User: Alexis, Location: Los Angeles
Asked on: Monday, August 19, 2024 at 9:41 pm EDT
Answered on: Thursday, March 6, 2025 at 1:22 am EST
Question: Hello,I'm planning a job for a 5 meter building and with all the code changes about separate compartments for unipacks, me and my inspector are now a bit confused. Feels like no one knows any longer what is ok and what is not. So I decided to do this project with a main service disconnect at 400A, a wireway and 5 separate panels as indicated in the single line I did.This setup is not as common here in SoCal, and I would appreciate an advice:1. Would I bond my neutral to ground in the service disconnect, wireway or separate panels?2. If I do it at service disconnect, which I'm leaning to, then I can't use standard 100A main panels with meters like Siemens MC1020B1100S, as they are rated as service equipment themself and have neutral bonded to ground. Would in this case be better to use meter sockets plus sub panels with a separate neutral and ground?Thank you in advance for your advice!
Okay, let's break down the complexities of this situation regarding bonding, service disconnects, wireways, and subpanels in your 5-meter building project in Southern California, particularly focusing on the changes in code regarding separate compartments for "unipacks" (likely referring to metering combinations).
Understanding the Issue: Unipacks and Compartmentalization
First, let's clarify the "unipack" issue you mentioned. Newer code cycles and utility requirements (especially in areas with advanced metering infrastructure) often require that metering equipment be physically and electrically separated from the service disconnect equipment. This separation aims to: Prevent unauthorized access to the service disconnect. Facilitate easier metering reading and maintenance by the utility. Enhance safety by isolating the service disconnect.The exact requirements for this separation vary by utility and local jurisdiction, which is why the uncertainty you and your inspector are experiencing is so prevalent.
Your Proposed Setup and Bonding Considerations
Your approach with a 400A service disconnect, wireway, and five separate panels is a solid strategy to navigate these challenges. Here's a breakdown of bonding in this scenario, followed by addressing your specific questions: Service Entrance vs. Distribution
It's crucial to understand the distinction between service equipment and distribution equipment. Service equipment is the first equipment that receives power directly from the utility. Distribution equipment receives power downstream from the service equipment. The bonding rules differ.
Bonding at the Service Disconnect
This is the correct location for your system bonding jumper. This means bonding the neutral conductor to the equipment grounding conductor (EGC) at the service disconnect. This establishes a low-impedance path for fault current to return to the source (the utility transformer), allowing the overcurrent protective devices to trip and clear the fault. Subpanel Bonding (or Lack Thereof)
Do NOT bond neutral to ground at the subpanels. Subpanels must be treated as remote distribution equipment. In a properly wired system the fault current will return to the main panel through the EGC and follow the low impedance path to the service bonding jumper.
Addressing Your Specific Questions1. "Would I bond my neutral to ground in the service disconnect, wireway, or separate panels?" Service Disconnect
YES. This is the only permissible location for the system bonding jumper in your setup. Wireway
NO. The wireway is a raceway. You run your conductors (including your equipment grounding conductor) through the wireway. Separate Panels
NO. Do NOT bond neutral to ground at the subpanels. This would create a parallel path for neutral current, which can lead to safety hazards and equipment malfunctions. Reasoning
Bonding only occurs once in the system. After the main bonding jumper at the service disconnect, the neutral conductor and the equipment grounding conductor are kept entirely separate.2.
"If I do it at service disconnect, which I'm leaning to, then I can't use standard 100A main panels with meters like Siemens MC1020B1100S, as they are rated as service equipment themself and have neutral bonded to ground. Would in this case be better to use meter sockets plus sub panels with a separate neutral and ground?" You are absolutely correct about standard main panels (like the Siemens MC1020B1100S) being unsuitable for use as subpanels in your setup! They are designed for service entrance applications and have the neutral-ground bond built in. Using them as subpanels would create the multiple neutral-ground bond you want to avoid. Your Proposed Solution (Meter Socket + Subpanel) is a Good Approach
This is a common and compliant method:
Meter Socket
A meter socket is just a connection point for the utility meter. It's not service equipment in the sense that it contains a service disconnect or overcurrent protection.
Subpanel (Without Neutral-Ground Bond)
Use a subpanel specifically designed for distribution, where the neutral and ground buses are isolated. These panels are often called "main lug only" (MLO) panels. The separate neutral and ground bars are isolated from the enclosure.
Enclosure
Consider using a NEMA 3R or 4 enclosure if outside.
Detailed Breakdown of the Recommended Setup1. Utility Service
The utility provides the service entrance conductors to your building.2.
Meter Socket
The service entrance conductors connect to a meter socket (separate compartment).3.
Service Disconnect (400A)
From the meter socket, the conductors go to your 400A service disconnect.
This is where you install the main bonding jumper, bonding the neutral to the enclosure and the equipment grounding conductor system.4. Wireway
From the service disconnect, conductors (including neutral, ground, and phase conductors) are run through the wireway to the individual subpanels.5.
Subpanels (MLO Panels)
At each subpanel location:
Connect the phase conductors to the subpanel's main lugs. Connect the neutral conductor to the isolated neutral bus. Connect the equipment grounding conductor to the isolated ground bus. Ensure there is no connection (bonding) between the neutral and ground buses in the subpanel.Important Considerations Local Codes and Utility Requirements
Always consult with your local electrical inspector and the utility company. They have the final say and may have specific requirements beyond the general NEC provisions. Get written clarification on their interpretation of compartmentalization requirements.
Grounding Electrode System
Ensure your grounding electrode system (ground rods, water pipe bond, etc.) is properly installed and connected to the equipment grounding conductor at the service disconnect.
Wire Sizing
Properly size all conductors (including grounding conductors) according to the NEC and the ampacity of the circuits.
Overcurrent Protection
Select appropriate overcurrent protection devices (fuses or circuit breakers) for each circuit.
Documentation
Maintain detailed documentation of your electrical system, including single-line diagrams and panel schedules.
Professional Installation
It is strongly recommended that a qualified and licensed electrician perform this work.
Separate enclosures: Always install the service disconnect in a separate enclosure from the meter. Do not use an all-in-one assembly, unless specifically allowed and approved by the local AHJ.
In summary, bond only at the service disconnect. Use meter sockets and "main lug only" subpanels to avoid creating multiple neutral-ground bonds. Communicate closely with your inspector and the utility to ensure compliance with all applicable requirements. Good luck with your project! Flag for review