Topic: UL listing and 110.3B

User: Isaiah, Location: Baton Rouge

Asked on: Tuesday, August 20, 2024 at 1:33 pm EDT
Answered on: Thursday, March 6, 2025 at 1:23 am EST

Question: Does UL listing and UL recognition both satisfy NEC 110.3(B) requirements?We have a massive amount of cable that is UL recognized and CSA listed. But not UL listed.

No, UL Recognized components do not automatically satisfy the requirements of NEC 110.3(B).NEC 110.3(B) requires equipment to be installed and used in accordance with any instructions included in the listing or labeling. UL Listing and UL Recognition are different certifications, and the scope of their application to NEC 110.3(B) is different.Here's a breakdown: UL Listing

A UL Listed product has been tested to meet specific, published UL standards for safety and performance for a
specific and intended end use. It's a complete product intended to be installed and used as is, typically. The Listing includes installation and use instructions, and compliance with those instructions is required per NEC 110.3(B).

UL Recognition

A UL Recognized component has been evaluated for use within a larger, UL Listed product or system. It's intended to be part of something else, not a standalone installation. The Recognition focuses on the component's safety characteristics when used in conjunction with other specific components in a larger system.

UL Recognition does not imply that the component is suitable for general field installation as a standalone item.
While the recognized component will have conditions of acceptability that must be followed when used in the end product, those conditions do not apply outside that specific end product.

In your case

Since your cable is UL Recognized but not UL Listed, it doesn't meet the requirements of NEC 110.3(B) for direct installation in a general wiring application unless it's being used as a component within a larger, UL Listed assembly according to the instructions for that assembly.

The CSA listing is potentially relevant.
You'll need to determine the scope of that listing. CSA (Canadian Standards Association) also has listing and recognition programs that are similar to UL. If the cable is CSA Listed for a particular application, and that application is permitted by the NEC, then the CSA listing could satisfy NEC 110.3(B), assuming that it is installed and used in accordance with the CSA listing's instructions.

What to do


Carefully review the CSA listing documentation

Specifically, determine what the cable is listed for. Is it listed for general wiring? What are the limitations and installation instructions associated with the CSA listing?2.

Consult with a qualified electrical engineer or inspector

They can review the CSA documentation and your intended application to determine if the CSA listing is sufficient to meet NEC 110.3(B) requirements. They can also assess the specific cable construction and the installation environment.
3.


Consider the specific NEC article governing the cable type

For example, if it's a communication cable, Article 800 may provide specific requirements.

In summary, relying on the UL Recognition for NEC compliance is generally not acceptable. The CSA listing is your potential path to compliance, but it requires thorough investigation.
Don't proceed without a qualified professional's assessment. Flag for review