Topic: Impedance question?

User: SonofAdam, Location: Portland Oregon

Asked on: Tuesday, August 20, 2024 at 8:26 pm EDT
Answered on: Thursday, March 6, 2025 at 1:25 am EST

Question: I took another swing at the load calc test yesterday and I got this question...Size the primary and secondary fuse rating of a 75kva transformer. The voltage is 480/ 240/120v single phase, 3 phase secondary 5% impedance.To me, it was worded weird and what I wrote here is strictly off memory...I couldn't get any answers to line up with what was given, and i think the impedance has something to do with it. With 4 answers to choose one i just shot from the hip on it.Any help is appreciated to help me understand this.Thanks

Okay, this is a tricky question because it's mixing single-phase primary with a three-phase secondary (or at least implying it). Let's break it down and see if we can clarify how to approach it. I'll also point out the confusing parts and assumptions we have to make.

Understanding the Problem



75 kVA Transformer

This is the apparent power rating of the transformer. This tells you the maximum power the transformer
can deliver without overheating, considering both voltage and current.

480V Primary

This is the voltage on the supply side (the utility side) of the transformer. This implies this is a single phase supply.

240/120V Secondary

This is where it gets a bit ambiguous. This likely means the secondary is a 3 phase, 4 wire, 'high leg' delta system with one of the phases being center tapped.


5% Impedance

This is crucial. It limits the fault current the transformer can deliver.

Steps to Solve


Calculate Full Load Primary Current

kVA = (V I) / 1000 Rearrange for I (Primary): I = (kVA 1000) / V I = (75 1000) / 480 I = 156.25 Amps (Primary Full Load)2.

Calculate Full Load Secondary Current (Line to Line)

kVA = (V I √3) / 1000 Rearrange for I (Secondary): I = (kVA 1000) / (V √3) I = (75 1000) / (240 1.732) I = 180.42 Amps (Secondary Full Load)3.

Primary Fuse Sizing

NEC 450.3(B) typically allows primary protection for transformers over 600V to be up to 300% of the full-load current if needed to allow for inrush current during energization. For transformers 600 volts and under the Overcurrent Protection is limited to 125% of the rated primary current. Fuse Size = Primary Full Load Current 1.25 Fuse Size = 156.25 1.25 = 195.3125 You'd round up to the next standard fuse size. Typical standard sizes are 175A, 200A, 225A, etc. So, you'd likely use a

200 Amp fuse
on the primary side.4. Secondary Fuse Sizing

NEC 450.3(B) (again) allows secondary protection to be up to 125% of the full-load current Fuse Size = Secondary Full Load Current 1.25 Fuse Size = 180.42 1.25 = 225.525 You'd round up to the next standard fuse size. So, you'd likely use a

225 Amp fuse
on each phase of the secondary side.

What about Impedance (5%)?

The impedance of the transformer is what
limits the fault current. You would use the impedance to calculate the maximum available short-circuit current at the secondary terminals. This information is critical for: Selecting the Interrupting Rating of the Fuses

The fuses must be able to safely interrupt the maximum fault current the transformer can deliver. The fault current will be significantly higher than the full load current.

Coordination Study

Ensuring that the overcurrent protective devices (fuses or breakers) are coordinated so that the fuse closest to the fault trips first, minimizing the impact of a fault.


Arc Flash Hazard Analysis

Determining the arc flash risk associated with potential faults, which dictates the necessary PPE for workers.

Calculating Fault Current (Important for Fuse Interrupting Rating)


Calculate Fault Current Multiplier

1 / Impedance (as a decimal) = 1 / 0.05 = 202.

Calculate Secondary Fault Current

Secondary Full Load Current Fault Current Multiplier 180.42 20 = 3608.4 AmpsThis means the fuses on the secondary side must have an interrupting rating of at least 3608.4 amps. Fuses are typically rated at 10kA, 20kA, 100kA, or 200kA interrupting capacity. You'd choose one that's greater than the calculated fault current.

Important Considerations and Why the Question is Tricky



Ambiguous Secondary Voltage

The 240/120V secondary could be interpreted as a single-phase center-tapped transformer. However, the question implies a 3 phase secondary.

NEC Code Compliance

The NEC (National Electrical Code) provides very specific rules for transformer protection. You
must consult the NEC for the most accurate and up-to-date requirements.

Fuse Type

The type of fuse (e.g., time-delay, fast-acting) also affects the selection and is important for motor starting and other inrush current considerations.

Motor Starting

If there are motors on the secondary circuit, you'll need to consider their inrush current during starting, which may require larger fuses or time-delay fuses.


Practical Application

In real-world applications, you would also consider the actual load on the transformer, future load growth, and coordination with other protective devices.

In Summary

Based on the information given, the most likely answers, considering rounding and standard fuse sizes, would be:

Primary Fuse

200 Amps


Secondary Fuse

225 Amps

However, you MUST also verify that the interrupting rating of the selected fuses is adequate for the calculated fault current!


The impedance is used to calculate the available fault current. This is the maximum current that the transformer can deliver under a short-circuit condition. The fuses must be able to safely interrupt this level of current. Flag for review