Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Continuity

User: guschash, Location: Ohio

Asked on: Saturday, August 17, 2024 at 8:45 am EDT
Answered on: Thursday, March 6, 2025 at 1:17 am EST

Question: I had to check some work being done at church, so I started at the lighting panel . It was being fed from QMB panel. So being fed from this QMB panel would make this a sub panel. So I had them remove the bar tiring together the neutral and ground bar. I check with my and I still had continuity between them. Is this right, I would expect them to be separate.

Okay, let's break this down to understand what you observed and what might be happening. You're right to be cautious and investigate further.

Understanding the Setup QMB Panel

This is likely the main electrical panel providing power to the church. Think of it as the central distribution point.


Lighting Panel

This panel fed from the QMB is indeed a

subpanel
.

Why Separating Neutrals and Grounds in a Subpanel is Crucial Safety

The primary reason for separating neutrals and grounds in a subpanel is to prevent neutral current from flowing on the ground wires. If neutral current uses the ground path, it can create a shock hazard. Any metal enclosure or grounded equipment connected to that ground wire could become energized.


Code Compliance

The National Electrical Code (NEC) requires separate neutral and ground buses in subpanels.

Your Observations and Expected Results
Removing the Bonding Jumper

Your instruction to remove the bonding jumper (the bar tying neutral and ground bars together) in the lighting subpanel was exactly the right thing to do. This is the
first step in isolating the neutral and ground systems.

Continuity Testing

You're using a multimeter (or similar tool) in continuity mode to test for a low-resistance path between the neutral and ground bars after removing the bonding jumper.

Expected Result (AFTER removing the jumper)

You should
not have continuity between the neutral and ground bars in the subpanel after the bonding jumper is removed. The neutral and ground systems should be isolated within that subpanel.

Your Result

You still have continuity between neutral and ground. This indicates a problem.

Possible Causes for Continuity Between Neutral and Ground in the Subpanel


Here are the most likely reasons why you're still seeing continuity, even after removing the bonding jumper:1. Neutral-Ground Bond Elsewhere (Most Common)



The
only place the neutral and ground should be bonded together is at the service entrance panel (the main panel).
This is typically the QMB panel in your case. Possible Scenario: If there's a neutral-ground bond also in the subpanel (even a hidden one), you'll see continuity. Common mistakes are; Accidental Connection

A screw touching both the neutral and ground bus.


Miswired Receptacle or Device

A receptacle or light fixture wired incorrectly, bridging the neutral and ground. Look for this in the circuit fed from the subpanel.

Internal Fault in Equipment

A device plugged into a circuit fed from the subpanel could have an internal short between its neutral and ground.


Another Subpanel Downstream

The lighting panel could be feeding another subpanel. If so, you need to check that one as well.2.

Shared Neutral (Less Likely, But Possible)

In very old wiring systems (rare in modern installations), there might be a "shared neutral" configuration where multiple circuits use a single neutral conductor. While technically possible, this is generally not permitted by current codes and can be dangerous.3.

Faulty Wiring or Damaged Insulation

A damaged wire or compromised insulation could allow a neutral wire to come into contact with a grounded metal surface, creating a path for continuity.4.

Improper Grounding

Check if the grounding electrode conductor (GEC) is properly connected to the main panel and to a suitable grounding electrode (ground rod, water pipe, etc.). A poor ground connection can sometimes lead to unusual readings.

Troubleshooting Steps
1. Verify the Main Panel Configuration

Confirm that the QMB panel (the main panel) does have a proper neutral-ground bond (usually a bonding screw or strap connecting the neutral and ground bus bars). This is essential. Verify the grounding electrode conductor (GEC) is connected to the neutral bus or the grounding bus if they are bonded.2.

Power Down the Subpanel Completely

Turn off the breaker in the QMB panel that feeds the lighting subpanel. This ensures no current is flowing during your testing.3.

Visual Inspection of the Subpanel

Carefully inspect the wiring in the lighting subpanel for any obvious signs of shorts, damage, or incorrect connections. Look closely at: All connections to the neutral and ground bars. The back of the panel for screws piercing wires. The integrity of the wiring insulation.4.

Disconnect Branch Circuits (Systematic Isolation)

This is the most effective way to find the problem.

One at a time

With the breaker to the subpanel still off, disconnect each branch circuit (one at a time) from the
neutral bar in the lighting subpanel.

Check for Continuity After Each Disconnection

After disconnecting each neutral wire, use your multimeter to check for continuity between the neutral bar and the ground bar in the subpanel.

The Culprit

When you disconnect the neutral of a specific branch circuit and the continuity
disappears, that circuit is the source of the problem.

Investigate the Problem Circuit

Once you've identified the problem circuit, carefully inspect the wiring, receptacles, and fixtures on that circuit for any miswiring, shorts, or damaged components.5.

Check Receptacles and Devices on Problem Circuit

Once you've isolated a problem circuit, go to each receptacle, switch, and light fixture on that circuit. Carefully inspect the wiring. Look for the neutral and ground wires accidentally touching.

Unplug everything

Unplug all devices from the receptacles on the problem circuit. Check for continuity again. If the continuity disappears, one of the unplugged devices is the source of the problem.

Important Safety Notes
Work De-energized

Whenever possible, work on electrical circuits with the power off. Verify the circuit is de-energized using a reliable voltage tester before touching any wires.

Qualified Person

If you are not comfortable or experienced working with electrical systems,
do not attempt to troubleshoot this yourself. Call a licensed electrician. Electricity is dangerous and can be deadly.

Code Compliance

Ensure that all repairs and modifications are done in accordance with the National Electrical Code (NEC) and any local electrical codes.*

Double-Check

Always double-check your work to ensure that all connections are secure and that the wiring is correct before restoring power.

In summary:
You're on the right track. The fact that you still have continuity after removing the bonding jumper in the subpanel indicates a wiring problem. The most common cause is a neutral-ground bond somewhere other than the main panel. Use the systematic disconnection method to isolate the problem circuit and then carefully inspect that circuit for faults. And, if you are not 100% confident in your abilities, call a qualified electrician. Flag for review

Previous Question Next Question