Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 110.26 (C)(2)2 Open doors on both sides

User: Pdan, Location: New York

Asked on: Monday, August 19, 2024 at 12:30 pm EDT
Answered on: Thursday, March 6, 2025 at 1:21 am EST

Question: don_resqcapt19 stated: where you have rows of equipment facing each other, for example MCCs. With doors open on both sides of the aisle, the space between the doors must not be less than 18".What is the source of the 18" requirement?Thanks.​

The 18" clearance between open doors of equipment like MCCs facing each other isn't a universally mandated code requirement in the NEC (National Electrical Code) in the specific way described. It's more likely derived from a combination of factors, including: Safety Considerations

The primary rationale is to provide enough space for personnel to safely work, maneuver, and escape in the event of an arc flash or other electrical incident. While the NEC may not explicitly state "18 inches between open doors," it does emphasize working space and access.


Accessibility

Adequate clearance helps ensure accessibility for maintenance, repairs, and inspections of the equipment.

Employer Safety Requirements
Employers are required to provide a safe work environment, and this may include specific spacing requirements. Manufacturer Recommendations

Some equipment manufacturers might specify a minimum clearance around their equipment, which could lead to the adoption of the 18" rule of thumb.

General Industry Practice

Over time, a certain practice may simply be adopted and carried over to the next project due to an accumulation of experience.While the NEC doesn't directly mention 18" between open doors, consider these relevant NEC articles:


NEC 110.26(A)(1), (2), (3) - Working Space

This article specifies the depth, width, and height of the working space around electrical equipment. The depth requirements are based on voltage to ground and the presence of exposed live parts on one or both sides of the working space. The width must be at least 30 inches wide or the width of the equipment, whichever is greater. The height must be at least 6.5 feet.

NEC 110.26(C)(2) - Entrance to Working Space

This requires at least one entrance of sufficient area to give access to the working space about electrical equipment.


NEC 110.26(C)(3) - Personnel Door:
This requires a personnel door for equipment rated 1200 amps or more that contains overcurrent devices, switching devices, or control devices.In summary, the 18" rule is likely a practical guideline born from a blend of safety, accessibility, and industry experience. You need to carefully consider the specific equipment, voltage levels, local codes, and company safety policies to determine the proper working space. Always consult with a qualified electrical engineer or inspector to ensure compliance with all applicable codes and standards. Flag for review

Previous Question Next Question