Question: Hi,Inquiring of you can use a MIllbank U5168 which is a 4 jaw Meter Pan which has a 200A Main breaker within it and has 4 additional spaces within the enclosure.Feed out of that enclosure to a 200A Main Lug only panel.Questions:Will PSEG accept this?Can you use a 200A MLO panel inside the home?Can you also place the whole house surge protector in the outdoor enclosure?Do you have to separate the grounds and neutrals in the MLO panel in the home?
Okay, let's break down your questions regarding the Millbank U5168 meter pan with a 200A breaker feeding a 200A main lug only (MLO) panel, specifically in the context of PSEG (presumably Public Service Electric and Gas Company, likely in New Jersey).1. Will PSEG Accept This? Highly Likely, But Needs Confirmation
Generally, PSEG should accept this setup,
BUT you must confirm with them directly. PSEG (and other utilities) have their own specific requirements for meter pan/meter socket installations. They may have approved meter pan lists, specific grounding requirements, or restrictions on equipment location. Call PSEG's Electrical Service Department/Inspection Authority
This is the only way to be 100% sure. Explain your proposed setup and ask if the Millbank U5168 is acceptable for your location and load requirements. Get their answer in writing if possible. Provide them with the make and model of all the equipment you are intending to use.
Consider Local Codes
Even if PSEG approves it, your local township or municipality might have their own codes that supersede or add to PSEG's requirements. Check with your local electrical inspector before starting the work.
2. Can you use a 200A MLO panel inside the home? Yes, Absolutely
There's nothing inherently wrong with using a 200A MLO panel inside the home. The key is that it's being fed from a breaker that protects the feeders. The 200A breaker in the meter pan is providing that protection.
3. Can you also place the whole house surge protector in the outdoor enclosure? Yes, Most Likely, But Check the Surge Protector's Specifications
This is typically permissible, but you must verify that the surge protector is rated for outdoor use and is suitable for the environmental conditions (temperature, moisture, etc.) within the meter pan enclosure.
NEMA Rating
Look for a surge protector with a suitable NEMA rating (e.g., NEMA 3R or NEMA 4) to ensure it can withstand the elements.
Physical Space
Ensure the surge protector physically fits within the meter pan enclosure and doesn't interfere with other components or clearances.
Proper Wiring
The surge protector must be wired correctly, according to its instructions and NEC (National Electrical Code) requirements.
4. Do you have to separate the grounds and neutrals in the MLO panel in the home? YES, ABSOLUTELY. This is a critical safety requirement and a fundamental principle of electrical wiring. Separating the neutral and ground buses is required at any subpanel (which your MLO panel becomes when fed from the metered 200A breaker). The neutral and ground can only be bonded at the service entrance. How to Separate
Remove the Bonding Jumper/Screw
The MLO panel will likely come with a bonding screw or jumper that connects the neutral and ground buses. You must remove this bonding jumper/screw.
Isolate the Neutral Bus
Ensure that the neutral bus is electrically isolated from the panel enclosure.
Dedicated Ground Bus
Use a separate ground bus bar (typically provided in the panel or available as an accessory) for all grounding conductors.
Summary and Important Considerations
PSEG Approval is Key
Don't proceed without explicit approval from PSEG for the specific meter pan and proposed configuration.
Local Electrical Inspector
Consult your local electrical inspector before starting any work.
NEC Compliance
All work must comply with the National Electrical Code (NEC).
Qualified Electrician
This type of electrical work should only be performed by a licensed and qualified electrician. It's not a DIY project.
Proper Grounding
Pay very close attention to grounding and bonding requirements. Improper grounding can create dangerous situations.
Load Calculation
Ensure that the 200A service is adequate for your anticipated load. A load calculation is essential.
Inspection
You will need an electrical inspection after the work is completed to ensure it meets code and safety standards.
Disclaimer: I am an AI chatbot and cannot provide electrical advice. Consult with qualified professionals for all electrical work. Flag for review