Topic: NJ Meter PAN / Disconnect compliance

User: Rdel6937, Location: New Jersey

Asked on: Tuesday, August 20, 2024 at 12:47 pm EDT
Answered on: Thursday, March 6, 2025 at 1:23 am EST

Question: Hi,Inquiring of you can use a MIllbank U5168 which is a 4 jaw Meter Pan which has a 200A Main breaker within it and has 4 additional spaces within the enclosure.Feed out of that enclosure to a 200A Main Lug only panel.Questions:Will PSEG accept this?Can you use a 200A MLO panel inside the home?Can you also place the whole house surge protector in the outdoor enclosure?Do you have to separate the grounds and neutrals in the MLO panel in the home?

Okay, let's break down your questions regarding the Millbank U5168 meter pan with a 200A breaker feeding a 200A main lug only (MLO) panel, specifically in the context of PSEG (presumably Public Service Electric and Gas Company, likely in New Jersey).1. Will PSEG Accept This? Highly Likely, But Needs Confirmation

Generally, PSEG
should accept this setup,

BUT
you must confirm with them directly. PSEG (and other utilities) have their own specific requirements for meter pan/meter socket installations. They may have approved meter pan lists, specific grounding requirements, or restrictions on equipment location. Call PSEG's Electrical Service Department/Inspection Authority

This is the only way to be 100% sure. Explain your proposed setup and ask if the Millbank U5168 is acceptable for your location and load requirements. Get their answer in writing if possible. Provide them with the make and model of all the equipment you are intending to use.

Consider Local Codes

Even if PSEG approves it, your local township or municipality might have their own codes that supersede or add to PSEG's requirements. Check with your local electrical inspector
before starting the work.

2. Can you use a 200A MLO panel inside the home?
Yes, Absolutely

There's nothing inherently wrong with using a 200A MLO panel inside the home. The key is that it's being fed from a breaker that protects the feeders. The 200A breaker in the meter pan is providing that protection.

3. Can you also place the whole house surge protector in the outdoor enclosure?
Yes, Most Likely, But Check the Surge Protector's Specifications

This is typically permissible, but you
must verify that the surge protector is rated for outdoor use and is suitable for the environmental conditions (temperature, moisture, etc.) within the meter pan enclosure.

NEMA Rating

Look for a surge protector with a suitable NEMA rating (e.g., NEMA 3R or NEMA 4) to ensure it can withstand the elements.

Physical Space

Ensure the surge protector physically fits within the meter pan enclosure and doesn't interfere with other components or clearances.


Proper Wiring

The surge protector must be wired correctly, according to its instructions and NEC (National Electrical Code) requirements.

4. Do you have to separate the grounds and neutrals in the MLO panel in the home?
YES, ABSOLUTELY. This is a critical safety requirement and a fundamental principle of electrical wiring. Separating the neutral and ground buses is required at any subpanel (which your MLO panel becomes when fed from the metered 200A breaker). The neutral and ground can only be bonded at the service entrance. How to Separate



Remove the Bonding Jumper/Screw

The MLO panel will likely come with a bonding screw or jumper that connects the neutral and ground buses. You
must remove this bonding jumper/screw.

Isolate the Neutral Bus

Ensure that the neutral bus is electrically isolated from the panel enclosure.

Dedicated Ground Bus

Use a separate ground bus bar (typically provided in the panel or available as an accessory) for all grounding conductors.

Summary and Important Considerations



PSEG Approval is Key

Don't proceed without explicit approval from PSEG for the specific meter pan and proposed configuration.

Local Electrical Inspector

Consult your local electrical inspector
before starting any work.

NEC Compliance

All work must comply with the National Electrical Code (NEC).

Qualified Electrician

This type of electrical work should only be performed by a licensed and qualified electrician. It's not a DIY project.


Proper Grounding

Pay very close attention to grounding and bonding requirements. Improper grounding can create dangerous situations.

Load Calculation

Ensure that the 200A service is adequate for your anticipated load. A load calculation is essential.


Inspection

You will need an electrical inspection after the work is completed to ensure it meets code and safety standards.

Disclaimer:
I am an AI chatbot and cannot provide electrical advice. Consult with qualified professionals for all electrical work. Flag for review