Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MCA is 200% of FLA for condenser unit

User: victor.cherkashi, Location: NYC, NY

Asked on: Saturday, August 17, 2024 at 6:58 pm EDT
Answered on: Thursday, March 6, 2025 at 1:18 am EST

Question: I need to supply power to a roof-mounted 5-ton Mitsubishi condenser unit, which includes one compressor with a FLA of 19A and two fans, each with FLA of 0.8A. The unit operates at 208/230V, single-phase, MCA = 40A and MOP = 45A. I was curious why the MCA is 200% of the FLA, so I reached out to technical support for clarification.Mitsubishi's support explained that the compressor current listed in the specifications is based on standard operation at 230V. For operation at 208V, you should add 20% to the FLA. In extreme weather conditions (0°F for heating or 115°F for cooling), the current can increase by another 40%, which is why the MCA is set at 40A.Since the building's system is 208V three-phase, I need to account for 34.6A per unit, calculated as (19 + 0.8 + 0.8) * 1.2 * 1.4 = 34.6A. Multiple units like these connected to the same panel will significantly increase the size of the feeder and panel.This is the first time I've seen such a large discrepancy between MCA and FLA.WHO gave them an idea for the exclusion of the 40% current increase from the FLA for extreme weather conditions.? What if 115°F temperatures last for 5 hours or more?I would appreciate your thoughts on this matter.

You've hit on a legitimate point of concern and a discrepancy between typical code application and the manufacturer's stated requirements. Let's break down the issue

Understanding the Standards & Code (Primarily NEC in the US)
FLA (Full Load Amps)

This is the
rated current draw of the motor under normal operating conditions. It's usually found on the motor's nameplate.

MCA (Minimum Circuit Ampacity)

According to the NEC (National Electrical Code), specifically Article 440 for air conditioning and refrigeration equipment, the MCA is calculated to account for the largest motor (usually the compressor) plus 125% of its rated-load current plus the sum of the full-load currents of all other motors and other loads served by the circuit. This is a minimum requirement.

MOP (Maximum Overcurrent Protection)

This is the maximum allowed size of the circuit breaker or fuses protecting the circuit. It's designed to protect the wiring from overcurrent conditions.

The Discrepancy and Mitsubishi's Approach


Mitsubishi is essentially layering on extra derating factors
beyond what the NEC typically mandates:1. 208V Derating (20% Increase)

They're accounting for the lower voltage (208V vs. 230V). A motor drawing the same power at a lower voltage will draw more current. This is perfectly valid and a common engineering practice. It ensures the motor can still perform its intended function at the lower voltage.2.

Extreme Weather Derating (40% Increase)

This is the more unusual aspect. They're accounting for additional current draw due to increased load in extreme temperatures. While it makes engineering sense, it's not a
standard requirement in the NEC.

Why the 40% Might Be Questionable (From a Code Perspective)



Code Doesn't Explicitly Require This

The NEC doesn't typically demand derating for extreme ambient temperatures beyond what's already factored into the MCA calculation (125% of the largest motor's current). The assumption is that the motor is designed to operate within a reasonable temperature range and the 125% factor provides sufficient margin for transient overloads.

Design Assumption vs. Reality

The NEC assumes the equipment is designed to handle typical operating conditions. Mitsubishi seems to be acknowledging a limitation in their design or a desire to ensure optimal performance even under extreme conditions.


Impact on Cost

Applying the 40% derating significantly increases the required wire size, conduit size, and overcurrent protection, leading to a more expensive installation.

Duration of Extreme Conditions

You're right to question the duration of the extreme temperature. If 115°F temperatures persist for extended periods (hours), the motor is likely to be running under heavier load, increasing current draw.

What Mitsubishi Might Be Thinking (Defending the 40%)



Warranty/Reliability

They might be trying to minimize warranty claims or ensure long-term reliability by preventing the motor from being constantly overloaded in extreme conditions.

Performance Guarantee

They might be guaranteeing a certain level of cooling capacity even at 115°F, which necessitates the higher current draw.


Specific Motor Characteristics

The compressor motor might have specific characteristics that make it more sensitive to overheating in extreme conditions. They may have measured data that validates this 40% increase.

Avoiding premature failure

The compressor might have been tested to have premature failure under extreme conditions at 230V.


Component Life

Continuous operation in extreme temperatures without derating could significantly shorten the lifespan of components within the unit, requiring more frequent maintenance and potentially leading to costly repairs.

Efficiency

Overheating the compressor can reduce its efficiency, leading to higher energy consumption and increased operating costs for the customer. Derating ensures the compressor operates within its optimal range, maximizing efficiency and minimizing energy waste.


Protection

Operating in extreme temperatures without derating could trigger thermal overload protection mechanisms, causing the system to shut down and interrupt cooling or heating service. Derating provides a buffer, reducing the likelihood of system shutdowns and ensuring continuous operation.

Compliance

Derating to account for extreme temperatures may be required to comply with local regulations or building codes. Some regions may have specific requirements for HVAC systems operating in extreme climates, necessitating a more conservative approach to circuit sizing and protection.

Recommendations
1. Challenge the Manufacturer (Again)

Politely push Mitsubishi for a more detailed explanation of why the 40% derating is necessary. Ask for specific data or test results that support this requirement. Ask if it's truly a hard requirement or a recommendation for optimal performance. Inquire if there are any alternatives or mitigation strategies. For example, can you improve ventilation around the unit to reduce ambient temperature?2.

Consult with an Experienced HVAC Engineer/Electrical Engineer

Get a professional opinion on whether the 40% derating is reasonable for your specific application and location. They can assess the local climate data (how often does it really reach 115°F for sustained periods?) and the building's load profile.3.

Code Official/Inspector

Discuss the situation with your local electrical inspector before you install the unit. Get their opinion on whether they'll accept the manufacturer's MCA requirement. Be prepared to provide the documentation from Mitsubishi. The inspector has the final say on whether your installation meets code.4.

Consider the Long-Term Costs

While oversizing the wiring and overcurrent protection increases the initial cost, it might be worthwhile if it extends the life of the equipment and reduces the risk of downtime, especially in critical applications.5.

Document Everything

Keep detailed records of all communications with Mitsubishi, the HVAC engineer, and the code official. This will be important if there are any issues down the road.

In Summary:


The 40% derating for extreme weather is unusual from a strict NEC perspective. While it might be prudent from an engineering standpoint, it significantly impacts cost. Thoroughly investigate the justification for this requirement, consult with professionals, and get approval from the code official before proceeding. Be sure to weigh the increased installation costs against the potential benefits of longer equipment life and reduced maintenance.Ultimately, you're trying to balance code compliance, performance, reliability, and cost. A well-informed decision is the key. Flag for review

Previous Question Next Question