Topic: Remodel Equipotential Bonding - Have to be Grid or Connected to Equipment

User: VickieKM, Location: Pleasanton, CA

Asked on: Thursday, August 15, 2024 at 10:38 am EDT
Answered on: Thursday, March 6, 2025 at 1:12 am EST

Question: Running into issues with equipotential bonding in a Bay Area City. I apologize if this has been discussed prior.They are requiring a copper grid to be installed under pavers and connected at the 4 pigtails of equal distance around the existing pool.Is it not possible to do the 4 clamps, run the copper wire around the pool and connect to equipment? Would that not be enough to keep the structural rebar grounded. Is there not an alternative than the grid to keep with the code?I ask because cost for this in our area is around $8000. Thats a lot to ask a homeowner.Appreciate any feedback!!

You're right, the copper grid requirement under pavers is a common point of contention, and $8000 is indeed a significant cost. Let's break down the situation and explore alternatives, keeping in mind this ultimately depends on the specific interpretation of the NEC (National Electrical Code) by your local Bay Area city's inspectors.

Understanding Equipotential Bonding

The goal of equipotential bonding is to create a low-impedance path between all metallic parts within and around a swimming pool. This prevents a dangerous voltage difference from arising between these parts. If a fault occurs (e.g., a short in a pool light), you want the current to flow safely back to the source, tripping the breaker, rather than potentially shocking someone in the water.

NEC Requirements (General Overview)



4 NEC 680.26(B)(1)

This section of the NEC requires equipotential bonding for conductive parts
within the pool structure itself. Typically, this involves bonding the rebar (if metallic) within the concrete shell. This is what the four "pigtails" you mentioned are likely for.

NEC 680.26(B)(2)

This section is crucial, and where the issue often arises. It requires bonding of perimeter surfaces within 3 feet horizontally of the inside walls of the pool and that are subject to wetting. This is often where the copper grid comes in.

NEC 680.26(B)(2)(a) & (b)

Allows the bonding to extend beyond 3 feet in situations where the perimeter surface is of a permanent barrier like a wall.

Why the City Might Be Insisting on the Grid



Interpretation of "Perimeter Surface"

The city inspector likely interprets "perimeter surface" very strictly to include the pavers. They may believe that without a grid, the pavers could become energized during a fault and pose a shock hazard. They may not be allowing an exemption due to permanence.

Local Amendments

Many jurisdictions, including those in the Bay Area, adopt the NEC but can also add their own amendments or interpretations. These amendments can be stricter than the national code. It is important to consult those amendments.


Liability Concerns

Cities and inspectors are often very risk-averse. If there's any ambiguity in the code, they may err on the side of caution and require the more robust (and expensive) solution.

Arguments Against the Grid (and Potential Alternatives)

Here's why the grid might be overkill and potential alternative solutions to discuss with the inspector:1.

Connection of Existing Pigtails

Your suggestion of connecting to the 4 pigtails, running the copper wire around the pool, and bonding that loop to all metallic equipment is a good starting point. This addresses the bonding of the pool structure itself. The key is to ensure this loop is effectively bonded to the rebar throughout the pool shell. Documentation (photos) of this process is vital.2.

Alternatives to a Full Grid (depending on the paver installation)



Concrete Collar

If the pavers are installed on a concrete base, you might argue that the concrete itself, if properly bonded, satisfies the "perimeter surface" requirement. This concrete would need to be bonded back to the pool's bonding grid.


Expanded Bonding Loop

Instead of a full grid, could you install a more substantial copper wire loop (e.g., larger gauge wire, multiple strands) buried under the pavers, closer to the pool's edge? This would act as a localized equipotential plane.

Steps to Take


Get the Exact Code Citation

Ask the inspector to provide the specific NEC section (and any local amendment) they are using to justify the grid requirement. This is crucial to understanding their reasoning.2.

Review Local Amendments

Thoroughly research your city's adopted electrical code, including any local amendments to the NEC. You can usually find this on the city's website.3.

Prepare a Detailed Proposal

Write a formal proposal outlining your alternative bonding solution. Include: Diagrams showing the proposed wiring layout. NEC code references that support your approach. Explanation of how your solution achieves the same level of safety as the grid. Emphasize that the pavers are non-conductive.4.

Meet with the Inspector

Schedule a meeting with the inspector to discuss your proposal. Be prepared to: Present your arguments clearly and respectfully. Listen to their concerns and address them thoughtfully. Be willing to compromise if necessary.5.

Consider a Second Opinion

If you can't reach an agreement with the initial inspector, ask if you can speak with their supervisor or another inspector for a second opinion.6.

Document Everything

Keep detailed records of all conversations, proposals, and code references. This documentation can be invaluable if you need to appeal the decision.

Important Considerations



Paver Material

The type of pavers matters. Are they concrete pavers, or are they a porous material that could become saturated with water? The more porous the pavers, the stronger the argument for some form of bonding.

Soil Type

Soil conductivity can also play a role.


Qualified Electrician

Make sure the electrician you hire is very experienced with pool bonding and knowledgeable about the NEC and local codes. They should be able to advocate for your interests with the inspector.

In summary:
While the city's requirement might seem excessive, it stems from a concern for safety. By thoroughly researching the code, preparing a well-reasoned proposal, and communicating effectively with the inspector, you may be able to negotiate a more cost-effective and acceptable solution. Good luck! Flag for review