Topic: Unexplained heating on feeder conductors

User: pct2607, Location: Huntsville Alabama

Asked on: Friday, August 16, 2024 at 3:12 pm EDT
Answered on: Thursday, March 6, 2025 at 1:16 am EST

Question: We were called out to a customer's site today and found that all four sets of the feeder conductors of a 1200A service have been overheating and melting away the insulation. It appears that it was torqued because of the sharpie mark on the bolt and when my guys took it apart the nuts were tight. First glance tells me that it maybe that each crimp does not appear to have been compressed correctly, but again I'm not 100% sure. We are in the process of getting this repaired and will monitor the load for several days. Has anyone seen this before?Thanks,Peter

Peter,You're right to be concerned and meticulous in diagnosing this situation. Overheating feeders on a 1200A service is a serious hazard. Here's a breakdown of potential causes, further investigation steps, and what others might have seen in similar situations

Likely Causes (beyond just bad crimps):
Crimp Connection Problems



Incorrect Die/Tool Combination

Using the wrong die size for the conductor or a non-compatible crimping tool is a frequent culprit. Crimps can look okay externally but be poorly connected internally.

Improper Crimp Technique

Overlapping crimps, too few crimps, or improper crimp placement (e.g., too close to the lug barrel end) can compromise the connection.


Damaged Crimp Tool

Worn or damaged crimping tools don't deliver consistent pressure. This is especially common with hydraulic crimpers if they haven't been calibrated.

Oxidation/Corrosion

Even with a good crimp, oxidation or corrosion between the conductor strands and the lug can significantly increase resistance over time. This is more prevalent in damp or corrosive environments. Was anti-oxidation compound (e.g., Noalox, Penetrox) used during installation?


Wrong Lug Material

Using aluminum lugs on copper conductors (or vice-versa) without proper bimetallic considerations is a recipe for corrosion and eventual failure.

Loose Connections (Despite Tight Nuts)



Thermal Cycling

Conductors heat up under load and cool down when the load decreases. This thermal cycling can cause the metal to expand and contract, gradually loosening connections even if they were initially torqued correctly. The fact that the nuts were still tight doesn't necessarily mean there wasn't a period of looseness during the thermal cycling.

Surface Imperfections

Small imperfections on the busbar, lug mating surface, or washers can prevent a truly solid connection, even with proper torque. These imperfections can increase resistance.


Incorrect Hardware

Using the wrong type of washers (e.g., flat washers instead of Belleville washers) can reduce the effectiveness of the torque.

Overloading



Actual Load vs. Calculated Load

Is the actual load on the service exceeding the calculated load? It's possible the initial calculations were incorrect, or new equipment has been added without recalculating the service requirements.

Harmonic Currents

Non-linear loads (e.g., variable frequency drives, LED lighting, UPS systems) can generate significant harmonic currents. These harmonics don't show up on a standard ammeter but can cause overheating of conductors and equipment.


Voltage Imbalance

A significant voltage imbalance across the phases will lead to uneven current distribution and potential overloading of specific conductors.

Conductor Issues



Undersized Conductors

Although unlikely on a 1200A service, double-check that the conductors are sized correctly for the load and ampacity requirements, considering ambient temperature and derating factors.

Damaged Conductors

Nicks, cuts, or kinks in the conductor can reduce its current-carrying capacity and create hotspots.


Environmental Factors



High Ambient Temperature

If the service is located in a hot environment, the conductors' ampacity will be reduced.


Poor Ventilation

Lack of ventilation can trap heat and exacerbate overheating problems.

Corrosive Environment

As mentioned earlier, corrosive environments can accelerate oxidation and degradation of connections.

Investigation Steps


Detailed Crimp Analysis



Cut Open and Inspect Crimps

Cut open several of the crimped lugs and examine the inside of the connection. Look for voids, corrosion, incomplete compression, and any signs of arcing. Photograph everything clearly.

Verify Tool and Die

Confirm that the correct crimping tool and die combination was used by reviewing records and examining the tool markings.


Crimp Technique

Interview the installer to understand their crimping technique.

Lug Quality

Verify the lugs are UL-listed or otherwise meet appropriate standards.2.

Torque Verification



Re-torque Connections

After cleaning and inspecting the busbar and lug surfaces, re-torque all connections to the manufacturer's specifications using a calibrated torque wrench.

Use Belleville Washers

Consider using Belleville washers to maintain constant pressure and compensate for thermal expansion/contraction.


Anti-Oxidation Compound

Apply anti-oxidation compound to all mating surfaces during reassembly.3.

Load Monitoring



True RMS Ammeter

Use a true RMS ammeter to measure the current on each phase over a period of several days, capturing peak and average values.


Harmonic Analysis

If you suspect harmonic currents, use a power quality analyzer to measure the harmonic content of the current.

Voltage Balance

Check the voltage between each phase and neutral to identify any voltage imbalances.4.

Infrared Thermography



Before and After Repair

Perform infrared thermography scans before and after the repairs to identify hotspots and verify the effectiveness of the repairs.5.

Service Load Calculation Review



Verify Initial Calculations

Re-evaluate the service load calculations to ensure they are accurate and account for all connected loads, including future expansion.6.

Conductor Inspection



Check Conductor Size

Verify the conductor size against the NEC ampacity tables, considering derating factors.

Inspect for Damage

Visually inspect the conductors for any signs of damage (nicks, cuts, kinks).7.

Environmental Assessment



Ambient Temperature

Measure the ambient temperature in the service area.

Ventilation

Assess the ventilation to ensure adequate airflow.

What Others Have Seen

"We had a similar issue on a 2000A service. The crimps looked okay externally, but when we cut them open, we found significant voids and corrosion inside. It turned out the installer was using an old, uncalibrated crimping tool with the wrong dies." "We found that harmonic currents from a large bank of VFDs were causing overheating in the neutral conductor, even though the service was not overloaded according to a standard ammeter." "We had a case where the lugs were aluminum and the busbar was copper. The connection looked tight, but corrosion had created a high-resistance joint." "Sometimes the busbar itself can have surface imperfections that prevent a solid connection. Polishing the busbar before reassembly can help." "Make sure you're using the correct torque values for the bolt size, material, and hardware. Under- or over-torquing can both lead to problems." "I’ve seen where undersized neutral conductors cause overloading and overheating when there are a lot of single phase non-linear loads. With modern electronics this is happening more and more often."

Important Considerations



Safety First

De-energize the service before performing any work. Use proper PPE.

Documentation

Thoroughly document all findings, repairs, and measurements. This will be valuable for future troubleshooting and warranty claims.


Professional Expertise

If you're not confident in your ability to diagnose and repair this problem, consult with a qualified electrical engineer or a specialized electrical contractor.*

Training:
Ensure your team receives proper training on crimping techniques, torqueing procedures, and the importance of using the correct tools and materials.This is a complex issue, and a thorough investigation is crucial. Good luck with the repair, and please let me know if you have any other questions. Flag for review