conductor to the required size of the bonding jumper. Even if each stub-up has smaller conductors, the bonding jumper size is based on the overall largest conductor feeding the equipment served by all the stub-ups.2. Increased Size if Necessary for Ground-Fault Current
NEC 250.4(A)(5)
While Table 250.102(C)(1) provides the minimum size, you must also ensure the bonding jumper is sized to adequately handle the available ground-fault current. If the calculated ground fault current is high, the bonding jumper size might need to be increased above the table minimum to ensure low impedance and effective fault clearing. Engineering calculations might be necessary in such cases.3.
Minimum Size based on Conduit Size (though often overridden by supply conductor size)
While typically not the determining factor in this specific scenario (multiple stub-ups serving an enclosure), it's worth remembering
NEC 250.102(E) mandates the bonding jumper not be smaller than what would be required for the conduit itself if used as the equipment grounding conductor (EGC). However, when multiple conduits are involved feeding an enclosure, the size is dictated by the larger supply conductor.
In Summary: Here's how to determine the bonding jumper size
Determine the Largest Ungrounded Conductor
Identify the largest ungrounded conductor supplying the equipment served by all the RMC stub-ups combined.2.
Consult Table 250.102(C)(1)
Look up the largest ungrounded conductor size in Table 250.102(C)(1) to find the minimum required size of the equipment bonding jumper.3.
Consider Ground-Fault Current
Evaluate the available ground-fault current. If it's high, perform calculations to ensure the bonding jumper size is adequate to handle the fault current effectively (low impedance path). Increase the size above the table minimum if necessary.4.
Consider other factors
Consider if there are other requirements dictating a larger bonding conductor (I.E. manufacturer requirements).5.
Install and Document
Install the bonding jumper, ensuring proper termination to both the enclosure and the grounding electrode system. Document the size and method used for sizing.
Example
Let's say you have three RMC stub-ups feeding a large electrical panel. Stub-up 1 has 3-#4/0 AWG conductors Stub-up 2 has 3-#3/0 AWG conductors Stub-up 3 has 3-#2/0 AWG conductorsThe largest ungrounded conductor is #4/0 AWG. Consulting Table 250.102(C)(1), a #4/0 AWG conductor requires a minimum bonding jumper of #6 AWG copper.
Important Considerations
Material
The bonding jumper must be made of copper or other suitable corrosion-resistant material.
Termination
Ensure proper and secure terminations to both the enclosure and the grounding electrode system. Use listed connectors or methods.
Accessibility
The bonding jumper should be accessible for inspection and maintenance.
AHJ
Always consult with the local Authority Having Jurisdiction (AHJ) for any specific requirements or interpretations of the NEC. They have the final say.
Engineering Judgement
In complex installations, especially with high available fault currents, rely on a qualified electrical engineer to perform calculations and ensure proper bonding.
Stub Up Purpose
Is the equipment bonded by the RMC itself per
NEC 250.92(A)? If so, the bonding jumper is not required.
Disclaimer: This information is for general guidance only. Always refer to the latest edition of the National Electrical Code (NEC) and consult with a qualified electrician for specific applications. Electrical work can be dangerous, and only qualified individuals should perform it. Flag for review