Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 690.12(C) Initiation Device Outside or Outside wall

User: darunedefig, Location: HV, New York

Asked on: Thursday, August 15, 2024 at 1:14 pm EDT
Answered on: Thursday, March 6, 2025 at 1:13 am EST

Question: Code states: "690.12(C) Initiation Device. The initiation device(s) shall initiate the rapid shutdown function of the PV system. The device “off” position shall indicate that the rapid shutdown function has been initiated for all PV systems connected to that device. For one-family and two-family dwellings, an initiation device(s) shall be located at a readily accessible location outside the building."Normally we install our main solar disconnect, rapid shutdown, on the exterior wall of the building the solar is going on next to a utility meter.I have a job where installing on the exterior wall is inconvenient and the utility meter/MSP are remote 100'+ away.Our AHJ in NY is saying "a rapid shutdown initiating device would be required on each of the buildings where the arrays are installed". I asked for where this is in the code and they sent me 690.12(C).If I am inside the building and I walk "outside the building" and I walk 20' or 100' away then I would still be "outside the building".If the code wanted the initiation device for rapid shutdown to be on the exterior wall of building or within 20' of the building then they should have said so.What is everyone else's interpretation of this?We have done plenty of jobs where placing the disconnect on the exterior wall was close to impossible and instead we had the rapid shutdown device on an exterior post mounted backboard within 10' of the utility meter and over 10' from exterior wall.I have a job coming up where the house has solar modules and the detached studio/apartment has solar modules. There is a remote meter and main service panel on a post mounted backboard off of the driveway on the way to the house and studio. There is an existing trenched rigid metal conduit from the inside of the studio to the remote meter. Plan is to run DC in metallic conduit inside the building to the SolarEdge inverters located on the same post mounted backboard as the utility meter and MSP. The studio is covered by windows on the lower level with no wall space. I think the main PV AC breaker located by meter or the SolarEdge inverters would follow the code without needing a disconnect at the studio or one for the house. The post mounted backboard by the driveway is readily accessible in my opinion. Maybe if the post mounted backboard was in the middle of the woods or 1000 ft away then that could be considered not readily accessible.

You've articulated the ambiguity in 690.12(C) perfectly. Your interpretation is a reasonable one, and many installers and AHJs have debated this same point. Here's a breakdown of the arguments and my thoughts

Arguments Supporting Your Interpretation (Remote Disconnect is Acceptable):
Literal Reading of the Code

You are correct that 690.12(C) only states "outside the building." It doesn't specify
how far outside, or that it must be attached to the building. "Readily accessible location outside the building" can reasonably include a nearby post-mounted location.

Intent of the Code

The intent of the rapid shutdown requirement is to provide firefighters and other emergency personnel with a quick and easily accessible way to de-energize the PV system. A clearly labeled, readily accessible disconnect at the main meter/service panel location achieves this goal.

Practical Considerations

As you point out, in many situations, mounting on the building wall is simply impractical or even dangerous. Requiring it in all cases ignores these realities.


Functional Equivalence

A disconnect located a short distance from the building, but at the main service location, is often more effective for emergency responders because it clearly identifies the point of disconnection for the entire PV system.

Precedent

You have successfully implemented similar solutions in the past, suggesting that other AHJs have also accepted this interpretation.

Arguments the AHJ Might Use (Disconnect at Each Building)



Safety First

The AHJ's stance is likely rooted in an abundance of caution. They might argue that a disconnect at each building ensures that local emergency responders can immediately de-energize the specific array they are dealing with, regardless of the location of the main service. They might be envisioning a scenario where firefighters are unaware of a remote disconnect.

Potential for Confusion

They might be concerned that a single disconnect at the main service could be confusing if multiple buildings have PV arrays, and emergency responders might not be clear on which arrays are de-energized.


Local Interpretation

AHJs have the right to interpret and enforce the code based on their local understanding and perceived safety needs.

Why the AHJ is Probably Being Conservative

The code language regarding rapid shutdown (especially as it has evolved in recent versions) is often subject to interpretation. AHJs are often the first line of defense in ensuring safety, and they tend to err on the side of caution. Also, there are potential liabilities if they approve an installation that later proves to be inadequate in an emergency situation.

How to Approach This with the AHJ


Formal Communication

Put your interpretation in writing. Clearly and concisely explain why you believe your proposed solution meets the intent of the code, and why it provides a safe and effective means of rapid shutdown. Include diagrams and photos to illustrate your setup.2.

Focus on Readily Accessible

Emphasize the "readily accessible" aspect. Explain how the remote disconnect is clearly labeled, easily identifiable, and accessible in all weather conditions.3.

Consider Compromise

If the AHJ is still hesitant, explore compromise solutions. Perhaps a prominent label at each building indicating the location of the main disconnect, or a remote monitoring system that allows emergency responders to verify the status of the system.4.

Appeal Process

If you cannot reach an agreement, understand the AHJ's appeal process. You may need to escalate the issue to a higher authority or obtain a formal interpretation from a qualified expert.

Regarding Your Specific Situation

Your plan to run DC conductors in metallic conduit to the inverter at the meter location is a good one. This minimizes DC voltage hazards within the building. The fact that the disconnect and inverters are located at the meter is a definite plus for accessibility.

Addressing the AHJ's Concerns



Labeling is Key

Excellent labeling is crucial. At each building with PV arrays, you need a highly visible label that clearly states something like: "PV System Rapid Shutdown Disconnect Located at [Location of Meter/Disconnect]. See main service panel for disconnect." This addresses the concern about firefighters being unaware of the remote disconnect.

Consider a Diagram

Include a weatherproof diagram near the meter/disconnect showing the layout of the PV systems on each building.*

Clear Indication

Ensure the disconnect is clearly marked as the "PV System Rapid Shutdown Disconnect" and has a visual indication (e.g., a flag) showing its status.

In conclusion:
You have a strong argument for your interpretation of 690.12(C). However, your success will depend on your ability to effectively communicate your reasoning to the AHJ and address their concerns with practical, well-documented solutions. Flag for review

Previous Question Next Question