User: gulf0927, Location: Lehigh Valley, PA
Asked on: Thursday, August 15, 2024 at 5:50 pm EDT
Answered on: Thursday, March 6, 2025 at 1:14 am EST
Question: Running a 100 amp feeder underground to a shed 150 feet away. I normally install an exterior disconnect, but customer "took initiative" and already had a section of pipe installed under the foundtion which enters inside the building. Can I just install a main breaker panel? I guess I should know this already, but I've been doing it so long with the outdoor disco.
Okay, let's break down the NEC requirements and best practices for this situation. Since the pipe is entering inside the building, a main breaker panel is the correct way to go. Here's what you need to consider
Key Requirements and Considerations
NEC 225.32 - Disconnect Required for Each Building or Structure
This section generally requires a disconnecting means to be installed at each building or structure. The main breaker in your panel will fulfill this requirement, as long as it's readily accessible to the occupants.
NEC 225.36 - Suitable for Use
The disconnecting means (your main breaker) must be suitable for use as service equipment. Main breaker panels are usually rated for use as service equipment.
NEC 225.39 - Rating of Disconnect
The disconnecting means (main breaker) needs to be rated at least as high as the calculated load but never less than the feeder size. Your 100A feeder would need a 100A main breaker (or higher, if the load calculation dictates).
NEC 225.33 - Maximum Number of Disconnects
Generally, only one disconnect is allowed per building. If you install a main breaker panel, you can't have another disconnect before the panel.
Grounding and Bonding
Very Important!
NEC 250.32 - Grounding at Separate Buildings or Structures
Since this is a separate building (the shed), you'll need a grounding electrode system at the shed. This typically involves ground rods (driven at least 8 feet apart) or other approved electrodes. You will run 4 wires from the house to the shed - 2 hots, a neutral and a ground. At the house the neutral and ground will be bonded at the main panel. At the shed, you will NOT bond the neutral and ground! The neutral will be isolated and land on the neutral bus bar, the ground will land on the ground bar, and the ground bar will be bonded to the ground rods.
Overcurrent Protection
The 100A feeder conductors must be protected at their ampacity. The 100A main breaker in the panel at the shed provides this protection. Also make sure your breaker back at the main panel is sized properly for the feeder conductors.
Conductor Ampacity and Type
Make sure the conductors you are using for the feeder are rated for at least 100 amps, considering the temperature rating of the terminals in your panel and any derating factors due to burial (if applicable). THHN/THWN is a common choice for underground feeders in conduit.
Wiring Methods
Ensure your wiring method (conduit type, burial depth, etc.) meets NEC requirements for underground feeders.
Steps to Take1. Inspect the Existing Conduit
Thoroughly inspect the conduit that the customer installed. Make sure it's the correct type for underground use (typically PVC or rigid metal), has the proper burial depth, and is in good condition. If it doesn't meet code, it will need to be replaced.2.
Conductor Selection
Choose the appropriate conductors for the 100A feeder (e.g., #3 AWG copper THHN/THWN).3.
Install the Main Breaker Panel
Install the main breaker panel inside the shed where the conduit terminates.4.
Wiring Connections
Pull the conductors through the conduit from the main panel at the house to the main breaker panel at the shed. Terminate the conductors in both panels, paying close attention to torque requirements and proper labeling.5.
Grounding Electrode System
Install the grounding electrode system at the shed.6.
Bonding (Important!) Bond the grounding electrode conductor to the ground bar in the shed's main breaker panel. Do not bond the neutral.7. Testing
After installation, thoroughly test the system to ensure proper voltage, polarity, and grounding.
Important Considerations
Local Codes and Permits
Always check with your local building department for any specific requirements or permits needed for this type of installation. Local codes may be stricter than the NEC.
Load Calculation
While you're installing a 100A feeder, perform a load calculation for the shed to ensure the feeder size is adequate for the anticipated load. It's possible the customer might want to add more load in the future.
In summary: Since the conduit enters the building, installing a main breaker panel inside the shed is the correct approach. Just make sure you follow all the grounding, bonding, and overcurrent protection requirements outlined in the NEC, and that the existing conduit is compliant. Flag for review