Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: What compound(if any) to use on 3 phase circuit breaker terminals to bus bar.

User: steve61, Location: Nebraska

Asked on: Thursday, August 15, 2024 at 9:02 am EDT
Answered on: Thursday, March 6, 2025 at 1:12 am EST

Question: I am replacing a 20 amp 3 phase circuit breaker in a 460 volt panel. I am replacing it because one of the bus bar connections had some arcing and lightly burned the bar on the breaker. Is there any compound that I should consider using on the breaker connections to the bus bar ? Thanks, Steve Wiese.

Yes, absolutely. Using an anti-oxidant compound is highly recommended when making connections to bus bars, especially with aluminum or dissimilar metals.Here's why and what to use

Why Use Anti-Oxidant Compound?
Prevents Oxidation

Aluminum (which many bus bars are made of) readily oxidizes when exposed to air. This oxidation layer is insulative and can increase resistance at the connection point.


Improves Conductivity

The compound helps break down existing oxidation and creates a better, more conductive connection.

Reduces Corrosion

It helps prevent future corrosion, especially important in environments with moisture or contaminants.


Reduces Heat Build-up

High resistance connections generate heat. A good connection minimizes resistance and reduces heat, preventing further degradation and potential failures.

Prevents Arcing

Improved connection integrity reduces the likelihood of future arcing, addressing the issue you're currently fixing.

What Compound to Use

You want an

anti-oxidant joint compound specifically designed for electrical connections.
These are typically: Copper-Based

Often contain fine copper particles suspended in a grease or petroleum-based carrier. These are good for copper-to-copper connections and aluminum-to-copper connections.

Zinc-Based

Similar to copper-based but use zinc particles. Good for aluminum-to-aluminum connections and aluminum-to-copper connections.


Aluminum-Based

These are specific for aluminum to aluminum connections.

Important Considerations when choosing a compound



UL Listing

Look for a compound that is UL listed.


Compatibility

Ensure the compound is compatible with the bus bar material (likely aluminum) and the breaker terminal material (likely copper). Read the product specifications carefully.

If you are unsure, use a compound that explicitly states it is suitable for both aluminum-to-aluminum and aluminum-to-copper connections.
Temperature Rating

Make sure the compound's temperature rating is appropriate for the panel's operating environment.

Examples of Suitable Compounds (check local availability and always verify specifications)



Ideal Noalox Anti-Oxidant Joint Compound

Very common and widely available. Typically suitable for aluminum and copper connections.

Burndy Penetrox

A popular brand, available in various formulations. Verify the specific Penetrox product is suitable for your materials.


ILSCO De-Ox

Another reputable brand of anti-oxidant joint compound.

How to Apply the Compound


De-energize and Lockout/Tagout



This is critical. Do not work on a live panel!
Verify the circuit is de-energized with a meter before proceeding.2. Clean the Bus Bar

Carefully clean the affected area of the bus bar. Use a wire brush or emery cloth to remove any remaining oxidation or burned residue. Vacuum away any debris.3.

Clean the Breaker Lugs

Wire brush or emery cloth if corrosion is apparent.4.

Apply Compound

Apply a thin, even coating of the anti-oxidant compound to both the bus bar connection point and the breaker lugs/terminals. A small acid brush or the applicator included with the compound is ideal.5.

Install Breaker

Carefully install the new breaker, ensuring a solid and secure connection. Torque the screws to the manufacturer's specifications.6.

Wipe Away Excess

Wipe away any excess compound that squeezes out during installation.7.

Re-energize

After confirming everything is properly installed and tightened, remove lockout/tagout and re-energize the circuit.

Important Safety Notes



Qualified Electrician

If you are not a qualified electrician, do not attempt this repair. Working on electrical panels can be extremely dangerous.


Personal Protective Equipment (PPE)

Always wear appropriate PPE, including safety glasses and insulated gloves.

Arc Flash Hazard

Be aware of the potential arc flash hazard when working on electrical panels.


Manufacturer's Instructions

Follow the breaker manufacturer's installation instructions and torque specifications precisely.*

Inspection:
After installation and energization, periodically inspect the connection for any signs of overheating or corrosion.By using an anti-oxidant compound and following proper installation procedures, you'll significantly improve the reliability and longevity of the connection and help prevent future problems. Good luck! Flag for review

Previous Question Next Question