User: TwistLock, Location: California
Asked on: Tuesday, August 20, 2024 at 10:03 pm EDT
Answered on: Thursday, March 6, 2025 at 1:25 am EST
Question: Any violation installing an add on Energy Management System onto a ‘sub’ panel ?EMS would feed EVSE. Any preferred EMS brands / devices ? (BlackBox etc).EVSE requested at a townhouse. 70 amp (siemens) interior ‘sub’ is only source available. Meter mains are on other side of building (zinsco).Sub fed with #2 AL cable. 40a HVAC / 40a Steam existing, rest are 15 / 20 amp branch.MercBenz Wallbox by EVbox
Okay, let's break down the considerations for installing an Energy Management System (EMS) connected to an EVSE (Electric Vehicle Supply Equipment) fed from a subpanel in your townhouse situation.
Potential Violations and Code Considerations (NEC - National Electrical Code is the primary reference point) Load Calculations (Article 220)
This is the MOST critical area. You must perform a proper load calculation on the entire subpanel to determine if you have enough capacity for the EVSE, even with the EMS. This calculation needs to account for:
Existing Loads
The 40A HVAC, 40A Steam, and all other general lighting/receptacle circuits. Note that you usually don't use the full breaker rating for continuously used loads (more on that below).
EVSE Load
Even with an EMS, the EVSE can still draw a significant amount of current. The EMS won't completely eliminate the demand; it will just manage it. You need to determine the maximum current draw the EVSE could pull when allowed by the EMS. If the EVSE can charge at 40A continuous, that's 80% of the 50A breaker, which is 40A.
Diversity Factors
The NEC allows you to apply diversity factors to certain loads (like general lighting/receptacles) to account for the fact that they won't all be running at their maximum at the same time. However, HVAC and EVSE are often considered continuous loads with limited diversity.
Continuous Load Rule (210.19(A)(1) and 215.2(A)(1))
Circuits that operate continuously for 3 hours or more are considered "continuous loads." The NEC requires that the overcurrent device (breaker) and conductors be sized at 125% of the continuous load current. This is why your EVSE circuit, even if the EVSE can only draw 40A continuous, often requires a 50A breaker (40A x 1.25 = 50A).
Subpanel Capacity (408.36 and 408.37)
The subpanel's rating (70A in your case) must be sufficient for the calculated load. You can't exceed the panel's rating.
Conductor Ampacity (310.15)
The #2 AL cable feeding the subpanel must be properly rated for the calculated load and protected by the 70A breaker. Aluminum wiring has different ampacity ratings than copper. You'll need to consult the ampacity tables in the NEC based on the cable's insulation type and termination temperature rating. Also, be aware of any derating factors if the cable is bundled with other cables or runs through insulated walls.
Overcurrent Protection (240)
The EVSE circuit needs to be properly protected by a breaker sized according to the EVSE's requirements (typically 125% of the continuous charging current).
Grounding and Bonding (Article 250)
Proper grounding and bonding of the EVSE, subpanel, and grounding electrode system are essential for safety.
Listing and Labeling (110.3)
All equipment (EVSE, EMS, subpanel) must be properly listed and labeled by a recognized testing laboratory (e.g., UL).
Manufacturer's Instructions (110.3(B))
You must follow the manufacturer's instructions for the EVSE, EMS, and any other equipment you install. Deviating from the instructions can void warranties and create safety hazards.
Local Codes and Permits
Always check with your local building department to see if permits are required for the EVSE and EMS installation. They may have specific requirements in addition to the NEC.
Townhouse Association Rules
Check any HOA/COA rules which are commonly in place.
Why an EMS May Be Necessary and How It Helps Load Shedding
The primary purpose of an EMS in this scenario is to prevent the subpanel from being overloaded. It does this by monitoring the current draw of the subpanel and temporarily reducing or interrupting the power to the EVSE when other loads (like the HVAC or steam) are active.
Demand Response
Some EMS systems can also integrate with utility demand response programs, further optimizing energy usage and potentially reducing electricity costs.
Preferred EMS Brands/Devices
Several EMS solutions are available, ranging in price and features. Some popular options include: BlackBox by ClipperCreek/Enphase
A common and reliable choice, designed to work specifically with EV charging. Often recommended for its ease of installation and integration.
Wallbox Power Boost
Since you have a Wallbox EVSE, their Power Boost system is designed for seamless integration. It's a good option for compatibility.
Sense Home Energy Monitor
While not solely for EV charging, Sense can provide whole-house energy monitoring and integrate with smart plugs to control loads. It provides detailed insights into energy consumption.
Schneider Electric Wiser Energy
A more comprehensive home energy management system that can integrate with EV charging and other smart home devices.
Emporia Vue
Similar to Sense, offering whole-house energy monitoring and the ability to control circuits.
Key Considerations When Choosing an EMS
Compatibility
Ensure the EMS is compatible with your EVSE and electrical panel.
Current Monitoring
The EMS must be able to accurately monitor the current draw of the subpanel and critical loads.
Load Shedding Capabilities
Understand how the EMS prioritizes loads and how it reduces power to the EVSE (e.g., gradual reduction or complete shutoff).
Ease of Installation and Configuration
Consider the complexity of installation and configuration. Some systems are easier to set up than others.
Remote Monitoring and Control
Some EMS systems offer remote monitoring and control via a smartphone app or web interface.
Cost
Compare the cost of different systems, including the EMS unit itself and any required installation costs.
Local Incentives
Check for local rebates or incentives for installing energy management systems.
Steps to Take
Hire a Qualified Electrician
Do not attempt this work yourself unless you are a qualified and licensed electrician. Electrical work can be dangerous, and improper installation can lead to fires or other hazards.2.
Perform a Detailed Load Calculation
The electrician will perform a thorough load calculation on the subpanel to determine if it has sufficient capacity for the EVSE. This is non-negotiable.3.
Select an Appropriate EMS
Work with the electrician to choose an EMS that is compatible with your EVSE, electrical panel, and meets your needs.4.
Install the EMS and EVSE
The electrician will install the EMS and EVSE according to the manufacturer's instructions and all applicable codes.5.
Obtain Permits and Inspections
Ensure that all necessary permits are obtained and that the installation is inspected by a qualified electrical inspector.
Example Scenario - Assuming Very Conservative Numbers
Let's say after a thorough load calculation using NEC guidelines: Existing non-HVAC, non-Steam loads on the subpanel, after applying diversity factors, total 20A. HVAC is considered a continuous load so counts as 40A. Steam is considered a continuous load so counts as 40A EVSE: You want to install a 40A EVSE (capable of drawing 40A continuous). The NEC requires the breaker and wiring to be rated for 125% of the continuous load, which is 50A. The EMS should prevent it from overloading.Total calculated load: 20A + 40A + 40A + 50A = 150A.This is FAR exceeding the 70 amp capacity.
Without EMS - you can't install the EVSE.
With EMS - you would need to find an EMS that could guarantee that the EVSE's demand would be reduced sufficiently such that the total load on the panel at any one time will never exceed the 70 amp capacity of the sub-panel.(Remember you might also need to reduce existing loads if an overload occurs frequently).
Crucial Considerations
#2 AL Cable
Verify the ampacity of the #2 AL cable. It might not be sufficient for the EVSE, even with an EMS. You might need to upgrade the cable.*
Zinsco Panel
The Zinsco panel at the meter is a known fire hazard and should be replaced, regardless of the EVSE installation. This is a safety issue that needs to be addressed.
In summary, installing an EVSE on a subpanel with an EMS is possible, but it requires careful planning, a thorough load calculation, and adherence to all applicable codes and manufacturer's instructions. It's essential to work with a qualified electrician to ensure a safe and compliant installation. Flag for review