Topic: What is acceptable for contact resistance using a DLRO?

User: 11bgrunt, Location: TEXAS

Asked on: Thursday, August 15, 2024 at 8:06 pm EDT
Answered on: Thursday, March 6, 2025 at 1:14 am EST

Question: A time crunch forced the purchase of a used Eaton 1200A frame with a 1000A trip.The existing breaker has a bad contact.A DLRO test was not provided by the vendor. An extended warranty was purchased for a 10% adder.A Vanguard AUTO-OHM 200 micro-ohmmeter was used today for bench testing the contacts.I have some DLRO experience dealing with EHV switches. The testing was set 200A with a 10 second burn in.Multiple tests were done because the cable connect points were fabricated.The average.L1 - .700 milliohmL2 - 1 milliohmL3 - 2.5 milliohmI like to focus on the Delta. The breaker handle was operated one time, and the results were not dramatically different.If experts believe these values are out of range, we can get with the vendor for an exchange.Thanks,

Okay, let's break down your DLRO results and see if they raise any red flags. Given your experience with EHV switches, you already have a good intuition for what to look for. Here's a structured analysis

1. Understanding the Context and Concerns:
Used Breaker

The key here is "used." Wear and tear are expected.


Missing Vendor DLRO

This is a significant gap in assurance. Reliance on a vendor's test report would have been ideal.

Extended Warranty

Good move. You anticipated potential issues.


Fabricated Cable Connections

This is a huge factor. Fabricated connections on your test setup can easily introduce higher-than-actual resistance readings. This is the MOST likely culprit for your elevated readings.

2. Analyzing the DLRO Results



Magnitude

The values themselves are high for a 1000A breaker. Typically, you'd expect to see values significantly lower than 1 milliohm, ideally in the hundreds of micro-ohms range for a healthy breaker, especially after burn-in.


Delta (Difference between phases)

The significant difference between phases is more concerning than the absolute values. L3's 2.5 milliohms is dramatically higher than L1's 0.7 milliohms. This suggests a potential problem unique to that phase.

3. Key Considerations & Troubleshooting (before a vendor exchange)



CONNECTION INTEGRITY (MOST IMPORTANT)



Re-evaluate your cable connections

This is the first, second, and third thing to check. Are the connections tight, clean, and making full contact? Use sandpaper to clean mating surfaces, apply a thin layer of conductive grease (like NO-OX-ID), and ensure bolted connections are torqued to spec.

Cable Size

Ensure your test leads are appropriately sized for 200A. Undersized leads will contribute to artificially high readings. Keep the leads as short as practically possible.


Cable Placement

Ensure that the test lead connections on the breaker terminals are made as directly as possible. Any loops or indirect connections can add to the resistance reading.

Burn-in Time

You used 10 seconds of burn-in. If you used the same current for each test, then this is suitable.


Multiple Tests

Good practice. Consistency between readings, after addressing connection issues, is important.

One Operation

Operating the breaker handle just once is not enough. You need to do at least 5-10 operations. This will help "scrub" the contacts and potentially reduce resistance if the issue is surface oxidation.


Ambient Temperature

Has the temperature of the breaker changed between tests? Are you sure the breaker is at ambient temperature?

Test equipment

Is your test equipment calibrated and is it verified on a shunt standard to be accurate at 200A?

4. Should You Exchange? (Recommendations)



Do NOT exchange yet!
Your fabricated cable connections are the most likely cause of the elevated readings. Do this first:1. Address the connection issue COMPLETELY. Clean and prep all surfaces, use conductive grease, torque correctly, and minimize lead length. Repeat the tests after this step.2. Operate the breaker 5-10 times between tests (after improving connections).3. If after repeating the tests after Steps 1 & 2 the Delta is still present then contact the vendor immediatelyIf, after carefully addressing the connections and operating the breaker multiple times, the DLRO readings still: Are significantly higher than expected (<1mΩ) Have a large delta between phases Are inconsistent

then: Immediately contact the vendor. The extended warranty exists for a reason. Explain your testing methodology, your concerns about the phase imbalance, and provide them with your DLRO data. Request either a replacement breaker OR a detailed DLRO test report from their lab, performed on the actual breaker you're considering keeping. This is critical.

In summary:

Your DLRO results are concerning, but not definitive until you eliminate your cable connections as a variable. Focus on connection integrity and perform multiple operations. Only then can you make an informed decision about whether to pursue an exchange. Good luck! Flag for review