Question: Currently doing a job at a middle school where the electrical engineer has listed taps from a 100 amp breaker from a MSB. Load is 3 different condensing units all fed from their own disconnects, one alone on a 40 amp ocpd, the other two (50A and 40A MOP) are being tapped off of a 100 amp breaker. The EE has listed that #6s shall be used for the tap conductors and it shall not exceed 10 feet. In my mind this is wrong because the total calculated load is 90A (240.21(1)(a)) there for if it’s under 10 feet of tap conductor the wire would have to be sized to 90A. If it were over 25 feet, it could be sized according to their respective disconnecting fuses (50A and 40A).The way I see it being done is; feeders are #3, tap conductors not over 25 feet but over 10’ are #6 for 50 amp fuses and #8 for 40 amp fuses landing in their respective disconnects. Does this sound about right?
You're right to question this setup. The electrical engineer's specification needs careful review. Here's a breakdown of the issues and how to approach it
Problems with the EE's Initial Design:
Oversized Breaker
A 100 amp breaker feeding a total calculated load of 90 amps is very close to being oversized. While it might technically be within the 125% rule for motors, it leaves very little room for future expansion and could lead to nuisance tripping.
Incorrect Tap Sizing
The #6 conductors might only be acceptable if the tap conductors were 10 feet or less.
Code Violation (Potential)
Taps exceeding 10 feet must terminate in a single breaker or fuse sized appropriately for that tap. This is important for safety.
Your Proposed Solution
Your solution is much more in line with good practice and NEC requirements, with a couple of points to clarify. Here's a breakdown:
Feeder Size
Using #3 conductors to the 100 amp breaker is suitable provided they are 75 degrees Celsius rated. (check the termination temp ratings)
Tap Length
The 25-foot tap rule from NEC 240.21(B)(2) is the most appropriate here.
Tap Conductor Sizing
This is where your thinking is correct, but let's refine it:
For the 50A fuse
#6 AWG copper is typically good for 55 amps, but you need to check the insulation type. If the termination temperature is 75 degrees Celsius, #6 is good for 55A.
For the 40A fuse
#8 AWG copper is typically good for 40 or 50 amps, but you need to check the insulation type. If the termination temperature is 75 degrees Celsius, #8 is good for 40A.
Important Considerations and Actions
Recalculate Load
Critically, independently verify the total calculated load for these three condensing units, adhering to NEC Article 440 requirements (air-conditioning and refrigeration equipment). This includes calculating the Largest Motor and adding the sum of the other motors at 25%. Double-check the FLA (Full Load Amps) and RLA (Rated Load Amps) of each unit on the nameplates.2.
Short-Circuit Current Rating (SCCR)
You need to verify the overall SCCR of the equipment. This will influence the type of fuses or breakers you might need to use. The SCCR of the equipment must be greater than the available fault current at the location.3.
Feeder Breaker Size
Base the feeder breaker (main 100A breaker) sizing on the calculated load according to NEC 440.22. Do not simply add up the disconnecting means. The overcurrent protection device is sized to protect the conductors.
4.
NEC 240.21(B)(2) - 25-Foot Tap Rule
This is the most likely applicable rule. All of these conditions must be met: The tap conductor ampacity is at least 1/3 of the overcurrent device protecting the feeder conductors (100A breaker). The tap conductors terminate in a single circuit breaker or set of fuses that will protect the tap conductors per their ampacity (NEC 240.4). The tap conductors are installed in a raceway or are otherwise protected from physical damage. The tap conductors do not exceed 25 feet in length.5.
Communication with the Engineer
Explain your concerns, your calculations, and your proposed solution to the electrical engineer in writing. This protects you and ensures everyone is on the same page. Use code references to back up your points. Politely point out the concerns with the original design.6.
Documentation
Keep detailed documentation of all calculations, code references, communication with the engineer, and any changes made to the original design.7.
Local Inspections
Be prepared to discuss your design with the local electrical inspector and justify your approach.8.
NEC Article 440
Thoroughly review NEC Article 440.9.
Termination Temperature
Ensure the conductors you select are rated for the termination temperature listed on the equipment.
Example Scenario (Assuming the 90A Calculated Load is Correct)
Calculated Load: 90A Feeder Breaker
A 100A breaker is reasonable in this scenario.
Feeder Conductors
#3 AWG Copper, THHN in conduit (rated for 100A at 75°C) from the 100A breaker to a junction box where the taps originate.
Taps
Unit 1 (40A Disconnect)
#8 AWG THHN (rated for 40A at 75°C) to the 40A disconnect.
Unit 2 (50A Disconnect)
#6 AWG THHN (rated for 55A at 75°C) to the 50A disconnect.*
Maximum Tap Length
Under 25 feet each.
Key Takeaway: Safety is paramount. You are responsible for ensuring the installation meets code and is safe to operate. Don't hesitate to question a design if you believe it's incorrect. Document everything. Flag for review