User: Bill Snyder, Location: Denver, Co
Asked on: Saturday, August 17, 2024 at 11:30 pm EDT
Answered on: Thursday, March 6, 2025 at 1:19 am EST
Question: What if the AHJ says Class A protection is not required on EVSE based on the manufacturer's instructions?
That's a tricky situation that requires careful navigation and documentation. Here's a breakdown of what to consider
Understanding the Conflict:
Code Requirement
The National Electrical Code (NEC) generally requires ground-fault circuit interrupter (GFCI) protection for EVSE installations, often interpreted as Class A GFCI protection (5mA trip threshold).
Manufacturer's Instructions
If the EVSE manufacturer's instructions state that Class A GFCI protection is not required, this creates a direct conflict with the standard interpretation of the NEC.
AHJ's Authority
The Authority Having Jurisdiction (AHJ) has the final say on interpretations and enforcement of the NEC within their jurisdiction.
Possible Reasons for the Manufacturer's Stance
Built-in GFCI
The EVSE might have an internal, non-field adjustable GFCI that provides equivalent or superior protection to an external Class A GFCI. These internal GFCIs might operate at a different trip threshold or have advanced diagnostic capabilities.
Specialized Protection
The EVSE might use a different, equally effective protection method that doesn't rely on a standard Class A GFCI. This could involve sophisticated ground fault detection and interruption technology within the unit.
Specific Application
The exception might apply only to very specific installation scenarios (e.g., commercial installations with qualified personnel, specific environmental conditions).
Misinterpretation
It's also possible the manufacturer's instructions are being misinterpreted, or are unclear.
Outdated Instructions
The instructions could be outdated and not reflect current code requirements.
Steps to Take
Thoroughly Review the Manufacturer's Instructions
Carefully read every page of the EVSE's installation manual. Look for any language relating to GFCI protection, ground fault detection, or alternatives to Class A GFCI. Pay attention to any limitations or conditions placed on the exception. Does it only apply in specific situations? Note the date of the instructions.2.
Contact the EVSE Manufacturer Directly
Call or email their technical support and ask for clarification on their GFCI requirements. Specifically ask them why they don't require Class A GFCI protection, and what alternative protection they provide. Request documentation from the manufacturer (e.g., a technical bulletin, letter of compliance) that supports their claim and explains how their EVSE meets safety standards without a Class A GFCI. This documentation should specifically address the NEC requirements. Keep a record of all communication with the manufacturer, including names, dates, and summaries of the conversations.3.
Communicate with the AHJ (in writing)
Before starting the installation, submit a formal request for clarification to the AHJ. This should be in writing (email or a formal letter is best). Clearly state that the manufacturer's instructions do not require Class A GFCI protection. Include the relevant sections of the manufacturer's instructions, the documentation you received from the manufacturer (see step 2), and your justification for believing the installation will be safe. Specifically ask for the AHJ's written approval to proceed with the installation without Class A GFCI protection, based on the manufacturer's instructions and the provided documentation. Ask the AHJ what type of ground fault protection they expect to see. Document everything! Keep copies of all correspondence and submitted materials.4.
Follow the AHJ's Decision
If the AHJ approves the installation without Class A GFCI protection, follow their instructions exactly. If the AHJ requires Class A GFCI protection, you must comply. You may need to modify the installation or choose a different EVSE.5.
Consider Options if the AHJ Disagrees
Install with Class A GFCI
The simplest (and safest) option might be to just install a Class A GFCI breaker, even if the manufacturer says it's not required. This might add cost, but it avoids a conflict with the AHJ and ensures compliance with the generally accepted interpretation of the NEC. Be aware that some EVSEs might be designed to trip Class A GFCIs due to nuisance tripping issues.
Appeal the AHJ's Decision
You may have the option to appeal the AHJ's decision, but this can be a lengthy and complicated process. Consult with an experienced electrical engineer or code expert.
Important Considerations
Safety First
Your primary concern should always be safety. If you have any doubts about the safety of the installation, err on the side of caution and install Class A GFCI protection.
Documentation is Key
Thorough documentation is crucial to protect yourself and demonstrate that you followed the proper procedures.
NEC 110.3(B)
NEC 110.3(B) requires that listed or labeled equipment be installed and used in accordance with any instructions included in the listing or labeling. So, if the EVSE is listed and its instructions contradict the general NEC GFCI requirement, it creates a conflict. This is why getting clarification from both the manufacturer and the AHJ is so important.*
Future Revisions
Remember that electrical codes are updated regularly. What is acceptable today might not be acceptable in the future. Keep abreast of changes to the NEC and any local amendments.
In summary, when the manufacturer and the AHJ disagree on GFCI requirements for EVSE, you need to be proactive, communicative, and meticulously document everything. Prioritize safety and be prepared to comply with the AHJ's final decision. Flag for review