User: Master_Krafter, Location: Seattle, WA
Asked on: Sunday, August 18, 2024 at 2:46 pm EDT
Answered on: Thursday, March 6, 2025 at 1:20 am EST
Question: Service call for frequent shutdown of computers and lighting flickers.3 phase service to an office warehouse. Mostly 129v circuits aside from basic hot water(30a 208v) and ac(17a 208v). Showing some wild readings.LN 1 - G 134vLN 2 - G 115vLN 3 - G 111vthis is with basic operation.Add a microwave on LN 3 and the voltage jumpsLN 1 - G 140vLN 2 - G 118vLN 3 - G 101 - 108vutility provider is reporting 90a spikes but no significant voltage changes. Grounding and bonding is solid. Anyone have some knowledge to share?
This is a classic symptom of a lost neutral. Here's a breakdown of why, what to check, and how to fix it
Why a Lost Neutral Causes These Problems:
Uneven Voltage Distribution
In a balanced three-phase system, the neutral provides a return path for the imbalanced loads on each phase. When the neutral connection is lost (broken, corroded, high resistance), the voltage will no longer be evenly distributed. One phase will "steal" voltage from the others, causing high voltage on some lines and low voltage on others. The more imbalanced the loads, the more dramatic the voltage swings.
Appliance Damage
The high voltage on some circuits can quickly damage sensitive electronic equipment, computers, and even lighting. The low voltage on other circuits can cause motors to overheat and fail.
Flickering Lights
The unstable voltage causes the lights to flicker.
High Neutral Current
With a compromised neutral, the current can't return properly, leading to increased neutral current and potential overheating.
Troubleshooting Steps
Verify your Meter and Connections
Before diving deep, make sure your meter is functioning correctly and your test leads are making good contact.2.
Isolate the Problem
Turn Everything Off
Turn off all breakers in the building.
Measure Voltage Again
Measure L-N voltage at the main panel. Ideally, you should see approximately equal voltages (e.g., 120V on each phase). If the voltages are significantly different even with everything off, the problem is likely upstream of your main panel (i.e., the utility company's responsibility).
Turn on Circuits One at a Time
After verifying balanced voltage with all breakers off, systematically turn on breakers, one at a time, while monitoring voltage at the panel. Watch for when the voltage imbalances appear. This will help isolate which circuits or area is contributing to the issue.3.
Inspect the Neutral Connection
This is the most critical step.
Work safely! De-energize the main breaker before inspecting. If you are not qualified to do this, call a licensed electrician.
Main Panel Neutral Bus
Visually inspect the main neutral bus bar. Look for:
Loose Connections
Tighten all neutral connections. Use the correct torque specifications.
Corrosion
Clean any corrosion on the neutral bus bar and connections.
Burn Marks
Look for signs of arcing or overheating. This is a serious red flag.
Physical Damage
Check for cracks or breaks in the bus bar.
Neutral-Ground Bond
Ensure the neutral-ground bond is intact at the service entrance (usually in the main panel). There should only be ONE neutral-ground bond at the service entrance. Multiple bonds can create circulating ground currents.4.
Check Neutral at Subpanels (if applicable)
If you have subpanels, inspect the neutral connections there as well. Subpanels should NOT have a neutral-ground bond. The neutral and ground should be kept separate in subpanels.5.
Check the Utility Company's Connection
If you've ruled out problems in your own wiring, contact the utility company. The lost neutral could be on their transformer or service drop. Common points of failure are:
Transformer Neutral Tap
The connection on the transformer itself can fail.
Service Drop Connection
The neutral wire where it connects to your building can corrode or break.6.
Check Neutral Conductor Integrity
Conduct a continuity test on the neutral conductor with power OFF. You should have close to 0 Ohms.7.
Load Balancing
Once the neutral issue is resolved, review the load distribution across the phases. Uneven loading exacerbates the effects of even minor neutral problems. Try to balance the load as much as possible.
Tools You'll Need
Multimeter
A good quality multimeter that can accurately measure AC voltage and resistance.
Screwdrivers/Wrenches
Appropriate for tightening electrical connections. Use insulated tools.
Torque Wrench
To tighten connections to the correct torque specifications (critical for electrical connections).
Wire Brush/Cleaning Supplies
To clean corroded connections.
Flashlight
For good visibility in electrical panels.
Clamp Meter (Optional)
To measure current on individual conductors.
Voltage Data Logger (Optional)
To capture voltage fluctuations over time.
Important Safety Considerations
Work De-energized
Whenever possible, work on electrical systems with the power off. Use proper lockout/tagout procedures.
Use Insulated Tools
Always use insulated tools when working on electrical systems.
Personal Protective Equipment (PPE)
Wear appropriate PPE, including safety glasses and gloves.
If in doubt, call a qualified electrician
Working with electricity can be dangerous. If you're not comfortable or qualified, don't attempt the repairs yourself.
Let me know if you have more information or specific questions about your setup, and I can try to provide more targeted advice.
Example of Troubleshooting Steps with the Provided Data
The fact that LN1-G is 134V while the others are significantly lower immediately points to a potential neutral problem.2.
The microwave test is even more telling. When you add a load to LN3, the voltage on LN3 drops significantly (111V to 101-108V), while the voltage on LN1 increases (134V to 140V). This confirms that the voltage is being "stolen" from LN3 and given to LN1 due to a poor or missing neutral return path.3.
Given this data, your first step should be a thorough inspection of the neutral connection at the main panel. Pay close attention to the neutral bus bar, connections, and neutral-ground bond.Good luck, and be safe! Flag for review