Asked on: Sunday, August 18, 2024 at 7:04 am EDT
Answered on: Thursday, March 6, 2025 at 1:19 am EST
Question: What Class of wiring would the CT conductors or cables used to monitor PV system be considered? Are they Class 1 or 2? Something else? I’ve seen some in Cat 6 cable in same raceway as power wiring and some with actual 600V conductor insulation in raceway with power conductors. In what manner can they be installed in a compliant manner from source panel to inverter? Clarification and code references appreciated. Thanks.
This is a great question with a nuanced answer. Here's a breakdown of how CT wiring in PV systems is classified and installed, along with relevant code references
Understanding the Classifications
Class 1 Circuits (NEC Article 725)
These are power-limited circuits that operate at higher voltages and currents than Class 2 or 3 circuits. They are typically not used for CT circuits in PV systems.
Class 2 Circuits (NEC Article 725)
These are low-voltage, low-energy circuits that are generally considered safer due to their limited power output. This is the most common classification for CT circuits in PV systems.
Class 3 Circuits (NEC Article 725)
Class 3 circuits are similar to Class 2, but they have higher voltage/current limits, which requires additional safety considerations. Not used in PV monitoring.
Why Class 2 is Typically Used for CT Circuits Low Voltage/Current
CT circuits are designed to produce a very small current (typically 0-5A) that is proportional to the current flowing in the conductor they are monitoring. The voltage across the CT secondary is also very low under normal operation.
Safety
Class 2 circuits are designed to limit the risk of electric shock and fire. This makes them a suitable choice for applications where the conductors may be accessible to unqualified personnel.
Isolation
The CT itself provides isolation between the high-voltage PV conductors and the low-voltage monitoring equipment.
Code Compliance
Here's how to ensure code-compliant installation of CT circuits:1. Conductor Type
Use conductors that are suitable for the voltage and temperature rating of the installation (e.g., THHN, XHHW). While Cat 6 cable can be used in some installations, it's important to verify that it is rated for the specific application and that the conductors are the correct gauge.
NEC 725.27 specifies requirements for wiring methods and materials on the load side of the Class 2 power source. NEC 310.10(C)(1)(4) & 310.10(H): Ensure conductor insulation is rated for the voltage of any conductor in the same raceway. If you're running CT wiring (even Class 2) in the same raceway as power conductors, your CT wiring insulation must be rated for the highest voltage present in that raceway. If in doubt, use conductor insulation rated for the highest voltage present.2. Raceway/Separation
NEC 300.3(C)(1)
Conductors of different electrical systems can occupy the same enclosure, raceway, or cable if all conductors are insulated for the maximum voltage of any conductor in the enclosure. This means if you have 600V conductors in a raceway, the CT wires must also be rated for 600V even if they are a Class 2 circuit.
NEC 725.136(D)
Separation from Class 1 circuits: Class 2 and 3 conductors shall be separated from Class 1, non-power limited fire alarm, and medium power network-powered broadband communications circuits as required by (1), (2), and (3): (1) Separation From Electric Light, Power, Class 1, Non-Power-Limited Fire Alarm, and Medium Power Network-Powered Broadband Communications Circuit Conductors. Class 2 and Class 3 conductors shall be separated from electric light, power, Class 1, non-power-limited fire alarm, and medium power network-powered broadband communications circuit conductors by a barrier or by maintaining a minimum spacing of 50 mm (2 in.). (2) In Cable, Cable Trays, Enclosures, Manholes, Outlet Boxes, Device Boxes, and Raceways. Class 2 and Class 3 conductors shall be installed so that there is not less than 6 mm (0.25 in.) separation from electric light, power, Class 1, non-power-limited fire alarm, and medium power network-powered broadband communications circuit conductors. (3) Hybrid Power and Communications Cables. Listed hybrid power and communications cables shall be permitted where the power cable is identified for the application.3.
Overcurrent Protection
NEC 725.41 requires that Class 2 and 3 circuits shall be protected against overcurrent. Use an appropriately sized fuse or circuit breaker. (Typically part of the power supply).4. Grounding
Follow the equipment manufacturer's instructions for grounding the CT circuit. Grounding requirements may vary depending on the specific equipment.5.
Marking
Clearly label the CT conductors and any enclosures containing them to indicate that they are part of a Class 2 circuit.
Specific Scenarios and Considerations CTs in the Same Raceway as Power Conductors
This is a common practice to simplify wiring and reduce the number of raceways. However, all conductors in the raceway must be insulated for the highest voltage present in the raceway, as per
NEC 300.3(C)(1). Therefore, if you have 480V or 600V power conductors in the same raceway, the CT conductors must also be rated for that voltage. Simply using Cat 6 cable in this scenario is not compliant unless the Cat 6 cable is rated for 600V insulation. You could use conductors with 600V insulation, such as THHN or XHHW, for the CT wiring in this case. CTs in a Separate Raceway
If you install the CT conductors in a separate raceway from the power conductors, you can use conductors with a lower voltage rating that are suitable for Class 2 circuits. This provides better isolation and can simplify the installation.
CTs and Inverter Requirements
Consult the inverter manufacturer's instructions for specific requirements related to CT wiring and installation. Some inverters may have specific recommendations for conductor type, size, and routing.
Key Takeaways CT circuits in PV systems are generally considered Class 2 circuits due to their low voltage and current. Always comply with NEC Article 725 for Class 2 circuit installations. When running CT wiring in the same raceway as power conductors, all conductors in the raceway must be insulated for the highest voltage present. Use conductors and wiring methods that are suitable for the specific application, voltage, and environmental conditions. Consult the equipment manufacturer's instructions for any specific requirements. If you have any doubts, consult with a qualified electrician or electrical engineer.
Disclaimer: Always consult with a licensed electrician or qualified professional for specific project requirements and code compliance.* Flag for review