User: Mr. Pickle, Location: Rogers MN
Asked on: Friday, August 16, 2024 at 9:03 pm EDT
Answered on: Thursday, March 6, 2025 at 1:17 am EST
Question: Working with a client on an underground vault. They are concerned about condensation in conduits, because they have had this issue in the past at other vaults. They are requesting to have conduit drains that have tubing ran to a floor drain. I can't find anything like this. Anyone know of such a product or application? Is this even acceptable under the NEC?We have tried to explain to them that if the conduit is properly sealed there would be no condensation. They don't want to hear it; they want a conduit drain. Only way around this that I can see is if the NEC doesn't allow such an installation, or there is no such product even made.If there is a product, I would be OK installing it, I just never heard or seen of such an install.
You're in a tough spot. You're facing a client's insistence on something that is, at best, unorthodox and potentially problematic. Let's break down the issues and explore potential solutions, keeping NEC compliance in mind.
The Problem: Condensation in Underground Conduits The Physics
Condensation occurs when warm, moist air comes into contact with a cold surface. In underground vaults, temperature differences between the soil and the vault air can lead to moisture forming inside the conduit. This is exacerbated by "breathing" – air movement in and out of the conduit due to temperature and pressure changes.
Why It's Bad
Water in conduits can corrode conductors and equipment, lead to ground faults, and eventually cause failures.
Why Conduit Drains are Problematic (and likely NEC Violations)
Compromised Seal
The core principle of preventing condensation is sealing the conduit system to minimize air exchange. Installing drains inherently creates a path for air and moisture to enter, defeating the purpose of sealing.
Foreign Substances
Drains introduce the risk of debris, dirt, and insects entering the conduit system.
Grounding Issues
Depending on how the drain system is implemented, it could unintentionally create a grounding path, leading to potential fault currents and safety hazards.
Siphon Effect
The tubing to the floor drain could create a siphon, constantly drawing moisture from the conduit, even when it's not condensing.
NEC Concerns
300.15(H) Raceways Exposed to Different Temperatures
NEC requires sealing where raceways enter enclosures from an area of higher temperature. Drains would likely violate this.
300.7(A) Raceways Exposed to Different Temperatures
This section requires sealing or other means to prevent circulation of warm air to a colder section of the raceway.
314.15 Damp or Wet Locations
Outlet boxes in damp locations must be placed or equipped to prevent moisture from accumulating. Adding a drain is not an approved method.
Likely unlisted
A field fabricated drain assembly would likely not be listed for its intended use.
Alternatives and Explanations to Give Your Client1. Emphasize Proper Sealing
Detailed Sealing Plan
Present a clear, written plan for sealing the conduits. Specify the type of sealant, locations for sealing (both ends of the conduit, at the vault entry, and at termination points in equipment), and the installation procedure. Use UL-listed sealing fittings and compounds.
Pressure Testing
Suggest pressure testing the installed conduit system (before backfilling, if possible) to verify the seals are effective. You can use a simple air pressure test with a gauge.
Seal-offs
Use explosion proof seal-offs if required per code.2.
Temperature Management in the Vault
Ventilation
Controlled ventilation can help regulate the temperature and humidity inside the vault. Consider a ventilation system that brings in outside air (filtered) only when the inside temperature and humidity are within acceptable ranges.
Insulation
Insulating the vault walls and roof can minimize temperature fluctuations and reduce condensation.
Heating
A small, thermostatically controlled heater can prevent the vault temperature from dropping below the dew point.3.
Conduit Material
PVC
Schedule 80 PVC conduit is a good option for underground runs.
RMC (Rigid Metal Conduit) with Proper Coatings
If RMC is used, ensure it has a high-quality coating (galvanized or epoxy) to prevent corrosion. Internally coat the conduit with a corrosion inhibitor.4.
Cable Selection
Wet-Rated Conductors
Ensure all conductors used are rated for wet locations (e.g., THWN, XHHW).5.
Documentation and "Doing Your Best"
Written Explanation
Provide a written explanation to the client outlining the reasons why conduit drains are not a standard practice, potential code violations, and the alternative methods you recommend.
Get it in Writing
If the client still insists on the drains, get a written directive from them stating that they understand the potential issues and are directing you to install the drains against your professional advice. This helps protect you from liability. Consult with your company's lawyer.6.
Consider a Mock-Up (If the Budget Allows)
If the budget allows, consider creating a small-scale mock-up of a conduit run with your proposed sealing methods. You can then subject it to temperature and humidity cycling to demonstrate its effectiveness.
If the Client Absolutely Insists on a Drain (Last Resort and with Extreme Caution)
Important: Only proceed if the client provides written direction after you've thoroughly explained the risks and NEC concerns. Consult with a Licensed Electrical Engineer
Before attempting any type of drain system, consult with a licensed electrical engineer experienced in underground electrical systems. They can help design a system that minimizes risks and potentially meets code requirements (though this is unlikely).
Use Listed Components (Highly Unlikely)
Thoroughly research if any manufactured drain assemblies are listed for this specific purpose. It is highly unlikely, but a listed product is more likely to be compliant.
Proper Grounding and Bonding
Ensure any metallic components of the drain system are properly grounded and bonded to the electrical system's grounding electrode system to prevent potential fault currents.
Backflow Prevention
Incorporate a backflow prevention device in the drain line to prevent sewer gases or water from entering the conduit.
Regular Inspection and Maintenance
Emphasize the need for regular inspection and maintenance of the drain system.
How to Handle the Conversation with the Client
Listen Empathetically
Acknowledge their concerns and past experiences. "I understand you've had problems with condensation in the past, and you want to prevent that from happening here."2.
Explain the Science
Clearly explain the physics of condensation and how proper sealing prevents it.3.
Present the Alternatives
Offer the alternative solutions (sealing plan, temperature management, etc.) and explain their benefits.4.
Address Their Concerns Directly
"I know you're concerned about water in the conduits. With our sealing plan, we are confident that we can prevent condensation from forming in the first place. Adding a drain could actually make the problem worse by introducing a path for moisture to enter."5.
Be Firm on NEC Compliance
"As a licensed electrical contractor, I am obligated to follow the National Electrical Code. Conduit drains are not a standard practice, and I'm concerned that they could violate several code sections."6.
Document Everything
Keep detailed records of all communications with the client, the explanations you provided, and their directive (if they insist on the drains).
In Summary: Conduit drains are generally a bad idea and likely violate the NEC. Focus on proper sealing, temperature management, and using appropriate materials. If the client insists on a drain, get it in writing, consult with an engineer, and proceed with extreme caution. Prioritize safety and code compliance.It's a delicate balance between meeting your client's needs and upholding your professional responsibility. Good luck! Flag for review