Topic: Inspector said we need to ground existing metal boxes

User: Stevenfyeager, Location: United States, Indiana

Asked on: Sunday, August 18, 2024 at 6:24 pm EDT
Answered on: Thursday, March 6, 2025 at 1:20 am EST

Question: Older two wire nonmetallic cable house we did some work in had metal boxes. Inspector said we need to ground those existing boxes. How does one do that without rewiring the whole house ?

Okay, dealing with ungrounded metal boxes in an older home with two-wire NM cable is a common and sometimes frustrating situation. The inspector is correct that, under current code, if you're adding new circuits or making extensions to existing circuits that connect to those metal boxes, the boxes generally need to be grounded. This is primarily a safety issue. Here's a breakdown of how to address this without rewiring the entire house, along with some crucial caveats

Understanding the Problem & Code (Simplified):
Two-Wire NM Cable

This older wiring has a hot (black) and a neutral (white) wire, but
no dedicated ground wire.

Metal Boxes

Metal boxes can become energized if a fault occurs in the wiring. Without a ground, that fault current has nowhere to go except through someone who touches the box.

The Goal

The aim is to provide a safe path for fault current back to the electrical panel, causing the circuit breaker to trip and de-energize the circuit.


Why not Rewire?
Rewiring an entire house is expensive and disruptive.

Acceptable Methods to Ground Metal Boxes (Without Rewiring Entirely)

The key is to find a reliable ground source. Here are a few options, from most desirable to less desirable and considerations:1.

Grounding to a Nearby Grounded Circuit (PREFERRED - if available and close)



How

If you have a
nearby grounded circuit (i.e., one with a three-wire NM cable – hot, neutral, and ground) within a reasonable distance, you may be able to extend a ground wire from that grounded circuit to the ungrounded metal box.

Requirements



Proximity

The grounded circuit must be reasonably close. The shorter the run, the better. The Code doesn't give an exact foot limit; it's left to the judgement of the AHJ (Authority Having Jurisdiction).


Wire Size

The grounding wire must be sized according to the circuit breaker size of the grounded circuit. Consult a wiring chart (easily found online or in the NEC) for the correct gauge. Typically 14 AWG or 12 AWG is used.

Proper Connections

Use approved grounding screws or clips to attach the grounding wire to the metal box. Use wire nuts or other approved connectors to make the connection to the grounding wire of the existing grounded circuit.


Considerations

This is the most preferred method because it provides a direct path to ground. However, it's only feasible if you have a suitable grounded circuit nearby.2.

Grounding to a Metal Water Pipe (CONDITIONAL - VERY Carefully Considered)



How

You
may be able to ground the metal boxes to a metallic water piping system, BUT this is highly dependent on the entire water system being metallic and continuous all the way back to where it enters the building and connects to a metal underground water service pipe that's in direct contact with the earth for at least 10 feet.

Requirements



Continuity

The water pipe
must be electrically continuous all the way back to the point where it enters the earth. This means no plastic pipe sections or dielectric unions that would break the electrical path.

Bonding

The water pipe must be properly bonded to the electrical service (usually at the main electrical panel).

Clean Connection

The connection to the water pipe must be made with an approved grounding clamp and the pipe must be clean and free of corrosion at the point of connection.


Supplemental Electrode

You STILL might need an additional grounding electrode (ground rod or other approved method) even if you use the water pipe, depending on local codes and the condition of the water pipe system.

Why it's Problematic



Plastic Pipe

The increasing use of plastic water pipes makes this method unreliable.

Electrolysis/Corrosion

Grounding to a water pipe
can contribute to electrolysis and corrosion of the pipe over time.

Changes to Plumbing

Future plumbing work (replacing sections with plastic) could unknowingly break the grounding path.

Important

If you're considering this, consult a qualified electrician and your local building inspector
before doing anything. They can assess the suitability of your water piping system.3.

Grounding to a Metal Gas Pipe (GENERALLY PROHIBITED)



DO NOT DO THIS.
Grounding to a gas pipe is extremely dangerous and is generally prohibited by electrical codes. Gas pipes are not designed to carry electrical current and could create a serious fire or explosion hazard.4. GFCI Protection (ACCEPTABLE AS AN ALTERNATIVE, NOT A TRUE GROUND)



How

Install a GFCI (Ground Fault Circuit Interrupter) circuit breaker in the panel to protect the circuit feeding the ungrounded boxes, or install GFCI receptacles as the first outlet on the circuit.


Why it's Acceptable (Sometimes)

GFCIs don't provide a true ground, but they do provide a high level of protection against electrical shock. They detect very small imbalances in current (indicating a ground fault) and quickly shut off the power.

Labeling

If you use GFCI protection, you
must label all the outlets served by the ungrounded boxes as "GFCI Protected" and "No Equipment Ground." This is crucial to inform future users of the electrical system that the outlets are not properly grounded.

Limitations



Doesn't Eliminate Noise

GFCIs primarily protect against shock. They don't eliminate electrical noise that can affect sensitive electronic equipment.


May Not Work with Surge Protectors

Some surge protectors require a ground to function properly.

Code Acceptance

The NEC
permits GFCI protection as a way to address ungrounded outlets in existing installations, but it's not always the preferred solution. Your local inspector may have specific requirements.

Important Considerations and Cautions



Licensed Electrician

Always consult with a licensed electrician. Working with electricity is dangerous, and they can properly assess your situation, determine the safest and most code-compliant solution, and perform the work correctly. This is especially important in older homes with potentially outdated or compromised wiring.

Local Codes

Electrical codes vary by jurisdiction. What's acceptable in one area may not be in another. Your local building inspector has the final say.


Permits

Check with your local building department to see if a permit is required for the electrical work.

Inspection

Have the work inspected by a qualified electrical inspector to ensure it meets code requirements.


Aluminum Wiring

If your home has aluminum wiring (common in some homes built in the 1960s and 1970s), special precautions are needed. Aluminum wiring requires the use of special connectors and anti-oxidant compounds to prevent corrosion and fire hazards.*

Don't Cut Corners

Grounding is a critical safety feature. Don't try to save money by doing it yourself if you're not qualified, or by using substandard materials.

In summary:
Grounding existing metal boxes in a house with two-wire NM cable can be done without rewiring the entire house, but it requires careful planning, a qualified electrician, and adherence to local codes. Prioritize finding a nearby grounded circuit as the best option. If that's not possible, carefully evaluate the suitability of grounding to a metal water pipe (with professional guidance). GFCI protection is an acceptable alternative, but it's not a true ground. Always put safety first! Flag for review