Topic: Standby generator wire sizing

User: Hfalz1, Location: Houston, Tx.

Asked on: Thursday, August 15, 2024 at 4:19 pm EDT
Answered on: Thursday, March 6, 2025 at 1:14 am EST

Question: I am hooking up 22kW to 26kW standby generators and I am being told that a whole wire generac cable is good for 24kW and below. The cable contains 3-#3 cu and 1-#8 cu conductor. Also it has 6- #18 cu wires for the controls. The generator has a 100A breaker and the ATS is 200A. Is this correct? It seems to me the wire would have to be larger for the feeds.

You're right to question this. Based on the information you've provided, the #3 AWG copper conductors in the Generac cable may be undersized for a 26kW generator and a 100A breaker at the generator. Let's break it down

Understanding the Problem
Generator Output

A 26kW generator, depending on voltage (240V single-phase is most common residential), can draw significant current.


Wire Ampacity

Wire ampacity is the maximum safe current a conductor can carry continuously. The ampacity of #3 copper wire depends on the insulation type and installation conditions, but let's consider common values.

Breaker Size

The 100A breaker at the generator is intended to protect the generator from overload.


ATS Size

The 200A ATS is irrelevant to the wire size between the generator and the ATS. It only dictates the wire size from the ATS to the main panel.

NEC (National Electrical Code)

All electrical installations must comply with the NEC, which dictates minimum wire sizes based on load and application.

Calculations and Considerations
1. Generator Current

Assuming 240V single-phase, a 26kW generator will output approximately:

Current (Amps) = Power (Watts) / Voltage (Volts)Current (Amps) = 26,000 W / 240 VCurrent (Amps) ≈ 108 Amps
A 22kW generator will output approximately:
Current (Amps) = Power (Watts) / Voltage (Volts)Current (Amps) = 22,000 W / 240 VCurrent (Amps) ≈ 92 Amps
2.


#3 Copper Wire Ampacity

The ampacity of #3 copper wire, as specified in NEC Table 310.16, is approximately 70-85 amps, depending on the insulation type (THHN, THWN, etc.) and the ambient temperature. Using the 75 degree celcius column of this table, it is rated for 75 amps.
3.


NEC Requirements (Simplified)
NEC 445.13 (A) requires generator conductors to be sized no less than 115% of the generator nameplate current rating. For 26kW: 108 amps 1.15 = 124.2 amps For 22kW: 92 amps 1.15 = 105.8 amps4. Analysis

Based on the 115% rating, #3 copper is

undersized
for a 26kW generator. It is questionable for a 22kW generator because it is sized very closely to the allowed amperage, leaving little to no wiggle room.

Why the Discrepancy?

The "Generac cable good for 24kW and below" statement
might be based on the following (but this is speculation and should be verified with Generac): Lower Output Current

Generac might be derating the generator's output, or basing the rating on a lower maximum continuous load. Some generators don't put out the nameplate number on a continuous basis.

Specific Installation Conditions

The cable's ampacity might be higher in specific, controlled installation conditions that are very unlikely to be met in a typical install.


Code Interpretations

There might be a specific code interpretation that allows for smaller conductors under very specific circumstances (e.g., short run lengths with adequate ventilation). This is highly unlikely to be a valid reason for using undersized wire.

Marketing/Sales

Unfortunately, sometimes marketing materials oversimplify or even bend the truth.

What to Do
1. Consult Generac Directly

Call Generac's technical support and get a written statement specifying the approved wire sizes for their 22kW and 26kW generators, considering the 100A breaker at the generator. Ask them to cite the specific code sections they are using to justify the wire size.2.

Consult a Licensed Electrician

This is the
most important step. A licensed electrician can: Perform accurate load calculations. Determine the correct wire size based on the specific installation conditions (distance, conduit type, ambient temperature, etc.). Ensure compliance with all applicable NEC and local codes. Properly terminate the wiring, which is critical for safety and performance.3.

Check the Generator's Nameplate

The generator's nameplate should clearly state its output current at the rated voltage. This is what you should use for calculations, not just the kW rating.4.

Review the ATS Installation Manual

The ATS manual will specify the acceptable wire sizes and termination methods.

Recommendations
Based on a 108A draw for the 26kW generator, #1 or even #1/0 copper conductors would likely be more appropriate. For the 22kW generator, #2 copper is likely a more appropriate option, depending on ambient temperatures. Consider using THHN/THWN-2 insulated conductors in conduit for better protection and heat dissipation.

Safety is Paramount

Undersized wiring can lead to: Overheating

This can damage the insulation and potentially cause a fire.


Voltage Drop

This can cause the generator to work harder, shorten its lifespan, and potentially damage connected appliances.*

Code Violations:
Using undersized wire is a code violation and could result in fines and the need for costly repairs.Do not cut corners on safety. Get professional advice and ensure that the wiring is properly sized and installed according to code. Flag for review