Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Existing Electrical Room now surpassing 1000 KVA

User: Grouch1980, Location: New York, NY

Asked on: Friday, August 16, 2024 at 9:07 pm EDT
Answered on: Thursday, March 6, 2025 at 1:17 am EST

Question: For those in the NYC area... we're looking at adding a new Service Switch to an existing electrical room, in NYC. The addition of this switch will push us over 1000 KVA. The electrical room doesn't meet all the requirements put forth by the EPR board. There's only 1 means of egress, and there isn't 5 feet of clearance in front of any Service Switches.How does one tackle this? If we add the new Service Switch, just make sure there's 5 feet of clearance in front of that switch only? Does everything else in the room stay the same?

Okay, this is a significant issue in NYC, given the strict enforcement of electrical codes and regulations by the Electrical Plan Review (EPR) Board. Here's a breakdown of how to approach this, including the likely challenges and necessary steps

Key Considerations & Problems:
Exceeding 1000 kVA

This is the trigger point that brings into play more stringent requirements for the electrical room, according to NYC Electrical Code and related regulations.


Non-Compliance with Existing Room

The existing room lacking proper egress and clearance is a pre-existing problem that will be amplified by the increased capacity.

EPR Board Scrutiny

Adding a new service switch above 1000 kVA will
definitely trigger a review by the EPR Board during permitting. They are very thorough, and they will require the entire room to be brought up to code.

Safety First

Non-compliance with clearance and egress requirements poses serious safety risks for electricians and emergency personnel.

Steps to Take


Engage a Licensed Professional Engineer (PE) with NYC Electrical Experience

This is absolutely critical. You need a PE experienced in navigating the NYC electrical code, EPR Board submissions, and utility (Con Edison) requirements. This is your first and most important step. They can assess the situation, develop a compliant design, and act as your advocate with the city. Don't try to do this without a qualified PE.2.

Detailed Site Assessment & Load Calculation

The PE will conduct a thorough assessment of the existing electrical room, including dimensions, equipment layout, ventilation, fire rating of walls/doors, and the existing and proposed electrical loads. An accurate load calculation is crucial.3.

Code Compliance Review

The PE will review the current NYC Electrical Code (likely based on the NEC with NYC amendments) and relevant regulations to identify all areas of non-compliance, focusing on:

Egress Requirements

NEC and NYC Code dictate the number and location of egress doors based on room size and equipment arrangement. Two means of egress might be required with separation, and appropriate fire-rated doors with panic hardware.


Working Clearance

This is probably your biggest hurdle. 5 feet of clearance is the bare minimum in many cases, and depending on the voltage and equipment configuration, it could be significantly more. The code specifies clear working space in front of electrical equipment based on voltage and whether the equipment is dead-front or has exposed live parts.

Headroom

Minimum headroom is required above working spaces.


Dedicated Space

The 2017 NEC article 110.26(E) dictates a dedicated space above and below the equipment that must be clear. This often causes the most issues.

Illumination

Adequate lighting is required for safe working conditions.


Ventilation

The room needs adequate ventilation to dissipate heat generated by the electrical equipment.

Fire Resistance

The room may need to have a specific fire-resistance rating, especially if it is adjacent to other occupancies.


Signage

Proper warning signs and equipment labeling are required.4.

Develop Solutions & Design Options

Based on the code review and site assessment, the PE will explore potential solutions. This may involve:

Room Expansion/Relocation

The most straightforward (but often most expensive and disruptive) option is to expand the electrical room or move it to a larger space that can meet the requirements.


Equipment Relocation

Rearranging existing equipment to maximize clearance. This might involve moving other equipment out of the room or consolidating equipment.

Equipment Replacement

Consider using more compact or rear-accessible equipment.


Variance Request (Last Resort)

In some cases, if strict code compliance is impossible due to physical constraints, the PE can explore the possibility of requesting a variance from the EPR Board. This is difficult and requires a very strong justification demonstrating equivalent safety. Documentation is crucial.

Fire Suppression

In some situations, installing a fire suppression system might be required to help mitigate the fire risk in a space that doesn't meet all the code requirements.5.

Permitting and EPR Board Submission

The PE will prepare the necessary permit drawings and documentation for submission to the NYC Department of Buildings (DOB) and the EPR Board. This includes:


Detailed Electrical Drawings

Showing the existing and proposed electrical systems, equipment layout, clearances, egress paths, ventilation, and other relevant details.

Load Calculations

Demonstrating the electrical load and compliance with demand factors.


Code Compliance Narrative

A written explanation of how the design complies with the applicable codes and regulations.

EPR Board Submission Package

This is a specific set of documents and forms required by the EPR Board.6.

EPR Board Review and Approval

The EPR Board will review the submission. They may request clarifications or revisions. The PE will attend meetings with the EPR Board to answer questions and advocate for the design.7.

Construction and Inspection

Once the permit is approved, you can proceed with the electrical work. A licensed electrical contractor must perform the installation. The work will be inspected by the DOB and potentially Con Edison.

Specific Answers to Your Questions



"If we add the new Service Switch, just make sure there's 5 feet of clearance in front of that switch only?"
No. This is highly unlikely to be acceptable. The EPR Board will almost certainly require the entire room to be brought into compliance with the code, given the increased capacity. "Does everything else in the room stay the same?" Almost certainly not*. The lack of egress and inadequate clearance are pre-existing deficiencies that will be flagged.

In summary: Adding a service switch that puts you over 1000 kVA in a non-compliant electrical room in NYC requires a comprehensive approach. Start with a qualified PE, be prepared for a thorough review by the EPR Board, and anticipate potential costs associated with upgrading the entire room to meet current code requirements. Don't underestimate the complexity and importance of this project. Flag for review

Previous Question Next Question