Topic: Size the transformer for (30) Apt. Units

User: zemingduan, Location: Philadelphia,PA

Asked on: Monday, August 19, 2024 at 10:40 pm EDT
Answered on: Thursday, March 6, 2025 at 1:22 am EST

Question: Let's say you have a high rise building and the incoming electrical service of the building is 480Y/277V 3ph 4wire. You will need a 480V 3ph 3wire - 208Y/120V 3ph 4wire transformer to supply (30) Apt. units on 10th & 11th floors. The NEC calculated load for these (30) Apt. units is 327 KVA based on NEC 220.84.1. Are you allowed to use a 300 KVA transformer for the (30) Apt. Units by NEC? My thought is yes, since I think NEC Article 450 doesn't require you to size the transformer for these Apt. based on 220.84.2. Will you specify 300KVA transformer for this case? The next standard transformer is 500KVA which is overkill for the (30) Apt. units. In practical, the actual KVA demand maybe just around 0.4-0.5 of the NEC calculated load. 300 KVA transformer should be enough. But as an engineer, is it good to specify 300 KVA for this case?Let me know you thoughts fellows! Thanks!

Okay, let's break this down according to the NEC and practical considerations.1. NEC Permissibility of a 300 kVA Transformer



Generally, No (with caveats).
While Article 450 doesn't explicitly prohibit using demand factors from Article 220 in sizing a transformer, it implicitly discourages it when you are using those demand factors for a load that is highly likely to grow. Here's why: NEC 450.3(B) typically requires transformer overcurrent protection to be 125% of the transformer's rated primary current. If your calculated load is 327 kVA, and you select a 300 kVA transformer, you're relying entirely on the demand factors provided in 220.84. Any increase in load beyond those demand factors (which can happen) would push the transformer into overload, potentially tripping the overcurrent protection, creating nuisance outages and shortening the life of the transformer. NEC 450.3(A) and (B) - Overcurrent Protection and Conductor Ampacity

You must ensure that the overcurrent protection (fuses or circuit breakers) on both the primary and secondary sides of the transformer, as well as the conductor ampacity, are adequately sized to handle the transformer's rated current and any potential overload within the limits allowed by the NEC. Using a 300 kVA transformer against a calculated load of 327 kVA creates a very tight margin, potentially causing nuisance tripping as the loads increase.


NEC 220.84 Note 1
"The demand factors of this section shall not be permitted to be used in determining the feeder or service-entrance conductor size or the transformer size, where there is evidence that the present demand exceeds these factors."This means if these apartment units will potentially exceed the NEC 220.84 load, you will need to use the standard load calculation.2. Specifying a 300 kVA Transformer (Engineering Considerations)



Risk Assessment

The key is to assess the risk of exceeding the NEC 220.84 demand factors.

Future Load Growth

Apartment units tend to increase their electrical consumption over time. People add more appliances, electronics, and potentially electric vehicle chargers. A 300 kVA transformer leaves very little headroom for this future growth.


Diversity Factors

While you're right that the actual kVA demand at any given moment might be lower (diversity), relying solely on diversity is risky. A temporary spike in demand (e.g., everyone turning on their air conditioners during a heat wave) could overload the transformer.

Professional Liability

As an engineer, you have a responsibility to specify a safe and reliable system. Undersizing the transformer, even if seemingly justifiable by the NEC 220.84 demand factors, increases the risk of problems and potential liability.


Cost vs. Reliability

While the 500 kVA transformer seems like overkill initially, the cost difference between it and the 300 kVA transformer should be weighed against the potential costs of: Nuisance tripping and service interruptions. Transformer failure due to overload (which would be far more expensive than the initial cost difference). Increased operational complexity.

My Recommendation

While it's tempting to save money by using the 300 kVA transformer, my recommendation would be to strongly consider the 500 kVA transformer, or explore options in between. Here's a structured approach:1.

Re-evaluate the load calculation

Double-check your calculations based on NEC 220.84 and consider what could make them exceed the demands of the section (additional loads per unit).
2.


Look at other transformers

Are there any 375kVA or 400kVA available?3.

Perform Load Monitoring

In some cases, if possible, temporarily monitor the existing load on similar apartment units in comparable buildings to get a better handle on the actual demand. However, this might not be feasible.4.

Conservative Approach

When in doubt, it's generally better to err on the side of oversizing the transformer slightly. This provides a buffer for future load growth and helps ensure long-term reliability.5.

Document Your Decision

Clearly document your load calculations, your reasoning for selecting the chosen transformer size, and any assumptions you made about future load growth. This documentation is critical for defending your decision should any problems arise.

Alternatives to Consider (with caveats)



Medium-Voltage Service and Smaller Transformers

Explore whether it would be more efficient to have a medium-voltage service coming into the building and using multiple smaller transformers to serve different sections of the building. This can sometimes provide better load balancing and redundancy, but it also adds complexity.

In summary:


While the NEC may technically allow you to use the 300 kVA transformer based on demand factors, the risk of future load growth and potential overloading makes it a less desirable choice from an engineering perspective. The cost of the bigger transformer is less than the problems that can occur from oversizing. The 500 kVA transformer provides greater headroom and ensures the overall reliability and longevity of the electrical system. Thorough analysis, careful documentation, and consideration of future load growth are crucial in making the right decision. Flag for review

Previous Question Next Question