User: DKE, Location: Oakland, Ca
Asked on: Monday, August 19, 2024 at 5:37 pm EDT
Answered on: Thursday, March 6, 2025 at 1:21 am EST
Question: Looking to upgrade the service on a 23 unit all electric building with a three phase elevator. Currently we have 120/240 delta coming in. The engineer I am working with wants to switch to a 120/208 wye. He says there will be no issues with the change. Any thoughts?
Your engineer's statement that there will be no issues is a strong one and warrants careful consideration. While switching to a 120/208V wye system can be advantageous, it's not without potential complications in an existing building. Here's a breakdown of the pros, cons, and things you need to verify
Pros of Switching to 120/208V Wye:
More Balanced Load
Wye systems generally provide better load balancing across the phases, which is beneficial for overall efficiency and minimizing voltage fluctuations.
Better Voltage Stability
Less prone to voltage fluctuations compared to a delta system, especially under heavy or unbalanced loads.
Lower Voltage to Ground
The voltage to ground is lower in a 120/208V wye system, providing a slightly safer environment.
Elevator Compatibility
Modern elevators are typically designed to work with 208V or have transformers to accommodate it. If the existing elevator works with 240v without a transformer it would need to be investigated.
Cons and Potential Issues
Existing 240V Loads
This is the BIG one. You have an existing building wired for 120/240V delta. Many appliances and equipment might be designed to operate specifically at 240V. This includes: Electric Ranges/Ovens
These are very common and will see a significant performance drop (about 25% reduction in heating power) if fed 208V instead of 240V. This means longer cooking times and potentially unsatisfactory results.
Electric Water Heaters
Similar to ranges, water heaters will heat water much slower with 208V.
Clothes Dryers
Again, slower drying times.
Air Conditioners/Heat Pumps (especially older ones)
While some newer units can handle 208V, older units might not function correctly or efficiently.
Specialty Equipment
Any other equipment in the building specifically designed for 240V.
Cost of Replacing or Modifying Equipment
Replacing all the 240V appliances in 23 units would be very expensive. Using buck-boost transformers to step up the voltage is an option, but adds cost and complexity, and can impact efficiency.
Elevator Modifications
While the engineer might believe the elevator is compatible, it
must be thoroughly checked. Is there an existing transformer? What are the elevator motor specifications? Does the elevator control system require 240V for certain functions? Neutral Wire Size
Switching to a wye system might require a larger neutral conductor, depending on the expected neutral current. This needs to be calculated based on the expected load imbalance.
Panelboard Compatibility
Are the existing panelboards rated for 208V? This is usually not an issue, but should be verified.
Lighting
Some older fluorescent lighting ballasts might not work as efficiently (or at all) on 208V. LED lighting is generally compatible.
What You Need to Verify
Detailed Load Survey
Conduct a thorough load survey of each unit to identify all 240V appliances and equipment. Note the manufacturer and model number of each appliance.2.
Appliance Compatibility Research
Research the voltage requirements of each 240V appliance identified in the load survey. Check the manufacturer's specifications. Many appliances can operate on 208V, but with reduced performance. Determine if that reduction is acceptable to the tenants.3.
Elevator Assessment
A qualified elevator technician
must inspect the elevator and confirm its compatibility with 208V. They need to verify the motor voltage, control system voltage, and the presence (or absence) and condition of any existing transformers. Get this in writing.4. Cost Analysis
Compare the cost of: Replacing all incompatible 240V appliances. Installing buck-boost transformers for each unit. Doing nothing and potentially facing tenant complaints about poor appliance performance.5.
Neutral Load Calculation
Have the engineer calculate the expected neutral load and verify that the existing neutral conductor is adequately sized.6.
Communication with Tenants
Inform the tenants about the potential change and its impact on their appliances. Gauge their reaction to the possibility of reduced performance.
Questions for Your Engineer
"What specific steps have you taken to verify that all existing 240V loads will operate acceptably on 208V?" "What are the estimated costs of addressing any voltage incompatibility issues?" "Can you provide a written guarantee that there will be no performance degradation of any appliances after the switch?" (They won't be able to, but it highlights the risk). "Can you provide the calculations for the new neutral load requirements?" "Have you consulted with a qualified elevator technician about the elevator compatibility?"
Conclusion:
Switching to a 120/208V wye system might be a good long-term solution, but it requires careful planning and execution. The statement that there will be no* issues is highly unlikely. You need to thoroughly investigate the compatibility of existing equipment and understand the costs involved before making a decision. If the cost of upgrading 240 volt equipment is going to be too high, you can investigate if there is a 120/240 3 phase high leg delta service available.In short, proceed with extreme caution and demand thorough documentation and justification from your engineer. Flag for review