User: jes25, Location: Midwest
Asked on: Friday, August 16, 2024 at 2:36 pm EDT
Answered on: Thursday, March 6, 2025 at 1:16 am EST
Question: Around here (Detroit), industrial customers often have medium voltage services. In the newer areas, the utility distribution is 13.2. My understanding is that this is a wye service. From what I observe on the pole, the utility is giving customers 3 phase wires with a concentric neutral. This makes sense to me as far as grounding/ bonding go. Essentially, this is no different than a 480/277 utility service. The concentric neutral would be the fault clearing path back to the center of the utilities wye. The customer owned medium voltage gear would be bonded to the grounded conductor like a CT cabinet in a 480/277 service. Am I thinking correct so far?In the legacy areas, customers get 4800 volt services. I understand this to be a Delta configuration. I don't understand how the grounded conductor works on these systems. Is a system like this typically corner grounded? Ungrounded? Where would the main bonding jumper be installed? I don't get it.
You're on the right track with your understanding of the 13.2 kV wye system! Your comparison to a 480/277V service is accurate in terms of grounding and bonding principles.Let's break down the 4800V Delta service, which is where things get more complicated
4800V Delta Systems - Options and Considerations
The key to understanding the 4800V Delta service is recognizing there are a few different ways it could be configured, and the grounding implications are drastically different. Corner Grounded Delta
How it Works
One of the phase conductors (let's say Phase B) is intentionally connected to ground at the service entrance.
Grounded Conductor
Phase B acts as the grounded conductor.
Fault Clearing Path
Fault current returns to the source through the grounded Phase B conductor.
Bonding
The main bonding jumper is connected from the grounded Phase B conductor to the service equipment enclosures, grounding electrode system (ground rods, water pipe, etc.), and any metal raceways.
Characteristics
Simpler and less expensive than other systems. Can present safety hazards if personnel are not aware of the corner-grounded configuration. Voltage from Phase A to ground and Phase C to ground will be the full 4800 volts. Can be prone to transient overvoltages.
Ungrounded Delta
How it Works
No phase conductor is intentionally connected to ground at any point. The only connection to ground is through stray capacitance.
Grounded Conductor
There is no grounded conductor.
Fault Clearing Path
There is no dedicated fault clearing path in the event of a single line-to-ground fault. Instead, the voltage on the other phases rises and the system can operate for a short period of time until the fault is located and cleared.
Bonding
The service equipment enclosures and metal raceways are connected to the grounding electrode system. However, there's no main bonding jumper in the traditional sense, because there is no grounded conductor.
Characteristics
Offers the advantage of continued operation in the event of a single ground fault. However, a second ground fault on another phase will create a phase-to-phase short circuit. Can be difficult to troubleshoot ground faults. Can be subject to transient overvoltages. Typically requires a ground detection system to alert maintenance personnel to a ground fault.
Delta with a High-Leg (or "Wild Leg") How it Works
One phase of a delta winding is center tapped, and that center tap is grounded. This creates two voltages to ground.
Grounded Conductor
The center tap of one phase.
Fault Clearing Path
The grounded conductor provides the fault clearing path.
Bonding
The main bonding jumper is connected from the grounded conductor to the service equipment enclosures, grounding electrode system (ground rods, water pipe, etc.), and any metal raceways.
Characteristics
Provides the advantages of both a single phase and three phase service. Phase A and C will have a voltage to ground that is one half of the phase to phase voltage. Phase B (the high leg) will be approximately 1.73 times the phase to ground voltage of Phase A and C. The high leg must be identified and marked at every termination point in the system.
How to Determine the Grounding Configuration
Since these grounding schemes each present different issues, it's important to know which system you have. Here's how you can determine the grounding configuration of a 4800V Delta service:1. Consult the Utility
This is the best and most reliable method. The utility knows exactly how they've configured the service. Contact them directly and ask for details about the grounding configuration, impedance, and fault current availability.2.
Check Existing Documentation
Look for one-line diagrams, relay coordination studies, or any other documentation that might indicate the grounding configuration.3.
Voltage Measurements (with extreme caution!)
Only qualified personnel should perform these measurements. Using a high-impedance voltmeter, measure the voltage from each phase conductor to ground.
Corner Grounded
One phase will read approximately 0 volts to ground. The other two phases will read 4800 volts to ground.
Ungrounded
All three phases will read roughly the same voltage to ground. The voltage will fluctuate if a ground fault is present.
Delta with a High-Leg
Two phases will measure half the phase-to-phase voltage to ground. One phase (the high leg) will measure approximately 1.73 times the phase to ground voltage of the other phases.
Where to Install the Main Bonding Jumper
The location of the main bonding jumper depends entirely on the grounding configuration: Corner Grounded Delta
The main bonding jumper connects the grounded phase conductor to the service equipment enclosure, grounding electrode system, and metal raceways at the service entrance.
Ungrounded Delta
There is no main bonding jumper in the traditional sense.
Delta with a High-Leg
The main bonding jumper connects the center tap of the phase winding to the service equipment enclosure, grounding electrode system, and metal raceways at the service entrance.
Important Considerations for Medium Voltage Services Qualified Personnel
Working with medium voltage requires specialized training and equipment. Only qualified personnel should perform installations, maintenance, and troubleshooting on these systems.
Coordination Studies
Ensure proper coordination of overcurrent protective devices (fuses, circuit breakers, relays) to minimize the extent of outages and protect equipment.*
Safety
Always follow strict safety procedures when working with medium voltage, including lockout/tagout procedures and the use of appropriate personal protective equipment (PPE).
In summary:
While your understanding of the 13.2 kV wye system is correct, the 4800V Delta service presents more complexity due to its different grounding options. It is essential to determine the specific grounding configuration from the utility and follow the applicable codes and standards for grounding and bonding. Always consult with qualified engineers and electricians when working with medium voltage systems. Flag for review