User: Cartoon1, Location: Florida
Asked on: Monday, August 19, 2024 at 9:10 am EDT
Answered on: Thursday, March 6, 2025 at 1:20 am EST
Question: Hi All. How do you typically size circuit breaker size for instantaneous water heaters? for 240V and 208V. I'm looking at the HA036240. As you can see in the attached It shows (4x38) for 240V and (4x32) for 208. My system is 208V, taking into consideration 32 X 125% = i end up with a 40A Breaker for each circuit. Now from what i see regarding these water heaters (different manufacturers) Is typically they show 240V and a recommended 40A breakers for a 36KW, they never show 208V in many instances. This particular one shows amperage: So 40A breaker for 208 or should it be 35A for 208?Thank you,
You are on the right track, but let's break down the process and address the discrepancies you've noticed
Understanding the Requirements
Continuous Load
Electric water heaters are considered continuous loads according to the NEC (National Electrical Code). This means they operate at maximum current for 3 hours or more. Therefore, the NEC requires that the branch circuit overcurrent protection (circuit breaker) be sized to at least 125% of the heater's full load current.
Voltage Matters
The current draw of an electric heater is directly related to the voltage. Lower voltage (208V) will result in a higher current draw for the same wattage (kW) compared to a higher voltage (240V).
Your Calculations and the HA0362401. HA036240 Specs
You're looking at an instantaneous water heater. The specs you mention (4x38A at 240V and 4x32A at 208V) likely refer to the current draw per heating element. This unit appears to have four heating elements.2.
208V Calculation (Based on HA036240 Info)
32A per element 1.25 (125% for continuous load) = 40A Therefore, you would need a 40A breaker per heating element.3.
Understanding the Discrepancy (240V vs. 208V)
Many manufacturers prioritize providing information for the more common 240V. They often assume electricians understand that the current draw will be higher at 208V for the same wattage.
Your Question: 40A or 35A for 208V?
Based on the manufacturer's information of 32A for 208V, I will stick with 40A, this is the calculated amps.
General Sizing Method
Here's a step-by-step process to size the circuit breaker:1. Determine Wattage (kW)
Know the total wattage (kW) of the water heater. In this case 36kW.2.
Calculate Full Load Current (FLC)
Use the following formulas: For 3-Phase 208V: FLC = (kW 1000) / (Voltage √3 Power Factor) For Single-Phase 208V: FLC = (kW 1000) / (Voltage Power Factor)Note: Many electric heating elements are close to unity power factor, meaning Power Factor is approximately 1. However, check the manufacturer's specifications to be sure.3.
Account for Continuous Load (125%)
Multiply the FLC by 1.25 (125%).
4.
Select the Next Higher Standard Breaker Size
Choose the next standard circuit breaker size that is equal to or greater than the calculated current. Common breaker sizes are 15A, 20A, 25A, 30A, 35A, 40A, 45A, 50A, 60A, etc.
Important Considerations NEC (National Electrical Code)
Always follow the latest edition of the NEC for all electrical installations. Article 422 covers appliances, and Article 422.10 specifically covers branch circuit sizing.
Manufacturer's Instructions
The most important factor is to follow the manufacturer's instructions for the specific water heater you are installing. They may have specific breaker size recommendations that supersede general calculations.
Wire Gauge
The wire must be properly sized for the amperage of the circuit breaker. Use the appropriate ampacity tables in the NEC.
Dedicated Circuit
Instantaneous water heaters require a dedicated circuit. They cannot share a circuit with other appliances.
Local Codes
Local building codes may have additional requirements beyond the NEC.
Electrician Recommendation
When in doubt, consult with a licensed electrician for the installation.
Example (Hypothetical, But Useful)
Let's say you have a 36 kW, 3-phase, 208V instantaneous water heater.1. FLC = (36 kW 1000) / (208V √3 1) = 100A2. 100A 1.25 = 125A3. Choose a 125A breaker. But, remember, the HA036240 specifications specifically call for four separate circuits, each with a smaller breaker, so this general calculation doesn't apply in this specific case.
In Summary for the HA036240
Follow the manufacturer's specification of 32A per element at 208V. Multiply 32A by 1.25 = 40A. Use a 40A breaker per heating element circuit.
Make sure the wire gauge is appropriate for a 40A circuit.* Consult with a licensed electrician if you are not comfortable with any part of this process.Always prioritize safety and compliance with all applicable codes. Flag for review