Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Should the transformer or the disconnect go to the ground rod?

User: Cjmccarthy, Location: Florida

Asked on: Wednesday, August 21, 2024 at 9:47 am EDT
Answered on: Thursday, March 6, 2025 at 1:26 am EST

Question: When grounding a service point, do you ground the disconnect and bond the transformer, ground the transformer and bond the disconnect, ground both the disconnect and transformer or , does it matter? bellow is a picture of a site and the plans we want to make sure complies to NEC.

Okay, let's break down the grounding requirements for a service point and how it relates to the disconnect and transformer. Based on the NEC, there's a specific order of operations to ensure safety.

Here's the general principle and why

The primary goal of grounding and bonding is to create a low-impedance path for fault current to return to the source (the transformer). This allows overcurrent protection devices (fuses or circuit breakers) to quickly trip and clear the fault, preventing dangerous voltages from lingering on equipment and reducing the risk of electric shock.

NEC Requirements


Based on the NEC, the following is required for grounding and bonding the service point:1. Ground the Secondary of the Transformer

This is the most critical step. You must establish a grounding electrode system at the transformer location. This usually involves:

Connecting the neutral point (X0 or similar designation) of the transformer secondary to a grounding electrode conductor (GEC).
The GEC must connect to a suitable grounding electrode system. Common grounding electrodes include: A metal underground water pipe (with specific requirements for supplemental electrodes). A ground ring encircling the building or structure. Rod, pipe, or plate electrodes. Concrete-encased electrode (ufer ground). The size of the GEC is determined by NEC Table 250.66, based on the size of the ungrounded conductors (phase conductors) from the transformer.2. Bond the Transformer Enclosure and Metal Parts

Bonding ensures that all non-current-carrying metal parts are at the same electrical potential.
Connect the transformer enclosure (the metal case) to the grounded neutral point (X0) using an equipment bonding jumper (EBJ). This EBJ should be sized according to NEC Table 250.102(C)(1) based on the size of the secondary conductors. Bond any other metal parts of the transformer installation, such as conduit, to the grounded neutral.3.

Grounding at the Service Disconnect



Establish a Grounding Electrode System at the Service Disconnect

Similar to the transformer, you need a grounding electrode system at the service disconnect. This is because the service equipment has its own grounding requirements in addition to the transformer.

Connect the neutral point of the service equipment to the grounding electrode system.
The grounding electrode conductor (GEC) size is determined by NEC Table 250.66 based on the size of the service entrance conductors. Bond the Service Disconnect Enclosure

Connect the metal enclosure of the service disconnect to the grounded neutral using an equipment bonding jumper.4.

Bonding at the Service Disconnect



Main Bonding Jumper (MBJ)

A main bonding jumper is installed at the service equipment (typically within the service disconnect). It connects the grounded conductor (neutral) to the equipment grounding conductors (EGCs) and the enclosure. The MBJ is sized according to NEC Table 250.102(C)(1).


Equipment Grounding Conductors (EGCs)

EGCs are run with the circuit conductors to all downstream equipment and connect to the equipment's metal enclosures. They provide a low-impedance path for fault current back to the service, allowing overcurrent devices to trip.

Therefore, in summary



Ground the transformer neutral and establish a grounding electrode system at the transformer.
Bond the transformer enclosure to the transformer's grounded neutral. Establish a Grounding Electrode System at the Service Disconnect. Ground the Service Disconnect neutral and connect the MBJ. Bond the Service Disconnect enclosure to the grounded neutral.Why this order is important



Fault Current Path

This arrangement creates a solid, low-impedance path for fault current to flow back to the transformer, ensuring that overcurrent devices will operate quickly.

Voltage Stabilization

Grounding the neutral point stabilizes the voltage to ground, reducing the risk of voltage imbalances and overvoltages.


Safety

It minimizes the potential for dangerous touch voltages on equipment enclosures during a fault.

Important Considerations from Your Site Plan


Without seeing the actual electrical single-line diagram and site-specific details, I can only give general advice. However, consider these: Distance

If the distance between the transformer and the service disconnect is significant, proper sizing of conductors and bonding jumpers becomes
critical to maintain a low-impedance fault current path. Voltage drop calculations may be necessary.

Separately Derived System

This sounds like a separately derived system which means the transformer's secondary neutral must be grounded as described above, independent of any grounding at the utility service entrance.

Grounding Electrode System

The grounding electrode system should be as effective as possible. Consider using multiple grounding electrodes if soil resistivity is high. Also, consider a ground ring if the site is extensive. Make sure all electrodes are bonded together to form a single grounding electrode system.


Local Codes and Regulations

Always check with the local electrical inspector or authority having jurisdiction (AHJ) for any specific requirements in your area. They may have amendments to the NEC or additional regulations you need to follow.

Coordination Study

For larger installations, a coordination study is recommended to ensure that overcurrent devices (fuses and circuit breakers) are properly coordinated to trip in the correct sequence during a fault, minimizing downtime and preventing damage.


Qualified Electrician

All of this work should be performed by a licensed and qualified electrician who is familiar with the NEC and local codes.

In conclusion, you must ground the neutral on the secondary side of the transformer and establish a grounding electrode system at the service disconnect. Then you must also bond the transformer and disconnect enclosures to their respective grounding systems. It's not a matter of choice; it's a safety requirement.
Flag for review

Previous Question Next Question