Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Generac 7.5KW PowerPact ATS Neutrals

User: ciscojoe, Location: Boston

Asked on: Tuesday, August 20, 2024 at 4:44 pm EDT
Answered on: Thursday, March 6, 2025 at 1:24 am EST

Question: In reference to a Generac 7.5 KW PowerPact generator. It ships with Automatic Transfer Switch (2 Pole). Reviewed ATS installation documentation. I believe install documentation contradicts itself. This is a 2 pole ATS, so Neutral is not switched. Factory installation Manual instructions say connect Main panel Neutral to ATS Neutral. Connect Generator Neutral to ATS Neutral. Then remove all targeted backup circuit neutrals, from Main Panel Neutral, and connect to ATS Neutral Bus. This makes no sense to me. Why not just leave targeted circuit Neutrals on Main Neutral Bus?

You've correctly identified a potential point of confusion and, in my opinion, a bad practice in some Generac 2-pole ATS installations. Here's a breakdown of why the instructions are the way they are, why they're potentially problematic, and a better approach

Understanding the Generac Instructions (and Their Logic... Sort Of):
Goal

Generac's instructions aim to ensure a "solid" neutral connection across the generator, ATS, and your backed-up circuits. They want to avoid any scenario where the generator neutral
might become disconnected from the neutral of the backed-up circuits.

Factory Instruction Interpretation


Main Panel Neutral to ATS Neutral

Connects the utility neutral to the ATS neutral bus.2.

Generator Neutral to ATS Neutral

Connects the generator neutral to the same ATS neutral bus. This usually bonds the generator neutral to the utility neutral through the ATS neutral bus.3.

Move Backup Circuit Neutrals

This is the crucial part. They want you to isolate the neutrals of the circuits powered by the generator from the main panel's neutral bus and only connect them to the ATS's neutral bus.

Rationale (Generac's Justification)



Eliminating Floating Neutrals

Generac's primary concern is to avoid a "floating neutral" situation when running on generator power. A floating neutral occurs when the neutral wire loses its connection to ground. This can cause dangerously high voltages on some circuits and damage equipment. By connecting the generator neutral to the ATS neutral and then running the backed-up circuit neutrals to the ATS neutral bus, they think they are ensuring a direct, always-connected neutral path.

Avoiding Neutral Current Issues

Another argument is to prevent neutral currents from flowing between the generator and the utility service (although this is much less of a concern with properly installed systems).

Why This is Problematic and Why You're Right to Question It



Unnecessary Complexity

It adds a lot of extra wiring and potential points of failure. It's far simpler and generally safer to use the existing main panel neutral bus.

Potential for Error

Moving all those neutral wires is tedious and increases the chance of making a mistake, such as miswiring or loose connections. This can create more problems than it solves.


Does NOT Solve Floating Neutrals

Even with this setup, a broken neutral on the utility side before the ATS could still create a floating neutral situation for the generator-backed-up circuits if the generator neutral is not properly bonded.

Potentially Violates Code (Depending on Implementation)

In some cases, this approach
could violate local electrical codes if it creates multiple neutral-to-ground bonds or introduces other unintended grounding paths.

A Better, Simpler, and Safer Approach (and What I Recommend Doing)



Leave the Targeted Backup Circuit Neutrals on the Main Panel Neutral Bus!


Here's why this is better and what you should do:1. Main Panel Neutral Remains the Central Point

The main panel neutral bus is
designed to be the central point for all neutral connections in your system. It's already bonded to ground. Using it simplifies wiring and reduces potential errors.2.

Generator Neutral Still Connects to ATS Neutral

You
still need to connect the generator neutral to the ATS neutral. This is important for the ATS to properly monitor voltage and for the generator's internal bonding.3.

Ensure Proper Grounding

Most modern generators and ATS units are designed to work correctly with this approach. The key is ensuring your main electrical panel is properly grounded according to code (usually with a grounding electrode conductor to a ground rod or water pipe).

Why This Works and is Safer



Continuity of Neutral

Leaving the circuit neutrals on the main panel neutral bus maintains a continuous, reliable neutral path.

Reduced Wiring

Less wiring means fewer chances for errors.


Simpler Troubleshooting

It's much easier to troubleshoot electrical issues when the wiring is straightforward.

Important Considerations



Local Codes

Always check with your local electrical inspector or a qualified electrician to ensure your installation complies with local codes and regulations. They may have specific requirements.

Generator Bonding

Make sure you understand how your generator is bonded (or not bonded) internally. Some generators have a neutral bonded to the frame, while others don't. This can affect how the generator interacts with your electrical system.

In summary:
The Generac instructions are overly cautious and, in my opinion, create more potential problems than they solve. You are correct in questioning them. Unless your local electrical inspector specifically requires you to follow Generac's instructions to the letter, I recommend leaving the targeted circuit neutrals on the main panel neutral bus. This is the simpler, safer, and more common practice. Just be sure to maintain a solid generator neutral connection to the ATS neutral bus and ensure your main electrical panel is properly grounded. Always prioritize safety and consult with a qualified electrician. Flag for review

Previous Question Next Question