Topic: Hub Bushing

User: Alwayslearningelec, Location: NJ

Asked on: Friday, August 16, 2024 at 10:53 am EDT
Answered on: Thursday, March 6, 2025 at 1:16 am EST

Question: So this has a locknut on it but no bushing. Is a sperate bushing required? I assume no beccasue it has an insulated throat?

You are likely correct. If the fitting has an insulated throat, it usually means a separate bushing is not required for protection of conductors. The insulated throat provides the necessary smooth and rounded surface to prevent damage to the wire insulation.Here's a breakdown of why: Purpose of Bushings

Bushings are primarily used to provide a smooth, rounded entry point into an enclosure to protect wire insulation from sharp edges that could be present on conduit or fittings.


Insulated Throat Fittings

These fittings are designed with a pre-installed insulated throat that serves the same purpose as a separate bushing. This insulation covers any sharp edges that would otherwise pose a threat to the wire.

Locknut function
The locknut serves to secure the fitting to the electrical box or enclosure.

When You
Would Need a Bushing (Even with a Locknut)



Damaged Insulation

If the insulation on the fitting is damaged or missing, you would need a separate bushing.

Larger Conductors

For larger conductors with a higher voltage you may need a bushing (check with your local code)


Specific Code Requirements

While unusual, there might be very specific local code requirements that supersede the general practice.*

If you're unsure,
it's always best to consult the National Electrical Code (NEC) or your local electrical inspector to ensure compliance.

In summary, if the fitting you have has an intact, properly designed insulated throat, you most likely do not need a separate bushing. Double-check the condition of the insulation and consult local codes if you have any doubts. Flag for review