Question: If you have a 300' run of (25) 4" conduits on the same trapeze could you have multiple crews working at different points? Say one crew at one end and another at the other end and working toward each other?
Yes, you absolutely can have multiple crews working on a 300' run of conduit on the same trapeze, working from opposite ends towards each other. Here's why, and some important considerations
Why it's possible and common practice:
Efficiency
Having multiple crews working simultaneously significantly reduces the overall installation time. On a long run like this, it's often the only way to meet tight deadlines.
No Interference (Usually)
Assuming the supports are properly installed and the conduit is secured, one crew's work won't directly impact another crew's ability to install conduit further down the line.
Standard Industry Practice
This is a normal practice on large conduit runs in commercial and industrial construction.
Important Considerations and Best Practices
Communication is Key
The most important thing is clear and constant communication between the crews and the foreman/supervisor. This includes:
Design Review
Ensure all crews have a common understanding of the conduit layout, including bends, offsets, and termination points.
Coordination
Schedule meetings (even short ones) to discuss progress, potential conflicts, and changes to the plan.
Radio Communication
Radios or cell phones are essential for real-time communication on the job site.
Proper Support Spacing
Ensure the trapeze supports are correctly spaced and sized to handle the weight of the conduit and wiring. This is crucial for stability and safety. Consult relevant electrical codes (NEC in the US, CEC in Canada, etc.) and manufacturer specifications.
Load Distribution
Be mindful of the weight distribution as conduit is added. If one section is heavily loaded while another is empty, it could cause stress on the supports.
Bending Strategy
Decide where bends and offsets will be placed and ensure the crews coordinate those. If a complex set of bends is needed in the middle, you'll want to plan when and how that's done to avoid interference.
Couplings and Expansion Fittings
Plan the location of conduit couplings and expansion fittings (if required due to temperature changes). Couplings need to be wrench tightened. This can be a problem if you are working at the same time so you need to plan which person tightens the couplings.
Safety
Fall Protection
Crews working at heights must use appropriate fall protection equipment (harnesses, lanyards, etc.).
Clear Work Areas
Keep work areas clear of debris and tripping hazards.
Material Handling
Use proper lifting techniques and equipment to move conduit.
Lockout/Tagout (LOTO)
If any electrical work is involved (e.g., pulling conductors), follow LOTO procedures to de-energize circuits.
Coordination with Other Trades
Coordinate with other trades (e.g., HVAC, plumbing) to avoid conflicts.
Inspection
Designate someone to periodically inspect the installation to ensure it meets code and specifications.
Marking
Use marking tape or paint to designate where the conduit should run.
Pulling Conductors
Decide where the conductor pulling is going to take place so you do not have two crews pulling toward each other in the middle of the conduit run.
In summary, it is perfectly acceptable to have multiple crews working on a long conduit run simultaneously. However, meticulous planning, clear communication, and strict adherence to safety protocols are essential for a successful and safe installation. Flag for review