Question: I was in a warehouse today picking up some materials and I saw this new pallet mounted transformer in front of the new panel and a new disconnect switch. When I was there a week ago they had the panel cover off and what they did was "tap" the original service conductors in the wireway and feed the main CB in the panel. They also "tapped" the conductors to the main CB and ran them to the disconnect switch. Both the new panel and the new disconnect switch are wired are service disconnects (you can see the GEC's). I'm assuming that this wasn't inspected just by the lack of working space in front of the panel. Besides the obvious hack work is it permissible to splice on to the existing service conductors in the wireway and then splice on to them in the panel to feed the additional disco?

You've described a concerning and potentially dangerous electrical installation. Here's a breakdown of the issues, addressing the permissibility of the "taps" and the other concerns

Key Issues & Code Violations (Likely):

1. Multiple Service Disconnects

Generally, the NEC severely restricts the number of service disconnects allowed per service. While there are exceptions (large buildings, multiple occupancy buildings, special occupancies), a standard commercial warehouse setup typically allows for a single service disconnect. Having two (the original and the new one) is almost certainly a violation unless they meet one of the exceptions. The exceptions are listed in NEC 230.2 and are highly specific and often require engineering design and approval.
2.


Tapping Service Conductors

While tapping service conductors is possible, it must meet very specific requirements in the NEC. The fact that they are "tapping" twice is even more concerning.

Feeder Tap Rules (240.21)

While not directly for
service conductors, feeder tap rules provide some guidance, though they are generally more restrictive. They would need to meet the length and ampacity requirements for either a tap that is less than 10 feet, 25 feet or a feeder tap exceeding 25 feet. These usually mean that the wire has to be equal to the existing wire or protected by OCPD (circuit breaker).

Taps within the Panel

Splicing and tapping inside electrical panels are strictly controlled. The NEC dictates how much space can be occupied with conductors and devices. Furthermore, the connections must be made with listed and identified connectors appropriate for the conductor size, material (copper or aluminum), and number of conductors. Using wire nuts alone, especially on larger service conductors, is often insufficient and potentially unsafe.3.

Service Entrance Conductors Overcurrent Protection

The NEC requires service entrance conductors to be protected against overcurrent. Tapping service conductors before the main overcurrent protective device (OCPD) of the original service disconnect creates an unprotected scenario. If an overload or short circuit occurs on the new panel, the conductors between the tap and the new disconnect's main breaker are vulnerable to overheating and fire. This is a serious safety hazard.4.

Working Space

The lack of working space in front of the panel is a direct violation of NEC 110.26. Adequate clear space (width, depth, and height) is mandatory for safe operation and maintenance of electrical equipment. The dimensions depend on the voltage and the presence of grounded parts opposite the equipment.
5.


Proper Grounding and Bonding

You mentioned seeing grounding electrode conductors (GECs) at both disconnects. While grounding is essential, simply having a GEC present doesn't guarantee a proper grounding and bonding system. The size and connection methods of the GEC must be compliant with NEC 250. Improper grounding can lead to dangerous voltage on metal parts.

Permissibility of the Taps (Almost Certainly NO)

Based on your description, it's highly unlikely that the "tapping" method is code-compliant for these reasons:

Service Conductors

Tapping directly off service conductors is inherently dangerous if not done correctly. The overcurrent protection is the biggest issue.


Multiple Disconnects

The multiple disconnects add complexity and are probably not allowed without specific, justifiable reasons.

Lack of Documentation and Inspection

The fact that this appears to be done without an inspection or proper engineering design further suggests a problem.

Why This Is Unsafe



Overheating and Fire

The undersized or improperly protected conductors after the taps are vulnerable to overheating if overloaded, potentially leading to a fire.

Electrical Shock

Improper grounding or bonding can create a shock hazard if a fault occurs.


Equipment Damage

Overloads and short circuits can damage the new panel, transformer, and other connected equipment.

What You Should Do


Do NOT touch the installation yourself.
This is dangerous work that requires qualified professionals.2. Report it to the local electrical inspector immediately. They are responsible for enforcing the NEC and ensuring electrical safety. They can inspect the installation and require it to be corrected. Provide them with as much detail as possible.3. Inform the facility owner/manager. They need to be aware of the potentially hazardous situation and should hire a qualified electrical contractor to address the issues. Make it clear that this needs to be rectified immediately.

In summary, what you've described sounds like a poorly executed and potentially dangerous electrical modification. It needs to be inspected and corrected by qualified professionals to ensure the safety of the building and its occupants. Flag for review