User: inforaj, Location: Chiago
Asked on: Thursday, August 15, 2024 at 11:29 am EDT
Answered on: Thursday, March 6, 2025 at 1:12 am EST
Question: Hello everyone,Yesterday, I visited the site and noticed that the utility company had installed a new CT cabinet with a meter and the service disconnect switch in the same cabinet in the button. Additionally, the customer has installed a tapping box to connect the solar system. The maximum size of the breaker is 1200A, 480V. In this setup, the solar system is connected to the load side rather than the line side.It appears that utilities are now installing new meter cabinets that include the service disconnect switch and the CT cabinet with a meter. This is the first time I've observed this setup at two sites.My question is: How can we install the solar system on the line side rather than the load side to maximize the system size?Looking forward to your insights and thoughts.TP = Tapping boxCT= Utility CT with meter cabinetsSD=Service disconnect switchXFMR = Utility transformer.
You've correctly identified the potential limitation of a load-side tap for a solar system, especially when aiming for a larger system size. Here's a breakdown of the issue and potential solutions for connecting on the line side
Understanding the Limitation of Load-Side Taps
Load-side taps are generally easier to install but are subject to the "120% rule" in NEC 705.12(B)(2). This rule limits the combined rating of all overcurrent devices on the supply side (utility) plus all overcurrent devices on the load side (solar) feeding into a conductor to a maximum of 120% of the conductor's ampacity. In your case with a 1200A breaker, this rule severely restricts the size of the solar backfeed breaker you can install.
Why Line-Side Connection is Desirable for Larger Systems
Line-side connections, in contrast, allow for a potentially larger solar system because the solar contribution doesn't directly add to the load calculation based on the same limiting percentage. However, line-side connections come with their own challenges and require significant coordination with the utility.
Strategies for Line-Side Connection
Here are the common approaches, ordered roughly from simplest to most complex (and usually most costly):1. Negotiate a Larger Service
How it works
This involves working directly with the utility to increase the existing transformer (XFMR) and service conductors. The utility might need to upgrade their infrastructure.
Pros
Allows for a more significant increase in solar capacity. Keeps the connection simple from your perspective.
Cons
Can be very expensive, time-consuming, and depends entirely on the utility's willingness and ability to upgrade. May require substantial lead times and engineering studies.2.
Utility-Owned Switchgear/Disconnect
How it works
The utility installs a separate switchgear specifically for the solar connection before the existing CT/Service Disconnect cabinet. This is essentially a new point of service for the solar system.
Pros
Clear separation of the solar system from the customer's load. Allows for a larger solar system size based on the new point of interconnection.
Cons
Expensive, utility-controlled, and typically involves significant fees and engineering studies. Requires space for the new switchgear.3.
Dedicated Transformer for Solar (Most Complex and Costly)
How it works
The utility installs a completely separate transformer dedicated solely to the solar system. This creates an entirely independent service connection for the solar, removing any limitations imposed by the existing service.
Pros
Provides the largest possible solar capacity and complete independence from the existing load.
Cons
Extremely expensive, requires significant space, and involves the most extensive utility coordination, permitting, and potential infrastructure upgrades.
Key Steps to Take
1.
Detailed Load Study
Conduct a thorough load study of the customer's existing electrical usage. This will help you understand the customer's demand and inform the discussion with the utility.2.
Consult with a Qualified Electrical Engineer (PE)
Engage a licensed professional engineer experienced in solar interconnection. They can perform the necessary calculations, design the connection, and provide technical support throughout the project.3.
Contact the Utility Interconnection Department
This is the most critical step. Discuss your goals with the utility's interconnection team early in the process. They will have specific requirements, application procedures, and fees for line-side connections. They will determine the feasibility of different line-side options. Understand their tariff and interconnection policies inside and out.4.
Thorough Interconnection Application
Complete the utility's interconnection application meticulously, providing all required documentation and technical data.5.
Consider Parallel Operation Studies
The utility might require detailed parallel operation studies to ensure the solar system doesn't negatively impact the grid. These studies can be costly but are often mandatory.
Important Considerations
Utility Requirements Trump All
The utility's rules and regulations are paramount. They have the final say on how the solar system will connect to their grid.
Cost-Benefit Analysis
Carefully evaluate the costs associated with each line-side connection option and weigh them against the benefits of a larger solar system.
Permitting and Inspections
Line-side connections require more complex permitting and inspections than load-side taps.
In summary, while a line-side connection offers the potential for a larger solar system, it comes with significant complexities, costs, and utility coordination. The best approach depends on the specific site, the desired solar system size, and the utility's requirements and capabilities. Start by talking to the utility interconnection department to understand their rules and determine the best path forward. Flag for review