Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sizing breaker size for a range/oven

User: Cartoon1, Location: Florida

Asked on: Tuesday, August 20, 2024 at 3:42 pm EDT
Answered on: Thursday, March 6, 2025 at 1:24 am EST

Question: I have a range spec sheet that says 40Amp rating for a 208V. But then it also says rated 12KW. How do you typically size the breaker?This is not a continuous load: so typically i do 40AMP breaker with a #8 copper. Should i increase the breaker to 50AMP with a #8 copper?Below is the range link im looking at

Okay, let's break this down and address the conflicting information.

Understanding the Information 40 Amp Rating at 208V

This likely refers to the
maximum current draw the range could have under certain worst-case operating scenarios (all burners on high, oven preheating, etc.).

12 kW Rated

This is the total power consumption of the range. This is a more accurate representation of the typical load.

208V

This is the voltage supplied to your range. Commercial ranges do come in 208V


Non-Continuous Load

This is extremely important. Ranges are generally considered non-continuous loads in residential/commercial cooking environments.

Your Plan

You're proposing a 40A breaker and #8 copper.

Calculations and NEC Considerations
1. Calculating Current from Power (kW)

We need to convert kW to Watts: 12 kW 1000 = 12,000 Watts Calculate Amps: Amps = Watts / Volts Amps = 12,000 Watts / 208 Volts = 57.69Amps2.

NEC (National Electrical Code) Considerations - Important!
The NEC provides specific rules for range circuits. These are essential to follow. Do not ignore the NEC. The NEC 220.55 will provide the sizing calculations for your equipment. Here are steps on how to use NEC 220.55Steps on how to size using 220.55.1. Determine the Demand Factor

NEC 220.55 provides demand factors for ranges based on their rated power. You'll need to use Table 220.55. Find the appropriate row based on the number of ranges (in your case, one range). Determine if there are additional requirements listed in 220.55 for your equipment.
2.


Apply the Demand Factor

Multiply the range's rated power (12 kW) by the demand factor. Example (This is just an example - do not use these exact numbers without consulting the actual NEC table): Let's say Table 220.55 gives you a demand factor of 80% for a single range. Calculated Demand Load: 12 kW 0.80 = 9.6 kW.
3.


Calculate the Demand Load Current

Convert the demand load from kW to Watts: 9.6 kW 1000 = 9600 Watts. Calculate the demand load current: Amps = Watts / Volts Amps = 9600 Watts / 208 Volts = 46.15 Amps4.

Select the Breaker Size

The breaker must be sized to protect the conductors and cannot be smaller than the calculated demand load. Using the example above (46.15Amps) a 50-Amp breaker is likely appropriate. Double-check the range's installation instructions, as they might specify a minimum breaker size.5.

Select the Conductor Size (Wire Size)

You must select a wire gauge that is rated to carry at least the calculated demand load current. Use NEC Table 310.16 (or the appropriate table for your wiring method – e.g., NM, THHN in conduit) to determine the ampacity of the wire. Temperature Rating: Pay close attention to the temperature rating of the terminals on the range and the breaker. You may need to use the 75°C column in Table 310.16 even if your wire is rated for 90°C.

This is critical for safety.
In our example (46.15Amps), and assuming THHN wire in conduit with 75°C terminals, a #8 AWG copper conductor with an ampacity of 50 Amps would appear acceptable based on ampacity alone. However, you must verify this in your specific situation using the NEC.6. Overcurrent Protection (Breaker)

The breaker protects the wire from overheating due to overcurrent. Select a breaker size that is appropriate for the wire size and the calculated demand load. Generally, you can round up to the next standard breaker size if the calculated current falls between standard sizes (e.g., round 46.15 A up to a 50 A breaker).
3.


Why your first plan might not be correct
You have to use the demand factor to get the actual current and load of the range you are putting in. It will be incorrect if you just assume it needs a 40AMP breaker, and #8 AWG wire.

Recommendations1. Consult the Range's Installation Instructions

Always prioritize the manufacturer's installation instructions. They might specify a minimum breaker size or other critical requirements. They may also provide information on using Table 220.55 for sizing.
2.


Perform the NEC Calculation (220.55)

This is the most important step. This is not optional. Use the NEC calculations to determine the actual demand load.3.

Verify Wire Ampacity

Ensure that the wire size you choose has an ampacity at least equal to the calculated demand load current after applying the demand factor.4.

Consider Voltage Drop

For longer runs of wire, calculate the voltage drop to ensure it's within acceptable limits (typically 3% for branch circuits). You might need to upsize the wire to compensate.5.

Grounding

Proper grounding is essential for safety. Follow NEC requirements for grounding range circuits.

In Summary


A 40A breaker with #8 copper might be sufficient after demand factors. A 50A breaker with #8 copper might be sufficient after demand factors. You MUST perform the NEC calculations in 220.55, and also look at the manufacturer spec sheet to see their suggestions.

IMPORTANT WARNING Electrical work can be dangerous. If you are not a qualified electrician, DO NOT attempt to perform this work yourself. Hire a licensed electrician to ensure the installation is safe and meets all applicable codes. Local Codes Prevail: Always check with your local building department for any specific requirements that might be different from the NEC.By following the NEC and the manufacturer's instructions, you can ensure a safe and compliant installation. Good luck! Flag for review

Previous Question Next Question