User: SafetyManDan, Location: Pennsylvania
Asked on: Monday, August 19, 2024 at 7:24 pm EDT
Answered on: Thursday, March 6, 2025 at 1:22 am EST
Question: Hi Mike. I watch a lot of your videos and love the clarity you provide. I have electrical experience 10+ years ago but by no means an expert on the current codes. Recently I lost power during a storm here in PA. It was hot and humid so at the time we had our AC on. I have a generac automatic standby generator for all the essentials. To beat the heat on the 2nd floor, I used my portable generator and powered my 2nd floor condenser. That helped keep us cool while we slept. My question relates to disconnecting means. Currently, I have an outdoor 2/p 30 disconnect with a breaker. Does the code allow me to swap that out with a 2 pole double thro switch? I would like to make a set up so if I were to need to run that condenser on generator power, I could just plug it in and not have to pull breaker and temporarily hook it up. Thanks in advance for any feedback. God bless
Hey there! Thanks for watching my videos and for the kind words. I'm glad I can provide some clarity on things. Let's talk about your situation with the AC and generator.First off, I want to offer a disclaimer
I'm providing this information for educational purposes based on my understanding of the NEC (National Electrical Code). Electrical work can be dangerous, and you should always consult with a qualified, licensed electrician in your area to ensure any work is done safely and in compliance with local codes. Codes can vary from state to state, and even municipality to municipality.Okay, let's break down what you're looking to do:
Understanding the NEC Requirements Disconnecting Means
The NEC requires a disconnecting means within sight and readily accessible from air conditioning equipment (see NEC 440.14). This disconnect isolates the equipment for servicing.
Overcurrent Protection
The AC unit also needs to be protected by an overcurrent device (breaker or fuses) sized appropriately for the unit's nameplate.
Double-Throw Switch (Transfer Switch) Considerations Your plan to use a double-throw switch to select between your main power and your portable generator is generally sound in principle, but it needs to be done safely and compliantly.
Addressing your specific setup and the code
Here’s how I see it, focusing on both safety and code compliance:1. The Double-Throw Switch (Transfer Switch) Idea
Replacing your existing 2-pole disconnect with a 2-pole, double-throw switch could work, but only if it meets specific requirements:
Listed and Rated
The switch must be listed (UL, ETL, etc.) for the intended use and rated appropriately for the voltage and amperage of the AC unit. This is absolutely crucial. The switch needs to be rated for "continuous duty" for an air conditioner. Cheaper "transfer switches" are not.
Break Before Make
The switch MUST be a "break before make" type to avoid simultaneously connecting your generator and the utility power. This prevents backfeeding into the grid, which is dangerous and illegal.
Marked
The switch needs to be clearly marked to indicate which position connects to the utility power and which connects to the generator power.
Lockable
The switch should be able to be locked in either position for safety during servicing.2.
Generator Inlet and Wiring
Inlet Box
You'll need a proper generator inlet box (usually a NEMA L14-30 for a 30-amp, 240V generator). This is a weatherproof box that allows you to safely plug in your generator.
Wiring
The wiring from the inlet box to the double-throw switch must be appropriately sized (usually 10 AWG copper for a 30-amp circuit) and installed in conduit or according to your local code requirements.
Grounding
Proper grounding is essential. Ensure the generator is properly grounded to the grounding system of your house. This might involve connecting the generator's frame to a grounding electrode (ground rod) and ensuring proper bonding within the generator.3.
Interlock is BETTER than a Double Throw Switch: Instead of a double throw switch, consider an interlock kit. This method works by installing a special circuit breaker in your main panel that only allows you to energize the generator breaker if the main breaker is turned off. This provides a secure, code-compliant method of switching between the main power and generator power, preventing dangerous backfeeding.4. Safety Considerations and Why You Need a Pro
Backfeeding
Connecting a generator directly to your home's wiring without proper isolation can backfeed power onto the grid, endangering utility workers and potentially damaging your equipment. This is why a transfer switch or interlock is absolutely essential.
Neutral Bonding
Generators can have a floating neutral or a bonded neutral. The correct configuration depends on your specific generator and your home's wiring. Improper neutral bonding can cause circulating currents and safety hazards. A licensed electrician can determine the correct configuration for your setup.
My Recommendation
Given your situation and the need for safety and code compliance, here’s my recommendation:1. Consult a Qualified Electrician
This is the most important step. Explain your situation and your goals. They can assess your existing wiring, your generator's capabilities, and your local codes to determine the safest and most compliant solution. They can also ensure proper grounding and bonding.2.
Consider a Manual Transfer Switch OR an Interlock
A properly installed manual transfer switch (the double-throw switch, installed correctly) or an interlock can provide a safe and convenient way to switch between utility and generator power. The electrician can recommend a suitable switch or interlock and install it according to code.3.
Generator Inlet
Have the electrician install a proper generator inlet box wired directly to the transfer switch or to the generator interlock.
In summary:Yes, it's possible to replace your existing disconnect with a double-throw switch or use an interlock. However, it must be done correctly, safely, and in compliance with all applicable codes. The risk of backfeeding and other hazards makes this a project best left to a qualified electrician.I hope this helps! Stay safe and God bless! Let me know if you have any other questions. Flag for review