Question: I have a multiple story building for a total of 35units. 2 of those units are very large that has 2 ranges, 2 a/c, and 2 instant water heaters. The service for the building is a meter center that is 208/120V 3 phase. Most units ore getting 2 of 3 (single) 208/120 phase with a 225A panel (based on their load). For the 2 larger units that i have: i was thinking of doing 225A 3/phase 208/120V instead of 400A 208/120 2 of 3 hot (single). Is this it a better solution to do 3 phase 225 or go to a single 400A panel? I was thinking a 3phase 225 load center can still be recessed in some wall compared to a 400A single phase panel. Is there any violations of running a 3 phase to some of the condos that I'm missing?Thank you
Okay, let's break down the best approach for powering those larger units in your multi-story building, considering the 208/120V 3-phase service.
Understanding the Load
First, it's crucial to have an accurate load calculation for these larger units. The fact they have dual ranges, A/C units, and tankless water heaters suggests a significant demand. A load calculation will help in selecting the correct size for the load center.
Comparing Options: 225A 3-Phase vs. 400A Single-Phase
Here's a comparative analysis of your two options: 225A 3-Phase (208/120V)
Pros
Balanced Load
Distributes the load more evenly across all three phases of your building's service. This helps prevent voltage imbalances and can improve overall system efficiency.
Smaller Enclosure Size
As you correctly noted, a 225A 3-phase panel is likely to be physically smaller than a 400A single-phase panel, making it easier to recess into a wall.
Potentially Better for High Instantaneous Loads
With 3 phases, you are less likely to see dramatic voltage dips when appliances start up.
Cons
More Complex Wiring
Wiring a 3-phase panel is more complex and requires a good understanding of 3-phase systems.
Not Standard in Residential
3-phase in residential units is not very typical.
Cost: 3 phase panel can be more expensive than single phase 400A Single-Phase (208/120V)
Pros
Simpler Wiring
Simpler to wire compared to a 3-phase panel.
Potentially Lower Cost
Single-phase panels are generally less expensive than 3-phase panels.
Standard Residential
More in line with the wiring in residential units.
Cons
Unbalanced Load
Places a much heavier load on two phases of the service, potentially creating voltage imbalances for other units in the building.
Larger Enclosure Size
400A panels are physically large, making it difficult to recess them and potentially impacting aesthetics.
Voltage Dip Concerns
Higher risk of voltage dips when high-demand appliances start up, as all the load is concentrated on two phases.
Why 225A 3-Phase is Likely the Better Choice (Assuming Load Calculations Support It)
Given your situation and considering the larger units with their dual appliances, the
225A 3-phase (208/120V) option is generally the superior solution, provided your load calculations confirm it's adequate. Here's why:1. Load Balancing
The most significant advantage is the better load balancing across the three phases. This is critical for the overall health and efficiency of your building's electrical system. Unbalanced loads can lead to voltage drops, increased losses, and potentially damage to equipment.2.
Voltage Stability
With high-demand appliances like ranges and tankless water heaters, the 3-phase setup will provide better voltage stability. This is because the load is distributed, reducing the impact of sudden current draws on any single phase.3.
Future-Proofing
While residential units typically use single-phase, these are larger units. 3 phase will give the unit owner more flexibility in the future.4.
Smaller size 3 phase panels are physically smaller and can be more desirable in residential units.
Important Considerations and Potential Code Implications
Load Calculation is Paramount
Before making any decisions, you must perform a thorough load calculation for each of the larger units. This calculation needs to account for all appliances, lighting, and receptacle loads. It's the only way to determine the correct size of the service panel required. Base your decision on an accurate load calculation, not just an assumption. A qualified electrician or electrical engineer should perform this calculation.
NEC Article 220
The National Electrical Code (NEC) Article 220 covers load calculations. Be sure your load calculation complies with NEC requirements.
NEC Article 215
Feeder Calculations. Make sure that the feeder calculation is calculated correctly.
NEC Article 230
Service Calculation. Making sure your total service is still capable of handling the new load is another crucial point.
Accessibility and Working Space
Ensure that you have adequate accessibility and working space around the panels, as required by the NEC (Article 110).
Conductor Sizing
Select appropriate conductor sizes for both the feeders and branch circuits, based on the calculated loads and NEC requirements for ampacity and voltage drop.
Overcurrent Protection
Use appropriately sized circuit breakers or fuses for overcurrent protection, as required by the NEC.
Neutral Conductor Sizing
Correctly size the neutral conductor. In 3-phase systems, the neutral carries the imbalance of the loads on the three phases.
Local Codes and Regulations
Always check and comply with all local codes and regulations, which may have additional requirements.
Phase Balancing Within the Unit
When wiring the 3-phase panel within the unit, distribute the loads as evenly as possible across the three phases. This will help maximize the benefits of the 3-phase system.
Coordination with the Utility Company
Contact your local utility company to ensure that they approve of the 3-phase service for these units and that their equipment can handle the additional load.
Answering Your Specific Questions
"Is there any violations of running a 3 phase to some of the condos that I'm missing?" The biggest risk is that the existing building service is not designed for multiple 3-phase loads. You need to verify that your building's transformer and service entrance conductors can handle the increased load from the 3-phase units. Also, check that your local codes allow for 3-phase in individual dwelling units.
Recommendations
Hire a Qualified Electrical Engineer/Electrician
This is a complex project that requires expertise. Engage a licensed and experienced electrical engineer or master electrician to perform the load calculations, design the electrical system, and ensure compliance with all applicable codes.2.
Perform Detailed Load Calculations
Accurate load calculations are the foundation of a safe and reliable electrical system.3.
Consult with the Utility Company
Coordinate with your local utility company to verify the capacity of their service and any specific requirements they may have.4.
Prioritize Load Balancing
Design the system to minimize load imbalances across the phases.5.
Document Everything: Keep detailed records of the load calculations, panel schedules, wiring diagrams, and inspection reports.By carefully considering all these factors and working with qualified professionals, you can ensure a safe, reliable, and code-compliant electrical system for your building and its residents. Flag for review